I got into a discussion with a college the other day about testing the attic connection to the house.

When the house is depressurized to -50pa wrt outside, and the attic wrt house is -49pa, isn’t the attic more “outside” then “inside”? When the house was depressurized to -50pa I also looked at the attic wrt outside, and got just -2pa. My understanding is that if the Blower Door is putting -50pa on the house interior, and the attic only goes -2pa wrt the outside, the ceiling is pretty darn tight.

Any thoughts on this? We talked zonal pressures until my head got foggy. Any other ways to describe this testing process would be greatly appreciated. I may even get a lunch out of it if I can explain it better!

Views: 412

Replies to This Discussion

If I am understanding this correctly when the house is at 50Pa relative to outside and the attic is at 2Pa relative to outside then there is not much connection between those two zones. The 2Pa in the attic could even be due to stack. Sounds like they have a very tight ceiling.

 

Silvie Votrubova, Retrotec


Here are a couple of things to remember when measuring zonalpressures.  First is that you want tomeasure the change in pressure caused by the Blower Door, so you will need torecord a baseline attic to outside pressure. Secondly zonal pressures do not tell you the size of the leakage betweenthe house and the attic.  The zonalpressure tells you the leakage ratio between the house and attic compared tothe leakage between the attic and the outside. For example, if the attic to outside number is 25 pa, then the hole sizebetween the house and attic is the same as between the attic and outside.  If the attic to outside number is 2 pa, thenthe ratio is 1 to 8.  It is possible tohave a attic to outside zonal pressure of 2 pa on one house and 25 pa onanother house and have an equal hole size between the house and attic.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Eric Kjelshus replied to Beverly Lerch's discussion Fireplace drafts
"A brick chimney will take some 70,000 BTU's to heat up to draft on a fireplace.   A…"
6 hours ago
Ed Voytovich replied to Beverly Lerch's discussion Fireplace drafts
"Our solution was to install a Lopi Answer wood burning insert that vents directly through a metal…"
13 hours ago
kevin mack is now a member of Home Energy Pros
16 hours ago
Jim Gunshinan's blog post was featured

A Healthy Home and a Healthy Bottom Line

There has been a lot of interest of late in the weatherization and broader home performance…See More
yesterday
Jonathan Beers commented on Home Energy Magazine's blog post Natural Gas is Becoming Less Attractive
"The carbon intensity of electricity use (lbs. of CO2/MWh) varies a lot from region to region. For…"
yesterday
Diane Chojnowski posted events
yesterday
Home Energy Magazine posted a blog post

Natural Gas is Becoming Less Attractive

The United States and Canada have been fortunate to have access to natural gas for space heating,…See More
yesterday
Jim Gunshinan posted a blog post

A Healthy Home and a Healthy Bottom Line

There has been a lot of interest of late in the weatherization and broader home performance…See More
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service