It difficult to imagine something bad happening as a result of doing something we feel is so good. But here's what is bound to happen, at least a few times...

  1. A manual-j load calculation is produced by an HVAC contractor or third party.
  2. The default CFM values are left in place for the final report.
  3. This report is handed off to someone that sizes the ductwork in the field.
  4. They use the CFM numbers on the Manual-J report to size the ducts.
  5. Ducts are installed.
  6. Equipment is selected to meet the total cooling load, as shown on the Manual-J report.
  7. The equipment that is to be installed is the next available size.
  8. This system blows more air that what was represented on the Manual-J report.
  9. System is installed.
  10. Balancing report is completed for ESv3. Actual CFM numbers are quite a bit larger than the targets - more than the 20% difference allowed. 
  11. Ducts are too small for the system installed. Transfer grilles are too small. System performance is low, due to low airflow.

We need to make sure that our TARGET CFM #'s on the Manual-J reports are representative of the ACTUAL amount of air the system will be moving around the house. This means that the installing contractor may need to modify the CFM targets to match the installed equipment. If you're a rater, and you're working on a Version 3 ENERGY STAR project, be sure you keep these things in mind when you're measuring transfer grille sizes or critiquing a balancing report.

Here's a post I recently did on this topic. Check it out. I would love to hear your thoughts on the topic!

Tags: duct, manual-j, sizing

Views: 458

Discussion Forum

Can you trust your Load Calc Software?

Started by Christopher Morin. Last reply by Eric Kjelshus Feb 18, 2014. 1 Reply

Attic insulation vs. Insulated roof deck

Started by Robert DV. Last reply by Robert DV Jul 6, 2012. 3 Replies

Support licensing in 2011

Started by Robert Zockoff. Last reply by Robert Zockoff Jun 20, 2011. 2 Replies

Latest Activity

Rob Buchanan posted a discussion

Building envelope and mechanical interactive effects

Good afternoon everyone,I was reviewing some of the old BPI newsletters and noticed a…See More
34 minutes ago
Jason Raddenbach replied to Brent Shapiro's discussion Investigating 3257KWH monthly usage issue.
"Brent, The fridge would be easy to isolate. You can borrow a Kill A Watt Meter from your local…"
2 hours ago
Mick Lane replied to Brent Shapiro's discussion Investigating 3257KWH monthly usage issue.
"My inclination would be to start with the water heater and the refrigerators.  You are looking…"
3 hours ago
Brennan Less replied to Brent Shapiro's discussion Investigating 3257KWH monthly usage issue.
"What about a hot water plumbing leak? I would expect on the order of 5,000 kWh per year with…"
3 hours ago

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service