It difficult to imagine something bad happening as a result of doing something we feel is so good. But here's what is bound to happen, at least a few times...

  1. A manual-j load calculation is produced by an HVAC contractor or third party.
  2. The default CFM values are left in place for the final report.
  3. This report is handed off to someone that sizes the ductwork in the field.
  4. They use the CFM numbers on the Manual-J report to size the ducts.
  5. Ducts are installed.
  6. Equipment is selected to meet the total cooling load, as shown on the Manual-J report.
  7. The equipment that is to be installed is the next available size.
  8. This system blows more air that what was represented on the Manual-J report.
  9. System is installed.
  10. Balancing report is completed for ESv3. Actual CFM numbers are quite a bit larger than the targets - more than the 20% difference allowed. 
  11. Ducts are too small for the system installed. Transfer grilles are too small. System performance is low, due to low airflow.

We need to make sure that our TARGET CFM #'s on the Manual-J reports are representative of the ACTUAL amount of air the system will be moving around the house. This means that the installing contractor may need to modify the CFM targets to match the installed equipment. If you're a rater, and you're working on a Version 3 ENERGY STAR project, be sure you keep these things in mind when you're measuring transfer grille sizes or critiquing a balancing report.

Here's a post I recently did on this topic. Check it out. I would love to hear your thoughts on the topic!

Tags: duct, manual-j, sizing

Views: 432

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Steve Mann replied to Steve Mann's discussion Eliminator EF400 Smoke Machine in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Yes it is. Steve"
2 hours ago
Laurie DiDonato updated an event
Thumbnail

Become a HERS Rater with the NE HERS Alliance this fall! at Classroom Component at Energize Connecticut Center

September 19, 2016 at 9am to October 21, 2016 at 5pm
Online Component: September 19th-30th - Weekdays 9am-12pm5-Day Classroom/Field Training:October…See More
4 hours ago
Melissa Baldridge posted a discussion

IECC 2012 & 2015 Compliance & HRVs

 I’m failing IECC 2012 with the HRVs we’ve been using – Honeywell .  (See specs below that I…See More
5 hours ago
Chris Woods replied to Steve Mann's discussion Eliminator EF400 Smoke Machine in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Is this still available?"
5 hours ago
Melissa Baldridge replied to Melissa Baldridge's discussion ENERGY STAR - Slab Insulation
"Thanks, John.  That's helpful.  And yes - I've seen projects with perimeter…"
5 hours ago
Jan Green commented on Diane Chojnowski's group Facebook Pages
"Great to see FB pages here!   "
5 hours ago
Brett Little replied to Rob Madden, Solar Home Broker's discussion Indoor Air Quality Monitors and Meters
"Great! Email me at Brett.Little@greenhomeinstitute.org"
7 hours ago
Quinn Korzeniecki replied to Larry Nissman's discussion Foam insulation on attic floor
"I'll send you a message on here for more details. Keep an eye on your inbox!"
8 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service