It difficult to imagine something bad happening as a result of doing something we feel is so good. But here's what is bound to happen, at least a few times...

  1. A manual-j load calculation is produced by an HVAC contractor or third party.
  2. The default CFM values are left in place for the final report.
  3. This report is handed off to someone that sizes the ductwork in the field.
  4. They use the CFM numbers on the Manual-J report to size the ducts.
  5. Ducts are installed.
  6. Equipment is selected to meet the total cooling load, as shown on the Manual-J report.
  7. The equipment that is to be installed is the next available size.
  8. This system blows more air that what was represented on the Manual-J report.
  9. System is installed.
  10. Balancing report is completed for ESv3. Actual CFM numbers are quite a bit larger than the targets - more than the 20% difference allowed. 
  11. Ducts are too small for the system installed. Transfer grilles are too small. System performance is low, due to low airflow.

We need to make sure that our TARGET CFM #'s on the Manual-J reports are representative of the ACTUAL amount of air the system will be moving around the house. This means that the installing contractor may need to modify the CFM targets to match the installed equipment. If you're a rater, and you're working on a Version 3 ENERGY STAR project, be sure you keep these things in mind when you're measuring transfer grille sizes or critiquing a balancing report.

Here's a post I recently did on this topic. Check it out. I would love to hear your thoughts on the topic!

Tags: duct, manual-j, sizing

Views: 438


  • Add Videos
  • View All


Latest Activity

Benny hani replied to Benny hani's discussion Manual J online
"Thanks Bob"
2 hours ago
Benny hani replied to Benny hani's discussion Manual J online
"Thank you Isaac"
2 hours ago
Bob Blanchette commented on Amber Vignieri's blog post Even with Polar Vortex, Hourly Pricing Participants Saved
"Looks like the days of paying a fixed amount per KWh are rapidly coming to an end. Many utilities…"
3 hours ago
Bob Blanchette replied to Benny hani's discussion Manual J online
"Be sure the size that you ACCURATELY calculate actually gets installed. Often…"
4 hours ago
Bob Blanchette replied to Sean Lintow Sr's discussion Water Saver or Gimmick? in the group Best Practices (Residential)
"The problem is these devices NEVER pay for themselves. Water is cheap, about $3 per 1,000 gallons…"
4 hours ago
Bud Poll replied to Rob Madden's discussion Blower Door Testing on Energy Star v3 home
"Where was the blower set up, front door, other?  Was if located in an unobstructed area, not a…"
15 hours ago
David N. Armington liked John Poole's discussion Two Part Epoxy and Repair of Structural Wood
David N. Armington joined John Poole's group

Historic Home

Historic and vintage homes are significant to our cultural heritage, yet often lack energy…See More

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service