Hi everyone!  

    I am learning TREAT, so perhaps this is too simple of a question for you guys but I am kind of stuck... when TREAT asked me about the building I choose attached, considering that one wall of the building is attached to the neighbor's house, but when I check walls, all of them are set up to the outside, and so far I have not found the way to change the setting for that attached wall. Just for me to learn, is that attached wall considered towards living space? -considering that there is a firewall separating both units. 

   Your help is greatly appreciated!

                                    Luis

Views: 156

Replies to This Discussion

Hi Luis,

This is a great question that points to a fundamental tenet of energy modeling: we don't worry about surfaces (walls, floors, etc.) where there's no energy transfer.  We assume that temperatures between adjacent units (or between conditioned bedrooms) are essentially the same, so UA∂T = 0 (the delta-T is zero), and there's no point in modeling the boundaries between them.

In other words, don't model walls between adjacent units, floors over conditioned spaces, ceilings under adjacent units, etc.  You've already discovered that TREAT doesn't give you the option to specify conditioned space adjacency. 

So, unlike detached single-family homes, that will have at minimum 4 walls, a floor, and a ceiling, attached units will often have fewer.  The most "minimal" case is an inside apartment unit on a middle floor, which might have only one surface, a wall, on the Walls/Surfaces screen.

I hope this helps clarify.  Remember, energy modeling is not the same as architectural modeling -- we don't need to worry about surfaces that are there for structural or aesthetic reasons, but that have no thermal transfer.

 - Ethan

Thanks for reply Ethan,  

    Just curious, exterior walls have negative energy transfer (energy loss), heat gain from sun exposure, wind, etc, so when modeled as adjacent to the outside, with the R value of all materials, there is a calculation of that lost energy. I am thinking that the firewall should be pretty energy neutral and so I was thinking it should be represented as wall adjacent to condition space; even though I understand that walls from inside the condition space are not modeled. But the other Townhouse is not part of this condition space....  maybe I am seeing this the wrong way...  hmmm, love building science!

              Luis

Exactly right, Luis.

The other unit is conditioned also, so there's negligible energy transfer between them, so the common walls don't provide a heating or cooling load, and there's no reason to enter them in the model.

And to simplify it, there's no way to enter them in TREAT.

If you created this model with the New Building Wizard, you probably have at least one wall that you just need to delete from the model -- the one that would have been adjacent to the other unit.

 - Ethan

Great Ethan!  

I am going to give it a try!!! I know that what you say makes sense... it just feel silly modeling 3 walls

I really appreciate your comments!

                      Luis 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Trip Smith replied to Hal Skinner's discussion What an RCC can do with no R- insulation in the walls.
"Wow, that's pretty incredible. I'm curious as to what other energy upgrades he did to the…"
15 minutes ago
Tom White's video was featured

Adaptive Thermostats - Western Cooling Efficiency Center Webinar

In buildings where variations in occupancy would fool a standard programmable thermostat, new adaptive thermostats have potential for significant energy savings
1 hour ago
Hal Skinner added a discussion to the group HVAC
Thumbnail

Old ductwork efficiency file

Allison,found the attached file on ductwork efficiency on an old CD I made.  Its definitely dated. …See More
6 hours ago
Hal Skinner posted a discussion

What an RCC can do with no R- insulation in the walls.

I have had a handful of folks on this forum tell me, in effect,  that an RCC can do a very good job…See More
8 hours ago
Trip Smith posted a discussion

Where to spend my marketing dollars?

Hey everyone, I'm a new home performance company owner. (Originally a general contractor who is…See More
9 hours ago
Profile IconManuel Gutierrez, Chris Baker, Sharon Cannizzo and 1 more joined Home Energy Pros
11 hours ago
Kevin Jordan replied to Kevin Jordan's discussion air infiltration total
"thanks.  but it was just an illustration of a hole 2x2 with money going out of that…"
13 hours ago
Tom White posted a video

Adaptive Thermostats Demonstration Results Installed at UC Davis 6/26/2014

In buildings where variations in occupancy would fool a standard programmable thermostat, new adaptive thermostats have potential for significant energy savi...
16 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service