    I am learning TREAT, so perhaps this is too simple of a question for you guys but I am kind of stuck... when TREAT asked me about the building I choose attached, considering that one wall of the building is attached to the neighbor's house, but when I check walls, all of them are set up to the outside, and so far I have not found the way to change the setting for that attached wall. Just for me to learn, is that attached wall considered towards living space? -considering that there is a firewall separating both units. 

   Your help is greatly appreciated!

                                    Luis

Views: 167

Replies to This Discussion

Hi Luis,

This is a great question that points to a fundamental tenet of energy modeling: we don't worry about surfaces (walls, floors, etc.) where there's no energy transfer.  We assume that temperatures between adjacent units (or between conditioned bedrooms) are essentially the same, so UA∂T = 0 (the delta-T is zero), and there's no point in modeling the boundaries between them.

In other words, don't model walls between adjacent units, floors over conditioned spaces, ceilings under adjacent units, etc.  You've already discovered that TREAT doesn't give you the option to specify conditioned space adjacency. 

So, unlike detached single-family homes, that will have at minimum 4 walls, a floor, and a ceiling, attached units will often have fewer.  The most "minimal" case is an inside apartment unit on a middle floor, which might have only one surface, a wall, on the Walls/Surfaces screen.

I hope this helps clarify.  Remember, energy modeling is not the same as architectural modeling -- we don't need to worry about surfaces that are there for structural or aesthetic reasons, but that have no thermal transfer.

 - Ethan

Thanks for reply Ethan,  

    Just curious, exterior walls have negative energy transfer (energy loss), heat gain from sun exposure, wind, etc, so when modeled as adjacent to the outside, with the R value of all materials, there is a calculation of that lost energy. I am thinking that the firewall should be pretty energy neutral and so I was thinking it should be represented as wall adjacent to condition space; even though I understand that walls from inside the condition space are not modeled. But the other Townhouse is not part of this condition space....  maybe I am seeing this the wrong way...  hmmm, love building science!

              Luis

Exactly right, Luis.

The other unit is conditioned also, so there's negligible energy transfer between them, so the common walls don't provide a heating or cooling load, and there's no reason to enter them in the model.

And to simplify it, there's no way to enter them in TREAT.

If you created this model with the New Building Wizard, you probably have at least one wall that you just need to delete from the model -- the one that would have been adjacent to the other unit.

 - Ethan

Great Ethan!  

I am going to give it a try!!! I know that what you say makes sense... it just feel silly modeling 3 walls

I really appreciate your comments!

                      Luis 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Kim Tanner posted a video

Zone Pressure Diagnostics with Rick Karg

Join Rick Karg, President of Residential Energy Dynamics, for this TEC hosted Zone Pressure Diagnostics (ZPD) webinar. Since its introduction around 1990, ZP...
27 minutes ago
Mary Desilva posted a blog post

Energy Saving Home Remedies

The quest for a cleaner earth is not one man’s job. It’s something all of us have to work for. In…See More
1 hour ago
Positive Energy posted videos
2 hours ago
Profile IconErnesto , Positive Energy, Cristy Kraus and 3 more joined Home Energy Pros
3 hours ago
Hal Skinner replied to Hal Skinner's discussion 'YGRENE' super fund for energy upgrade financing
"Thanks Susan.  It is appreciated."
20 hours ago
Adin Maynard commented on Corbett Lunsford's video
Thumbnail

Beyond Blower Doors: Zonal Pressure Testing

"Great video. Your approach of simplifying the reading as X/50 = percent leaking to outside (with…"
21 hours ago
Chris Dorsi posted an event
Thumbnail

2015 Habitat X Summer National Conference at Big Sky Resort

July 21, 2015 to July 23, 2015
The 2015 Habitat X Summer National Conference will take place at Big Sky Resort, just down the road…See More
23 hours ago
Royce Gleason posted a status
"The passion to learn and gain more advanced energy efficiency techniques, news, videos and much more from home energy pros across the globe."
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service