The goal of conducting a load calc is finding the CORRECT load on a house.  How does one know if the final answer that Wrightsoft provides is correct or not?  The short answer is they don't - unless the check their work thoroughly and verify that pertinent project project information has been correctly specified in the model.  

 

Wrightsoft software doesn't know if a user has calculated ceiling, wall, or floor area incorrectly.  The program doesn't provide an error message if a user entered 24,000 btuh (2 tons!) for appliance loads as opposed to a more realistic 2,400 btu (2 tenths of a ton!).  The best way to figure out if a load is correct is to DOUBLE CHECK all areas, R-values, U-values, HTM's, and final loads.  

 

Below is the checkout process that I use on every load....  Feel free to add to it!

 

▪Is exact location of home known?  Does it match specified climate data?

▪Is orientation known?  Has it been verified with homeowner / builder?  Does it match orientation as specified in Wrightsoft?
▪Are level elevations and ceiling heights correct?
▪Have all rooms drawn on plans been drawn in Wrightsoft?  Is every room set to “include in load” (this can be changed on the properties sheet for each room).
▪Have all windows been drawn in Wrightsoft?  (Be careful, glitches in the Wrightsoft program sometimes cause windows to disappear).
▪Are wall areas correct for rooms with multiple ceiling heights?  Is roof area correct?  Is floor area / perimeter correct?  (remember, slab on grade construction is evaluated by the linear length of the perimeter).
▪Have floor, wall, and ceiling r-values been verified in the component construction report?  Do Heating and Cooling HTM’s make sense?
▪Has duct location, insulation, and infiltration been specified for  each room?
▪Are U and SHGC values correct?  Have these been verified on site, with builder, or with window rep?
▪Have window overhangs been specified?
▪Is glazing in the ballpark of 50% of the total cooling load?
▪Have occupant loads been included?
▪Have appliance loads been specified for kitchen, utility, office equipment, etc…?
▪Have infiltration and fireplace details been specified?
▪Has fresh air ventilation been specified?  ERV, HRV, supply only?
▪Are warning messages displayed in the load meter?
▪Is the square foot per ton ratio somewhere between 800 and 1400 (for a new home)?  Does this make sense for the house?

 

Tags: calculation, j, load, manual, manual j, training, wrightsoft

Views: 191

Replies to This Discussion

I found the drawing feature to be very frustrating to master so I mostly use the worksheet feature. I'm assuming the glitche is in the drawing board feature, is that correct?

 

Dale, yes, there are several drawing board related glitches that are basically all related to one setting: grid point snap spacing.  

Basically, the smaller the snap setting number is, the more likely glitches are.   Problems can range from windows disappearing and rooms resizing themselves to the load changing drastically with just the click of a mouse (while not changing anything in the drawing).  

Folks get tempted to set the snap points to increments of 3 inches or lower especially when drawing homes with walls on 45 degree angles.  However, If you leave the grid set to 12" increments and set the snap to 6" you will still be able to draw a very accurate footprint and should be glitch free!  

I've had my grid and snap set to 4" for a couple of years now, and the "glitches" rarely occur, if at all.
I'll occasionally set snap to 1" to accurately line up my backgrounds to the grid, then immediately go back to 4".
This was a the recommendation from my good buddy, Hamilton, with WS technical support.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Dennis Heidner replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"The press report really doesn't give enough information to clearly answer why  they are…"
2 hours ago
Edward Foskey commented on Edward Foskey's blog post Preparing to Update the Heat Pump
"Gustavo, Thanks for the input. I agree with you in that I will be waiting till my system's…"
4 hours ago
Gustavo Melo commented on Edward Foskey's blog post Preparing to Update the Heat Pump
"Any system that is out of warranty is really a coin toss as to whether it is financially better to…"
4 hours ago
Dennis Heidner replied to J.C. Martel's discussion Disasters & sustainable energy
"Such as Greensburg…"
7 hours ago
Tom Delconte commented on Edward Foskey's blog post Preparing to Update the Heat Pump
"Thanks, Ed, I get it now. I would just put in what my hvac guy tells me to put in: a $17,000…"
7 hours ago
Jim Gunshinan commented on Jim Gunshinan's blog post The Universe Is Made of Stories
"Hi Tom, I'm sorry you didn't think my blog post was helpful or appropriate. I'll…"
8 hours ago
Tom Delconte commented on Jim Gunshinan's blog post The Universe Is Made of Stories
"Whatever happened to separation of church, state, and scientific home building science? What would…"
9 hours ago
Craig Savage's video was featured

What is Building America

The U.S. Department of Energy's (DOE) Building America program is a source of innovation in residential building energy performance, durability, quality, aff...
12 hours ago
Jim Gunshinan's blog post was featured

The Universe Is Made of Stories

The late poet and political activist Muriel Rukeyser famously said, The Universe is made of…See More
13 hours ago
Jim Gunshinan posted a status
"New blog post, "The Universe Is Made of Stories""
13 hours ago
Jim Gunshinan posted a blog post

The Universe Is Made of Stories

The late poet and political activist Muriel Rukeyser famously said, The Universe is made of…See More
13 hours ago
Craig Savage posted videos
18 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service