Permalink Reply by Isaac Savage on July 6, 2012 at 6:28am The best way to determine what RSU does with scenarios like this is to do it both ways, then compare the reports to each other. The "component constructions" report (found in the Load section) will show you the gains losses attributed to each portion of your building. You could compare the two to each other here.
The general difference is that different roof types in RSU reference different construction assemblies in ACCA's Manual-J 8th Edition book. These "types" often have different U-values and assumed temperature differences, which means that they have varying HTM's (Heat Transfer Multipliers). For instance, a sloped ceiling with R38 cavity insulation is referencing group 18A, while a flat ceiling under vented attic references group 16B.
You'll also notice that anytime you're specifying a sloped roof surface using the room properties tab, Wrightsoft is making assumptions about the square footage of these surfaces. When you define a ceiling via the "room properties," flat ceilings use the rooms footprint as the sqft, while sloped ceilings assume a "typical" slope (somewhere around a 6/12, I believe). If your roof is steeper than 6/12, you should use the "ceiling tool" to draw a separate ceiling object on top of your room/building. This will allow you actually define the pitch of the roof, thus being more accurate.
Hope that helps!
Here's a recent post on how Manual-J can lead you to undersized ductwork, if you're not careful. I'd love to know what you think about it. Please comment!
Permalink Reply by Robert DV on July 6, 2012 at 10:53am Thanks for the information, I'll start running a few models and see what happens.
Permalink Reply by Brady Mills on July 6, 2012 at 6:56am In addition to Isaac's response below, if you're insulating the roof deck and encapsulating the attic, be sure to model the ductwork as being within building envelope. This will reduce energy losses through the ducts.
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Eric Kjelshus replied to Johnny Ritzo's discussion Selecting a Water Heater
Bachi Brunato replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Bachi Brunato's discussion was featured
Johnny Ritzo's discussion was featured
Tom Delconte's blog post was featured
Christopher Morin's blog post was featured
Mike Rogers's blog post was featured
Mike Rogers posted a blog post
Orvil D Boyer replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase© 2013 Created by Lawrence Berkeley National Laboratory.