It difficult to imagine something bad happening as a result of doing something we feel is so good. But here's what is bound to happen, at least a few times...

  1. A manual-j load calculation is produced by an HVAC contractor or third party.
  2. The default CFM values are left in place for the final report.
  3. This report is handed off to someone that sizes the ductwork in the field.
  4. They use the CFM numbers on the Manual-J report to size the ducts.
  5. Ducts are installed.
  6. Equipment is selected to meet the total cooling load, as shown on the Manual-J report.
  7. The equipment that is to be installed is the next available size.
  8. This system blows more air that what was represented on the Manual-J report.
  9. System is installed.
  10. Balancing report is completed for ESv3. Actual CFM numbers are quite a bit larger than the targets - more than the 20% difference allowed. 
  11. Ducts are too small for the system installed. Transfer grilles are too small. System performance is low, due to low airflow.

We need to make sure that our TARGET CFM #'s on the Manual-J reports are representative of the ACTUAL amount of air the system will be moving around the house. This means that the installing contractor may need to modify the CFM targets to match the installed equipment. If you're a rater, and you're working on a Version 3 ENERGY STAR project, be sure you keep these things in mind when you're measuring transfer grille sizes or critiquing a balancing report.

Here's a post I recently did on this topic. Check it out. I would love to hear your thoughts on the topic!

Tags: duct, manual-j, sizing

Views: 347

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Kurt, check your emails.  Sent you a friend request you need to confirm then I can send you a…"
6 hours ago
Kevin Jordan replied to Kevin Jordan's discussion Does anyone have pointers on approaching real estate induatry.
"thank you sir!! If you have any other tips Id appreciate. I am new in this industry and I go and…"
6 hours ago
Bud Poll replied to Kurt Shafer's discussion Where can I find the best radiant barrier to install under my roof?
"Hi Kurt, You mentioned "On a RESNET discussion some insulation experts agreed that insulation…"
7 hours ago
Kurt Shafer commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Wow, I am very sad to hear about your eyes.  Would have been super to do that comparison. Good…"
8 hours ago
Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"My dads house has an attached garage.  It was converted to living space around 20 years…"
8 hours ago
Kurt Shafer commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Hal, do I see a terrific chance for you to show us all the power of your RCC? Your father's…"
9 hours ago
Hal Skinner replied to Kevin Jordan's discussion Does anyone have pointers on approaching real estate induatry.
"Kevin, Several years ago I worked closely with a general contractor and a real estate…"
9 hours ago
Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"That same RCC, used as paint on the ceiling of living space, will do the same as if it was applied…"
9 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service