Can anyone tell me how Wrtightsoft treat a a insulated roof deck compared to a insulated flat attic.

Views: 568

Replies to This Discussion

The best way to determine what RSU does with scenarios like this is to do it both ways, then compare the reports to each other. The "component constructions" report (found in the Load section) will show you the gains losses attributed to each portion of your building. You could compare the two to each other here.

The general difference is that different roof types in RSU reference different construction assemblies in ACCA's Manual-J 8th Edition book. These "types" often have different U-values and assumed temperature differences, which means that they have varying HTM's (Heat Transfer Multipliers). For instance, a sloped ceiling with R38 cavity insulation is referencing group 18A, while a flat ceiling under vented attic references group 16B.

You'll also notice that anytime you're specifying a sloped roof surface using the room properties tab, Wrightsoft is making assumptions about the square footage of these surfaces. When you define a ceiling via the "room properties," flat ceilings use the rooms footprint as the sqft, while sloped ceilings assume a "typical" slope (somewhere around a 6/12, I believe). If your roof is steeper than 6/12, you should use the "ceiling tool" to draw a separate ceiling object on top of your room/building. This will allow you actually define the pitch of the roof, thus being more accurate.

Hope that helps!

Here's a recent post on how Manual-J can lead you to undersized ductwork, if you're not careful. I'd love to know what you think about it. Please comment!

Thanks for the information, I'll start running a few models and see what happens.

In addition to Isaac's response below, if you're insulating the roof deck and encapsulating the attic, be sure to model the ductwork as being within building envelope. This will reduce energy losses through the ducts. 

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Paul Scheckel posted a blog post

Renewable Rant: Traditional Energy!

Why, when I open up a newsletter or market evaluation report about “traditional energy” markets, do…See More
5 hours ago
Rob Madden, Solar Home Broker's discussion was featured

Indoor Air Quality Monitors and Meters

I'm considering purchasing the AirAdvice for Homes indoor air quality monitor but it seems to have…See More
5 hours ago
Luis Hernandez's discussion was featured

ERV Configuration

Greetings everyone,     I did an energy audit on this new home that is too tight and needs…See More
5 hours ago
Kim Tanner's discussion was featured
5 hours ago
John Nicholas's discussion was featured

Slab Edge Insulation - A Side Thread to Melissa's Question

Melissa Baldridge inquired about installing slab edge insulation on a potential E-Star certified…See More
5 hours ago
Melissa Baldridge's discussion was featured

ENERGY STAR - Slab Insulation

Folks,Let's say I have a client who's building slab on grade and intending to certify E-STAR.  I'm…See More
6 hours ago
Sean Maxwell's discussion was featured

Blower Door Databases: ATTMA and Retrotec rCloud

Hi guys,We're pushing for blower door testing in the building code here in Australia and we think…See More
6 hours ago
Bob Blanchette's discussion was featured

Real World Ceiling Fan CFM

Has anybody done testing on delivered CFM of ceiling fans? Energy star has a test room where the…See More
6 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service