Vital to the operation of the refrigeration cycle, superheat must be maintained and stable to protect the compressor.  We all know that the heart of the system cannot compress liquid (slug) without bad things happening.  This would represent low/no superheat.  But, did you know high superheat can cause valve and compressor problems as well?  No matter the reason for attaching your gauges to the system, you must check the superheat, in the air-conditioning cycle.

Read More

Views: 603

Comment

You need to be a member of Home Energy Pros to add comments!

Join Home Energy Pros

Comment by Bob Blanchette on January 16, 2014 at 2:12pm

Depends on type of system. TXV and Fixed orifices have different charging methods. As Steven stated airflow needs to be addressed, in many systems it falls WAY short. 3+ ton systems seem to be the worst offenders.

Comment by Steven Lewis on January 16, 2014 at 8:12am

Super heat readings without knowing airflow only gives you 1/2 the equation.  Dirty filters/ low airflow/refrigerant overcharge/low temp in building or low outdoor temp will all affect the superheat of the system.  If the superheat is out of range (high or Low) then the cause needs to be determined and corrected.  We all say that the house is a system but in HVAC  I say everything is Relative.  When you change one condition, it effects everything else, so it not the superheat temp but how it relates to the other information you gather.  As an example an A/C can have a high super heat of 20 if the indoor temp is high 88+ and outdoor temps are high as well and then when the unit has the house cooled down and running under normal conditions the superheat will be in normal range ( approx 8)  If you tried to charge the unit to reach the 8' you  would have vastly overcharged the system and dramatically raised its operating costs and shortened it life while making the homeowner uncomfortable as well.

Comment by Eric Kjelshus on January 10, 2014 at 6:34pm

I had a printer ask for just 2' superheat +-1'  to keep the paper very dry and never shut down the air handler/AC unit no case heater.    Most ask for 8'+ up to 30' superheat  next to the compresser.  so whats the deal?

Videos

  • Add Videos
  • View All

Latest Activity

Barbara Smith posted videos
14 hours ago
CharlieK posted a discussion

Eco-Cottage Program Applauded By Housing Groups, Suppliers & Lenders

AmeriSus a leading player in the eco-kit home business kicked off a new program on MLK-day which…See More
19 hours ago
Diane Chojnowski posted a discussion

Call for Nominations: Tony Woods Award and Building Performance Hall of Fame

The Building Performance Institute, Inc. (BPI) is seeking nominations for the 2017 Tony Woods Award…See More
19 hours ago
Diane Chojnowski added a discussion to the group 1000 Home Challenge
Thumbnail

January Webinar: Intro to the 1000 Home Challenge

The January Intro to the 1000 Home Challenge webinar will be  Friday, Jan 20 at 10-11:30 AM eastern…See More
19 hours ago
Diane Chojnowski's event was featured
Thumbnail

Introduction to the 1000 Home Challenge Webinar at Eastern Time

January 20, 2017 from 10am to 11:30am
The January Intro to the 1000 Home Challenge webinar will be  Friday, Jan 20 at 10-11:30 AM eastern…See More
19 hours ago
Diane Chojnowski posted an event
Thumbnail

Introduction to the 1000 Home Challenge Webinar at Eastern Time

January 20, 2017 from 10am to 11:30am
The January Intro to the 1000 Home Challenge webinar will be  Friday, Jan 20 at 10-11:30 AM eastern…See More
19 hours ago
Barbara Smith's video was featured

NY State Weatherization Story

The Weatherization Assistance Program (WAP) is an energy efficiency and conservation program administered by the New York State Homes and Community Renewal (...
20 hours ago
Quinn Korzeniecki added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Call for Nominations: Tony Woods Award and Building Performance Hall of Fame

The Building Performance Institute, Inc. (BPI) is seeking nominations for the 2017 Tony Woods Award…See More
21 hours ago

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service