I got into a discussion with a college the other day about testing the attic connection to the house.

When the house is depressurized to -50pa wrt outside, and the attic wrt house is -49pa, isn’t the attic more “outside” then “inside”? When the house was depressurized to -50pa I also looked at the attic wrt outside, and got just -2pa. My understanding is that if the Blower Door is putting -50pa on the house interior, and the attic only goes -2pa wrt the outside, the ceiling is pretty darn tight.

Any thoughts on this? We talked zonal pressures until my head got foggy. Any other ways to describe this testing process would be greatly appreciated. I may even get a lunch out of it if I can explain it better!

Views: 378

Replies to This Discussion

If I am understanding this correctly when the house is at 50Pa relative to outside and the attic is at 2Pa relative to outside then there is not much connection between those two zones. The 2Pa in the attic could even be due to stack. Sounds like they have a very tight ceiling.

 

Silvie Votrubova, Retrotec


Here are a couple of things to remember when measuring zonalpressures.  First is that you want tomeasure the change in pressure caused by the Blower Door, so you will need torecord a baseline attic to outside pressure. Secondly zonal pressures do not tell you the size of the leakage betweenthe house and the attic.  The zonalpressure tells you the leakage ratio between the house and attic compared tothe leakage between the attic and the outside. For example, if the attic to outside number is 25 pa, then the hole sizebetween the house and attic is the same as between the attic and outside.  If the attic to outside number is 2 pa, thenthe ratio is 1 to 8.  It is possible tohave a attic to outside zonal pressure of 2 pa on one house and 25 pa onanother house and have an equal hole size between the house and attic.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Rob Madden, Solar Home Broker replied to Rob Madden, Solar Home Broker's discussion Indoor Air Quality Monitors and Meters
"Awesome respnose...thanks for your insight!"
19 hours ago
Zane Goff replied to Rob Madden, Solar Home Broker's discussion Indoor Air Quality Monitors and Meters
"We use the air advice quick test device and I'd recommend it for the depth of home…"
20 hours ago
Amber Vignieri posted a status
"#Solar does WHAT?! #SunShot busts myths aboutt #SolarRealEstate http://energy.gov/eere/articles/5-common-myths-about-residential-solar"
20 hours ago
Profile Iconnaryking, Rob Hoehn, Hannah Wood and 2 more joined Home Energy Pros
23 hours ago
Chris Laumer-Giddens posted a blog post

Building with Rocks, Rocks. Check out the Drying Potential

Building with Rocks, Rocks! Check out the Drying Potential.Check this out! This 24" x 48" x 2"…See More
yesterday
Evan Mills's blog post was featured

Looking Back and Looking Forward: Home Energy Pros at 5 and 5000

Over the past five years, the Home Energy Pros social network has grown from a twinkle in our eyes…See More
yesterday
Eve Dunham joined Diane Chojnowski's group
Thumbnail

News & Announcements

Share your news and announcements with the community in this group.To post news or an announcement,…See More
yesterday
Eve Dunham joined Tom White's group
Thumbnail

Weatherization

Share your concerns and successes as a weatherization professional, or information for this…See More
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service