It difficult to imagine something bad happening as a result of doing something we feel is so good. But here's what is bound to happen, at least a few times...

  1. A manual-j load calculation is produced by an HVAC contractor or third party.
  2. The default CFM values are left in place for the final report.
  3. This report is handed off to someone that sizes the ductwork in the field.
  4. They use the CFM numbers on the Manual-J report to size the ducts.
  5. Ducts are installed.
  6. Equipment is selected to meet the total cooling load, as shown on the Manual-J report.
  7. The equipment that is to be installed is the next available size.
  8. This system blows more air that what was represented on the Manual-J report.
  9. System is installed.
  10. Balancing report is completed for ESv3. Actual CFM numbers are quite a bit larger than the targets - more than the 20% difference allowed. 
  11. Ducts are too small for the system installed. Transfer grilles are too small. System performance is low, due to low airflow.

We need to make sure that our TARGET CFM #'s on the Manual-J reports are representative of the ACTUAL amount of air the system will be moving around the house. This means that the installing contractor may need to modify the CFM targets to match the installed equipment. If you're a rater, and you're working on a Version 3 ENERGY STAR project, be sure you keep these things in mind when you're measuring transfer grille sizes or critiquing a balancing report.

Here's a post I recently did on this topic. Check it out. I would love to hear your thoughts on the topic!

Tags: duct, manual-j, sizing

Views: 383

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hannah Miller commented on Adam Flowers's blog post Comfort as a Selling Point
"Hello Adam! I hope you are still messages from this site. I just was forwarded your post and it…"
7 hours ago
Michael Dunseith replied to robert jones's discussion Should your local weatherization company be required to have someone BPI certified on their staff?
"Why the concern with airflow around heating and domestic pipes? Most are inside the envelope. What…"
9 hours ago
Tom White posted a video

Weatherization to Home Performance -- Tools & Tips for Developing For-profit Services

Are you a low income weatherization contractor looking to add home performance work you your services? The Home Performance Resource Center, Efficiency First, and NCAF present resources developed through expert industry engagement. While many of the…
11 hours ago
Jim Gunshinan posted a discussion

Tax Time Blues

There is a tax credit available to homeowners who have walls insulated. The credits were continued…See More
11 hours ago
Bruce Glanville replied to robert jones's discussion Should your local weatherization company be required to have someone BPI certified on their staff?
"I have been testing homes for my state utility as a baseline residential load data collection…"
11 hours ago
Stan Kuhn replied to Jim Gunshinan's discussion When your shower is in your kitchen...
"I think this is in the wrong Forum, it belongs in Hall of Shame.  One the dumbest ones…"
12 hours ago
Terrell posted a status
"Ebook version of my book Passive Buildings in Canada - detailed sections http://store.blurb.ca/ebooks/521524-passive-buildings-in-canada"
13 hours ago
Terrell posted an event

Boots on the Ground webinar at Toronto

March 10, 2015 all day
Passive Buildings Canada is pleased to be a sponsor and webinar host for BlueGreen Consulting…See More
14 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service