I've been doing HP assessments for 12 years, but find myself a little limited in my knowledge of this issue.

Here's the scenario: I do an initial assessment where I find a 7-year old NG water heater with 1500 ppm undiluted CO. The homeowner brings in his plumber to "fix" it. The plumber, who doesn't own a CO monitor, cleans the burner and air intake grill, and proclaims it good. After work is done on the home, I re-test and find the CO to be even higher this time, and the draft weak.

What typically can be done to a fairly new water heater to fix the CO problem? The gas/air ratio must be out of wack, I'm thinking. Is it usually corrected by replacing the gas control valve?

The homeowner is left hanging, the plumber is without a clue and me telling him it needs to be corrected. I would recommend a different plumber, but I want to find out what a knowledgeable individual would typically do to correct this, short of replacing it. One thing I know is I need to align with a knowledgeable person to address this in the future.

John Shillito

Tags: CO, heater, plumber, water

Views: 709

Reply to This

Replies to This Discussion

I have to agree with Kurt. 2000 ppm is exceedingly high. I have tested hundreds of hot water heater (NG, Oil) and mostly they come in around 16 ppm. There is clearly something wrong and we all know that a gas hot water draft can easily be compromised. 

hey thanks for the links. Very informative on FVIR units

Hello John (and everyone else in the forum),

I'm a new visitor at this forum and it this is my first post. I look forward to more sharing and learning in the future.

The first condition that I would investigate the "weak draft". Is the flame lazy too? Is the equipment in place the same as what the flue was originally designed for?

I find the best place to contact when at a loss is the manufacturer's technical support.

Steve

RSS

Groups

Latest Activity

Victor Rols Lindsay commented on Diane Chojnowski's event Better Buildings Peer Exchange Call: Home Improvement Catalyst: Keeping the Ball Rolling with Homeowners by Delivering More Value
"Hi Diane, Unfortunately some of us are unable to partake in this webinar/ forum. Is there a…"
7 hours ago
Ken Summers replied to Gregory Cisco's discussion Abandoning under-slab HVAC ductwork which fills with groundwater seasonally.
"My largest concern is moisture. I have seen mold forming on interior walls in the heating season…"
10 hours ago
Seth Romme replied to Sonja Persram's discussion Energy Savings Guarantee for single family dwellings in cold climate??
"Hi Sonja We provide home energy optimization services and provide a 5-year heating and cooling…"
12 hours ago
Lindsay Bachman posted events
14 hours ago
Derrick Koehn's video was featured

How Technology and Innovation Are Making Outdoor Wood Burning Stoves More Efficient and Environmentally Friendly

Introduction Since ancient times, wood burning has been used for heating in some capacity or other. Although, of late, wood stoves are thought of more as a decorative appliance than a heat source, in truth wood heat is still one of the most…
15 hours ago
Efficiency First California's blog post was featured
15 hours ago
Diane Chojnowski's event was featured
Thumbnail

Better Buildings Peer Exchange Call: Home Improvement Catalyst: Keeping the Ball Rolling with Homeowners by Delivering More Value at Eastern Time

September 21, 2017 from 1pm to 2:30pm
Thursday, September 21 1-2:30pm Eastern TimePlease join this Peer Exchange call to…See More
15 hours ago
Diane Chojnowski posted an event
Thumbnail

Better Buildings Peer Exchange Call: Home Improvement Catalyst: Keeping the Ball Rolling with Homeowners by Delivering More Value at Eastern Time

September 21, 2017 from 1pm to 2:30pm
Thursday, September 21 1-2:30pm Eastern TimePlease join this Peer Exchange call to…See More
15 hours ago

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service