It difficult to imagine something bad happening as a result of doing something we feel is so good. But here's what is bound to happen, at least a few times...

  1. A manual-j load calculation is produced by an HVAC contractor or third party.
  2. The default CFM values are left in place for the final report.
  3. This report is handed off to someone that sizes the ductwork in the field.
  4. They use the CFM numbers on the Manual-J report to size the ducts.
  5. Ducts are installed.
  6. Equipment is selected to meet the total cooling load, as shown on the Manual-J report.
  7. The equipment that is to be installed is the next available size.
  8. This system blows more air that what was represented on the Manual-J report.
  9. System is installed.
  10. Balancing report is completed for ESv3. Actual CFM numbers are quite a bit larger than the targets - more than the 20% difference allowed. 
  11. Ducts are too small for the system installed. Transfer grilles are too small. System performance is low, due to low airflow.

We need to make sure that our TARGET CFM #'s on the Manual-J reports are representative of the ACTUAL amount of air the system will be moving around the house. This means that the installing contractor may need to modify the CFM targets to match the installed equipment. If you're a rater, and you're working on a Version 3 ENERGY STAR project, be sure you keep these things in mind when you're measuring transfer grille sizes or critiquing a balancing report.

Here's a post I recently did on this topic. Check it out. I would love to hear your thoughts on the topic!

Tags: duct, manual-j, sizing

Views: 432

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Eve Dunham replied to Kim Tanner's discussion Facebook page targeting and privacy in the group Marketing Energy Efficiency
"I have used the targeted ads feature for age, location, etc. I have had moderate success with this.…"
16 hours ago
Home Energy Magazine's blog post was featured
yesterday
Hannah Finch posted a blog post
yesterday
Profile Iconpank and Carrie Sturrock joined Home Energy Pros
yesterday
tedkidd commented on Amber Vignieri's blog post Chicago Winter No Match for Retrofitted Logan Square Building
"This case study is an example of how hard it is simply to do a compelling case study. Everyone has…"
yesterday
B. M. Lubin posted an event
Thumbnail

GPRO Construction Management Class at USGBC-LI headquarters in Hauppauge, NY at USGBC-LI Headquarters

September 19, 2016 at 9am to September 20, 2016 at 2pm
Taught by industry experts using real-life classroom exercises, GPRO CM gives experienced building…See More
yesterday
B. M. Lubin is now a member of Home Energy Pros
Monday
Eric Kjelshus replied to tedkidd's discussion Dear DOE, PACE sucks - please fix or make it go away...
"Most HVAC system upgrade - change outs and attic seals-R-49 end up $20-30K   Most house -…"
Monday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service