How are attic slopes modeled for foam insulation. When ever I've added a foamed slope I get a very low SIR with virtually no savings. What am I doing wrong?

Thanks

Views: 201

Replies to This Discussion

You are doing nothing wrong.  Modelling software does not properly reflect savings and I suspect 2 reasons: 

1 - Air sealing.  Foam provides insulation AND air sealing.  Once you play with this you start to see that the bigger direct energy benefit of foam is air sealing.  (Like a furnace with an ECM blower, you need to combine savings from multiple benefits).  So remember not to obsess on one improvement, step back and look at the whole impact.  

Oh - and smaller furnaces tend to model higher consumption, THAT has proven over and over to be TOTALLY inaccurate.  So be cautious relying on the software for design.  It's A tool, not THE tool. The most important tool is above your shoulders.

2 - Conditioned Space vs Unintentionally Conditioned Space.  When you redefine an attic the software sees the additional space as additional load.  In practice this space is an insulating buffer in and of itself.  Heat transfer from conditioned to unintentionally conditioned is very slow due to small delta.  And heat lost from unintentionally conditioned to outdoors is slower because IT has a smaller delta.  

I'm sorry this is not a very scientific explanation, but it's a conclusion arrived at by struggling with the same question you are asking.  In NY there is a "work around" that moves existing insulation to the surface being improved, then adding the foam to the existing surface.  

Remember, SIR is an absurdity.  Net cost is what people are really concerned about.  True up your model, use accurate fuel rates, and you can get pretty accurate net cost.  We've experienced realization of between .9 and 1.3, which feels about as close to dead nuts as one could expect given unforeseeable variables of behavior and weather.  

Ok , so put some of the cost for foam as an air sealing improvement, that I got. Unfortunately Home Performance w/ Energy Star requires an SIR of 1.01 and if the heating fuel is gas or electric it must pass a TRC of 1.

So I'll see how it all works out.

Thanks

In March they changed the rules.  Some improvements are "deemed" cost effective even if they are not cost effective.  (love that one, this thing has turned into a Frankenstein monster.)  

Then later they changed the rules again.  I believe Natural Gas requires SIR of .8

For approval I think air sealing can't be more than 49% of the cost.  

Combine machine gun "change notifications" that are then not followed up with updated Eligible Measures lists and everyone is confused.  Because challenge and thus cost of getting jobs approved has gone through the roof, I believe very few are even trying to run work not "deemed" effective.  

Last one I'm aware of is January 1, which it completely inaccurate.  Good luck!

Paul, since you are in NY, call Earl Hicks or Terry Clough at CSG. They'll tell you the work around.  

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

John Kaye posted a status
"Looking for contributing writer who know & understand EEM's"
12 minutes ago
John Kaye posted a status
"If you're a Realtor please email me for the next meet-up in San Gabriel, CA"
32 minutes ago
John Kaye posted a status
"I'd love to change the world, but I don't know what to do"
1 hour ago
Malcolm McKelvie replied to Alan Gindt's discussion Minneapolis Blower Door System for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"yes I would pay the delivery fee!"
Saturday
Alan Gindt replied to Alan Gindt's discussion Minneapolis Blower Door System for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Malcolm, If you want to pay delivery from USA we can talk. Otherwise no thanks."
Saturday
Malcolm McKelvie replied to Alan Gindt's discussion Minneapolis Blower Door System for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"How old is it? I assume it is in good working order? I'm interested in it but the price needs…"
Saturday
William H Nickerson replied to Kim Tanner's discussion Fantastic innovation
"So that's where you use those True Flow plates....."
Friday
Colin Genge updated an event
Thumbnail

Passive House Testing Webinar with Kevin Brennan of the Passive House Academy at Online

September 29, 2015 from 1pm to 2pm
Tests needed to qualify as a passive houseWhy we’re seeing an increase in PH buildingsBest…See More
Friday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service