The goal of conducting a load calc is finding the CORRECT load on a house.  How does one know if the final answer that Wrightsoft provides is correct or not?  The short answer is they don't - unless the check their work thoroughly and verify that pertinent project project information has been correctly specified in the model.  

 

Wrightsoft software doesn't know if a user has calculated ceiling, wall, or floor area incorrectly.  The program doesn't provide an error message if a user entered 24,000 btuh (2 tons!) for appliance loads as opposed to a more realistic 2,400 btu (2 tenths of a ton!).  The best way to figure out if a load is correct is to DOUBLE CHECK all areas, R-values, U-values, HTM's, and final loads.  

 

Below is the checkout process that I use on every load....  Feel free to add to it!

 

▪Is exact location of home known?  Does it match specified climate data?

▪Is orientation known?  Has it been verified with homeowner / builder?  Does it match orientation as specified in Wrightsoft?
▪Are level elevations and ceiling heights correct?
▪Have all rooms drawn on plans been drawn in Wrightsoft?  Is every room set to “include in load” (this can be changed on the properties sheet for each room).
▪Have all windows been drawn in Wrightsoft?  (Be careful, glitches in the Wrightsoft program sometimes cause windows to disappear).
▪Are wall areas correct for rooms with multiple ceiling heights?  Is roof area correct?  Is floor area / perimeter correct?  (remember, slab on grade construction is evaluated by the linear length of the perimeter).
▪Have floor, wall, and ceiling r-values been verified in the component construction report?  Do Heating and Cooling HTM’s make sense?
▪Has duct location, insulation, and infiltration been specified for  each room?
▪Are U and SHGC values correct?  Have these been verified on site, with builder, or with window rep?
▪Have window overhangs been specified?
▪Is glazing in the ballpark of 50% of the total cooling load?
▪Have occupant loads been included?
▪Have appliance loads been specified for kitchen, utility, office equipment, etc…?
▪Have infiltration and fireplace details been specified?
▪Has fresh air ventilation been specified?  ERV, HRV, supply only?
▪Are warning messages displayed in the load meter?
▪Is the square foot per ton ratio somewhere between 800 and 1400 (for a new home)?  Does this make sense for the house?

 

Tags: calculation, j, load, manual, manual j, training, wrightsoft

Views: 194

Replies to This Discussion

I found the drawing feature to be very frustrating to master so I mostly use the worksheet feature. I'm assuming the glitche is in the drawing board feature, is that correct?

 

Dale, yes, there are several drawing board related glitches that are basically all related to one setting: grid point snap spacing.  

Basically, the smaller the snap setting number is, the more likely glitches are.   Problems can range from windows disappearing and rooms resizing themselves to the load changing drastically with just the click of a mouse (while not changing anything in the drawing).  

Folks get tempted to set the snap points to increments of 3 inches or lower especially when drawing homes with walls on 45 degree angles.  However, If you leave the grid set to 12" increments and set the snap to 6" you will still be able to draw a very accurate footprint and should be glitch free!  

I've had my grid and snap set to 4" for a couple of years now, and the "glitches" rarely occur, if at all.
I'll occasionally set snap to 1" to accurately line up my backgrounds to the grid, then immediately go back to 4".
This was a the recommendation from my good buddy, Hamilton, with WS technical support.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Craig Savage commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Hello Tom Not sure if you are being sarcastic, but a serious answer would be that GE is selling…"
2 hours ago
Tom Delconte commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Craig: do you have a diagram of one that will run longer than one year? They don't really seem…"
3 hours ago
Cory Chovanec replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"All good points brought up. My advice is not to leave the lights. When you said halogen I think…"
4 hours ago
Jon Haehnel replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"The first 2 answers by Tom and Sean jive with my thinking and experience. Thank you Don for…"
5 hours ago
Tom Smith replied to Patrick Michaelyan's discussion Hot Upper Stories
"The most bang for your buck will come from airsealing the attic plane and sealing the…"
5 hours ago
John Rising replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"Hi Bachi, We have done many projects where we have installed boxes around recessed lights to…"
6 hours ago
Isaac Savage's event was featured
7 hours ago
Craig Savage's video was featured

What is a Heat Pump Water Heater

A simple animation describing how a heat pump water heater works
7 hours ago
Profile IconJeff Pello, Maxmam, Barbara Hall and 1 more joined Home Energy Pros
8 hours ago

John Abdo just added their location.
(via Member Map)

18 hours ago
Nick Helmholdt replied to Joshua Knittel's discussion Google Thermal View? in the group INFRARED THERMOGRAPHY USERS
"Any bets on how long it will take this company to land in court? A local energy efficiency group in…"
yesterday
Matthew Redmond posted a photo
yesterday

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service