It is very important that as professionals we can agree on what we are testing.  Carbon Monoxide (CO) is one of the most confusing issues.

First, BPI's prime directive is health and safety first.  Monitoring the ambient CO during analysis is clear.  A personal CO monitor or a combustion analyzer can be used to monitor ambient CO.  Use the CO value on the analyzer for this.

Second, combustion analyzers can be used to measure the combustion byproduct CO in incomplete combustion.  To accomplish that, the probe of the analyzer must be sampling the undiluted gases in the flue.  Where you locate the probe depends on the appliance you are testing, and most of the combustion analyzers provide information on how to accomplish that.

Third, most combustion analyzers provide two CO values: CO and CO-AF or CO Air Free. CO-AF is the value that BPI is looking for for combustion testing.  (If in doubt, record the CO, the CO-AF, and the O2 levels.)  If the analyzer does not provide an O2 value or a CO-AF value, use the CO value and note that on the report.

CO-AF is a value calculated by the analyzer that subtracts the oxygen from the CO reading.  The analyzer should be initiated in clean air with a oxygen level close to 20.9%.  The formula is:

                                              CO ppm x ((20.9)/(20.9 – 02))

A furnace with a CO level of 2 and oxygen of 8.9% would have a calculated CO-AF reading of 3.5.

A furnace with a CO level of 46 and oxygen of 3.2% would have a calculated CO-AF reading of 54.3.

Fourth, since the CO-AF value will be higher than the CO value, it is important to get the right CO value to begin with and that means inserting a NOx scrubber in the path to the analyzer - either using an analyzer that has one built in or adding it to the hose.

 

If we can agree on the use of these values in this way, then I think we will be much further along in providing consistent, reliable results.

Views: 918

Replies to This Discussion

Paul,  Thank you for writing this clear description of the issue and the testing protocol.  Question:  What is the Action Level for CO-AF for natural draft appliances and gas ranges, and what is the recommended Action?  Thank you, Tamasin

Paul,

Does this mean that if the air's O2 percentage is exactly 20.9 that the calculated CO-AF reading is infinite?                       Or that if the O2 percentage is greater than 20.9 that CO-AF is negative?  What do these numbers indicate in more practical/intuitive terms?  Thanks.

Curious where you found that BPI is looking for CO-AF.  I've always been told BPI is looking for CO not air free CO.  Would love to know where the clarification is as to which CO reading BPI's action levels are for.

In the BA Standards under review.  You'll find what is planned.  These standards are not what folks are expected to know, follow, and test under however.  We're just looking ahead.

Thanks, Tamasin.  Unfortunately the description of CO measurement in the present BPI BA Standard uses the terminology of "CO as measured" which is not a value that appears on a combustion analyzer screen.  It's CO or some form of CO Air Free like COAF.  So the question is which one are they referring to?   I vote for COAF because I KNOW that much of the time the analyzer probe is not in the right place, sampling CO that has not been diluted.  Also, the COAF value tells us not only how much CO is in the sample but also how much oxygen which tells us something about how well the appliance is functioning which is basically the point of the exercise.  Chris, if you get to a location with those oxygen levels, I would love to hear the results.  What can I tell you?  I'm not enough of a scientist to create that formula.

Thanks Paul.  I haven't seen >20.9% oxygen levels in a home, I'm just trying to understand the combustion chemistry that the formula is based on, and what exactly COAF is measuring that CO isn't, and why that is important.  

Okay, so based on this it looks like COAF is meant to correct for how much available O2 is available in the combustion air relative to how much the appliance requires for complete combustion.  The formula you gave essentially removes the excess O2 in the flue gasses, allowing you to measure the CO concentration as if there was zero excess O2 (that it, if it were undiluted).  And this allows an apples-to-apples comparison of combustion efficiency/CO production between appliances having different combustion air requirements?  Maybe this explanation could be useful for other people (like me) who are new to all this.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Amber Vignieri posted a status
"In the market for a #solar home? We're bringing you improved solar #MLS listings. http://bit.ly/2auldQ8"
16 hours ago
Tom White's video was featured

CalCERTS Plenum Pressure Matching

This video describes how to perform plenum pressure matching to measure system airflow.
16 hours ago
Rob Madden, Solar Home Broker replied to Rob Madden, Solar Home Broker's discussion Indoor Air Quality Monitors and Meters
"Awesome respnose...thanks for your insight!"
yesterday
Zane Goff replied to Rob Madden, Solar Home Broker's discussion Indoor Air Quality Monitors and Meters
"We use the air advice quick test device and I'd recommend it for the depth of home…"
yesterday
Amber Vignieri posted a status
"#Solar does WHAT?! #SunShot busts myths aboutt #SolarRealEstate http://energy.gov/eere/articles/5-common-myths-about-residential-solar"
yesterday
Profile Iconnaryking, Rob Hoehn, Hannah Wood and 2 more joined Home Energy Pros
yesterday
Chris Laumer-Giddens posted a blog post

Building with Rocks, Rocks. Check out the Drying Potential

Building with Rocks, Rocks! Check out the Drying Potential.Check this out! This 24" x 48" x 2"…See More
yesterday
Evan Mills's blog post was featured

Looking Back and Looking Forward: Home Energy Pros at 5 and 5000

Over the past five years, the Home Energy Pros social network has grown from a twinkle in our eyes…See More
Tuesday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service