Hi everyone!  

    I am learning TREAT, so perhaps this is too simple of a question for you guys but I am kind of stuck... when TREAT asked me about the building I choose attached, considering that one wall of the building is attached to the neighbor's house, but when I check walls, all of them are set up to the outside, and so far I have not found the way to change the setting for that attached wall. Just for me to learn, is that attached wall considered towards living space? -considering that there is a firewall separating both units. 

   Your help is greatly appreciated!

                                    Luis

Views: 162

Replies to This Discussion

Hi Luis,

This is a great question that points to a fundamental tenet of energy modeling: we don't worry about surfaces (walls, floors, etc.) where there's no energy transfer.  We assume that temperatures between adjacent units (or between conditioned bedrooms) are essentially the same, so UA∂T = 0 (the delta-T is zero), and there's no point in modeling the boundaries between them.

In other words, don't model walls between adjacent units, floors over conditioned spaces, ceilings under adjacent units, etc.  You've already discovered that TREAT doesn't give you the option to specify conditioned space adjacency. 

So, unlike detached single-family homes, that will have at minimum 4 walls, a floor, and a ceiling, attached units will often have fewer.  The most "minimal" case is an inside apartment unit on a middle floor, which might have only one surface, a wall, on the Walls/Surfaces screen.

I hope this helps clarify.  Remember, energy modeling is not the same as architectural modeling -- we don't need to worry about surfaces that are there for structural or aesthetic reasons, but that have no thermal transfer.

 - Ethan

Thanks for reply Ethan,  

    Just curious, exterior walls have negative energy transfer (energy loss), heat gain from sun exposure, wind, etc, so when modeled as adjacent to the outside, with the R value of all materials, there is a calculation of that lost energy. I am thinking that the firewall should be pretty energy neutral and so I was thinking it should be represented as wall adjacent to condition space; even though I understand that walls from inside the condition space are not modeled. But the other Townhouse is not part of this condition space....  maybe I am seeing this the wrong way...  hmmm, love building science!

              Luis

Exactly right, Luis.

The other unit is conditioned also, so there's negligible energy transfer between them, so the common walls don't provide a heating or cooling load, and there's no reason to enter them in the model.

And to simplify it, there's no way to enter them in TREAT.

If you created this model with the New Building Wizard, you probably have at least one wall that you just need to delete from the model -- the one that would have been adjacent to the other unit.

 - Ethan

Great Ethan!  

I am going to give it a try!!! I know that what you say makes sense... it just feel silly modeling 3 walls

I really appreciate your comments!

                      Luis 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Mark Wozniak posted a status
"I am looking for energy efficiency software training in Massachusetts."
1 hour ago
daniel manriquez replied to Trip Smith's discussion Starting a Home Weatherization Business. Considering it...
"Here's a contractor perspective on incentives. Not that I agree with all of it, but its a good…"
1 hour ago
Rick Wertheim joined Kyle Brown's group
Thumbnail

Wrightsoft - Manual J / Manual D

If you use Wrightsoft to calculate loads or design ducts, you likely have questions.  Get answers…See More
2 hours ago
Rick Wertheim joined Leslie McDowell, BPI's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
2 hours ago
Casey Gesell posted a video

How Dr. Energy Saver Helped Me Grow My Home Services Business | Dealer Testimonials

http://www.drenergysaverdealerships.com | 1-877-479-3637 Real Dr. Energy Saver dealers explain how the proven marketing, sales and training programs allowed ...
3 hours ago
Casey Gesell commented on Tom White's video
Thumbnail

Ducts in an Attic

"Hi Tom, Thank you for sharing our Dr. Energy Saver video!"
4 hours ago
Diane Chojnowski posted a discussion

EEBA 2014 Conference Presentations

EEBA has posted many of the presentations from their conference in St. Louis last week. Check them…See More
4 hours ago
Profile IconJames Tucker, Dean Brewer and CPB Mechanical joined Home Energy Pros
4 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service