It is very important that as professionals we can agree on what we are testing.  Carbon Monoxide (CO) is one of the most confusing issues.

First, BPI's prime directive is health and safety first.  Monitoring the ambient CO during analysis is clear.  A personal CO monitor or a combustion analyzer can be used to monitor ambient CO.  Use the CO value on the analyzer for this.

Second, combustion analyzers can be used to measure the combustion byproduct CO in incomplete combustion.  To accomplish that, the probe of the analyzer must be sampling the undiluted gases in the flue.  Where you locate the probe depends on the appliance you are testing, and most of the combustion analyzers provide information on how to accomplish that.

Third, most combustion analyzers provide two CO values: CO and CO-AF or CO Air Free. CO-AF is the value that BPI is looking for for combustion testing.  (If in doubt, record the CO, the CO-AF, and the O2 levels.)  If the analyzer does not provide an O2 value or a CO-AF value, use the CO value and note that on the report.

CO-AF is a value calculated by the analyzer that subtracts the oxygen from the CO reading.  The analyzer should be initiated in clean air with a oxygen level close to 20.9%.  The formula is:

                                              CO ppm x ((20.9)/(20.9 – 02))

A furnace with a CO level of 2 and oxygen of 8.9% would have a calculated CO-AF reading of 3.5.

A furnace with a CO level of 46 and oxygen of 3.2% would have a calculated CO-AF reading of 54.3.

Fourth, since the CO-AF value will be higher than the CO value, it is important to get the right CO value to begin with and that means inserting a NOx scrubber in the path to the analyzer - either using an analyzer that has one built in or adding it to the hose.

 

If we can agree on the use of these values in this way, then I think we will be much further along in providing consistent, reliable results.

Views: 442

Replies to This Discussion

Paul,  Thank you for writing this clear description of the issue and the testing protocol.  Question:  What is the Action Level for CO-AF for natural draft appliances and gas ranges, and what is the recommended Action?  Thank you, Tamasin

Paul,

Does this mean that if the air's O2 percentage is exactly 20.9 that the calculated CO-AF reading is infinite?                       Or that if the O2 percentage is greater than 20.9 that CO-AF is negative?  What do these numbers indicate in more practical/intuitive terms?  Thanks.

Curious where you found that BPI is looking for CO-AF.  I've always been told BPI is looking for CO not air free CO.  Would love to know where the clarification is as to which CO reading BPI's action levels are for.

In the BA Standards under review.  You'll find what is planned.  These standards are not what folks are expected to know, follow, and test under however.  We're just looking ahead.

Thanks, Tamasin.  Unfortunately the description of CO measurement in the present BPI BA Standard uses the terminology of "CO as measured" which is not a value that appears on a combustion analyzer screen.  It's CO or some form of CO Air Free like COAF.  So the question is which one are they referring to?   I vote for COAF because I KNOW that much of the time the analyzer probe is not in the right place, sampling CO that has not been diluted.  Also, the COAF value tells us not only how much CO is in the sample but also how much oxygen which tells us something about how well the appliance is functioning which is basically the point of the exercise.  Chris, if you get to a location with those oxygen levels, I would love to hear the results.  What can I tell you?  I'm not enough of a scientist to create that formula.

Thanks Paul.  I haven't seen >20.9% oxygen levels in a home, I'm just trying to understand the combustion chemistry that the formula is based on, and what exactly COAF is measuring that CO isn't, and why that is important.  

Okay, so based on this it looks like COAF is meant to correct for how much available O2 is available in the combustion air relative to how much the appliance requires for complete combustion.  The formula you gave essentially removes the excess O2 in the flue gasses, allowing you to measure the CO concentration as if there was zero excess O2 (that it, if it were undiluted).  And this allows an apples-to-apples comparison of combustion efficiency/CO production between appliances having different combustion air requirements?  Maybe this explanation could be useful for other people (like me) who are new to all this.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

David Eakin commented on Elisa Wood's blog post Momentum builds for energy efficiency...but is the wolf at the door?
"Here's a very recent article on Green Building Advisor that reinforces the issues to…"
6 hours ago
Home Energy Magazine posted blog posts
8 hours ago
Egr renovation posted a status
"of course he is in paris but works around europe http://ning.it/16KrbS7"
11 hours ago
Egr renovation posted a status
"i just find a good photogrpahe for your master piece http://www.armanimage.com"
11 hours ago

Tom Mallard just added their location.
(via Member Map)

yesterday
Profile IconDon Hughes, Julian Sark, James Hatheway and 4 more joined Home Energy Pros
yesterday
Meagan Foster posted events
yesterday
Meagan Foster updated an event

EnergyLogic's RaterFest! at Black Hawk, CO

September 13, 2013 at 10am to September 15, 2013 at 12pm
Join us for one of the best home energy conferences available!  This retreat will provide…See More
yesterday
Meagan Foster updated an event

Homes 401: Green Rater Training at Berthoud, CO

June 25, 2013 to June 26, 2013
This highly interactive workshop builds upon the material presented in the online course, further…See More
yesterday
Meagan Foster updated an event

HERS Rater Training - Online at Online

July 1, 2013 to July 26, 2013
NEW - our great RESNET HERS Rater online training is now completely self-paced, so you can start at…See More
yesterday
Meagan Foster updated an event

BPI Building Analyst Training - Online at Online

June 3, 2013 to June 28, 2013
Join the EnergyLogic Academy for our BPI BA online training - we just went to a completely open…See More
yesterday

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service