It difficult to imagine something bad happening as a result of doing something we feel is so good. But here's what is bound to happen, at least a few times...

  1. A manual-j load calculation is produced by an HVAC contractor or third party.
  2. The default CFM values are left in place for the final report.
  3. This report is handed off to someone that sizes the ductwork in the field.
  4. They use the CFM numbers on the Manual-J report to size the ducts.
  5. Ducts are installed.
  6. Equipment is selected to meet the total cooling load, as shown on the Manual-J report.
  7. The equipment that is to be installed is the next available size.
  8. This system blows more air that what was represented on the Manual-J report.
  9. System is installed.
  10. Balancing report is completed for ESv3. Actual CFM numbers are quite a bit larger than the targets - more than the 20% difference allowed. 
  11. Ducts are too small for the system installed. Transfer grilles are too small. System performance is low, due to low airflow.

We need to make sure that our TARGET CFM #'s on the Manual-J reports are representative of the ACTUAL amount of air the system will be moving around the house. This means that the installing contractor may need to modify the CFM targets to match the installed equipment. If you're a rater, and you're working on a Version 3 ENERGY STAR project, be sure you keep these things in mind when you're measuring transfer grille sizes or critiquing a balancing report.

Here's a post I recently did on this topic. Check it out. I would love to hear your thoughts on the topic!

Tags: duct, manual-j, sizing

Views: 427

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Dan Antonioli replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"Daniel,  Several years ago I was researching two different systems, one of which I almost…"
3 hours ago
Dan Antonioli replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"Rich, it always depends on site conditions, but generally speaking the 80% figure is a common…"
3 hours ago
Rick Causo posted a video

Swing Green GFX Drain Water Heat Recovery - GreenFoX

PowerHouseTV aired Sept 5 & 6, 2015. Segment 2 of the show highlights Swing Green, Inc. and the 4th generation of Drain Water Heat Recovery system, the Green...
8 hours ago
Matt Thornberry replied to Kim Tanner's discussion Game of Homes
"Thanks Kim! Game of Homes is an exciting new way to earn professional development credits for BPI…"
10 hours ago
Tom White posted a video

Enhabit: the non-profit that helps homes work better

Hear from homeowners Sonia, Amy, Roberta and Ty of Portland, Oregon, and Andy of Beaverton, Oregon, about their experiences with Enhabit. Enhabit is a non-pr...
10 hours ago
Daniel Beauchemin replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"Dan Antonioli, You can use a ThermoDrain, drain water heat recovery to preheat your water and…"
11 hours ago
Steve Leombruno replied to Tim Kendzia's discussion Cooling effect from solar panels
"I have been told t"
11 hours ago
Rich Manning replied to Diane Chojnowski's discussion Poll: Where do you go for information on home performance?
"My favorite is Building Science Corp. Its not only comprehensive, its free!"
11 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service