Hi everyone!  

    I am learning TREAT, so perhaps this is too simple of a question for you guys but I am kind of stuck... when TREAT asked me about the building I choose attached, considering that one wall of the building is attached to the neighbor's house, but when I check walls, all of them are set up to the outside, and so far I have not found the way to change the setting for that attached wall. Just for me to learn, is that attached wall considered towards living space? -considering that there is a firewall separating both units. 

   Your help is greatly appreciated!

                                    Luis

Views: 163

Replies to This Discussion

Hi Luis,

This is a great question that points to a fundamental tenet of energy modeling: we don't worry about surfaces (walls, floors, etc.) where there's no energy transfer.  We assume that temperatures between adjacent units (or between conditioned bedrooms) are essentially the same, so UA∂T = 0 (the delta-T is zero), and there's no point in modeling the boundaries between them.

In other words, don't model walls between adjacent units, floors over conditioned spaces, ceilings under adjacent units, etc.  You've already discovered that TREAT doesn't give you the option to specify conditioned space adjacency. 

So, unlike detached single-family homes, that will have at minimum 4 walls, a floor, and a ceiling, attached units will often have fewer.  The most "minimal" case is an inside apartment unit on a middle floor, which might have only one surface, a wall, on the Walls/Surfaces screen.

I hope this helps clarify.  Remember, energy modeling is not the same as architectural modeling -- we don't need to worry about surfaces that are there for structural or aesthetic reasons, but that have no thermal transfer.

 - Ethan

Thanks for reply Ethan,  

    Just curious, exterior walls have negative energy transfer (energy loss), heat gain from sun exposure, wind, etc, so when modeled as adjacent to the outside, with the R value of all materials, there is a calculation of that lost energy. I am thinking that the firewall should be pretty energy neutral and so I was thinking it should be represented as wall adjacent to condition space; even though I understand that walls from inside the condition space are not modeled. But the other Townhouse is not part of this condition space....  maybe I am seeing this the wrong way...  hmmm, love building science!

              Luis

Exactly right, Luis.

The other unit is conditioned also, so there's negligible energy transfer between them, so the common walls don't provide a heating or cooling load, and there's no reason to enter them in the model.

And to simplify it, there's no way to enter them in TREAT.

If you created this model with the New Building Wizard, you probably have at least one wall that you just need to delete from the model -- the one that would have been adjacent to the other unit.

 - Ethan

Great Ethan!  

I am going to give it a try!!! I know that what you say makes sense... it just feel silly modeling 3 walls

I really appreciate your comments!

                      Luis 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Energy Center University posted an event

Better Buildings: Better Business Conferences at Crowne Plaza Chicago O'Hare Hotel & Conference Center and Kalahari Resort and Convention Center

February 26, 2015 to March 13, 2015
Better Buildings: Better Business ConferencesFebruary 26−27, 2015 │ Rosemont, ILMarch 11−13, 2015 │…See More
9 hours ago
Kris Grube added a discussion to the group Job Board
Thumbnail

Good Energy Retrofit, Portland, Or. Hiring Home Performance Salesperson.

Good Energy Retrofit is a small and focused, woman owned and operated, specialty residential…See More
13 hours ago
Benjamin Gromicko posted events
13 hours ago
Nate Adams joined Diane Chojnowski's group
Thumbnail

Hall of Shame

In this group, members share an array of images from the field, showing the kinds of issues…See More
14 hours ago
tedkidd commented on Diane Chojnowski's group Hall of Shame
"Give this thread a bump - here's my "bad" album and some of the…"
15 hours ago
Eric Kjelshus commented on Adam Swain's blog post Top Worst Crawl Space Insulation Ideas
"6) Radiant barrier- under the gravel is just a barrier but with holes each square inch its not a…"
15 hours ago
tedkidd replied to Luis Hernandez's discussion Distribution Efficiency and heating safety factor in TREAT in the group TREAT Software
"It is very common to find equipment grossly oversized. I mean 1.5 - 2x Manual J and 2-3x the size…"
15 hours ago
tedkidd replied to Luis Hernandez's discussion Basic Heat loss information in the group TREAT Software
"Luis,  Click "selected reports, energy savings and use, design heating and cooling…"
15 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service