Hey there,

 

First post on HEP!  Exciting times, indeed.  A question on ACH and N-factors for multifamily:

 

LBNL’s N-factor converts between pressure induced (i.e.- fan measured) and natural air infiltration rates.  The well known N-factor charts max out at 3 story building heights.  In the past, I used these N-factors daily when working on single family homes. 

 

Any idea if there are equivalent N-factors that can be used (or calculated….) for mid/high rise buildings?

 

I would prefer to deal with a natural ACH rate rather than an ACH50, or whatever else.  Any help would be much appreciated.  

 

Thanks a ton,

 

-Grant 

Tags: ACH, factor, n

Views: 352

Replies to This Discussion

Hi Grant,

I checked with our tech support department and here' what they had to say.

The short answer is no. The wind and stack coefficients that are used in the n-factor calculations are empirically determined from many experiments. There is simply not enough data to extrapolate results for taller buildings. It would be recommended to use ACH50, or permeability, or any other accepted result for larger buildings. ACH natural was meant for houses.

Silvie

 

 

Grant,

 

ACHn is irrelevant in a building big enough to have any continuous venilation -- the fans completely change the pressure regime in the building. Many MFBs over three stories (at least in my part of the world) have some sort of continuous ventilation.

Further, the n-factor is fairly local and fairly specific, since it has to take into account stack effect AND wind, across all the weather conditions in the entire year. So the calculation is quite complex, and the n-factor can be significantly different for cities in the same state, with similar HDDs. 

So, when LBL did the original tables, they did them only for low-rise housing. They were (probably) calculated largely to support weatherization work -- and that was entirely focused on single-family, low-rise buildings.

Many mid-rise and high-rise models will accept input based on ACH50 or CFM50. So, if you've actually measured the building, you can use that as a proxy. If not, you just gotta guess, and see what happens when you true-up to actual energy use.

In my part of the world, 1 CFM50 per ft2 of ABOVE GRADE wood-frame envelope is a good guess (even if the building has single-wythe brick cladding). Make it about half that for a masonry-wall building. I don't know WHAT the right number is for buildings in your part of the world.

Thanks folks!

In a past life, I had always used the following formula for determining potential energy savings for reducing infiltration:

 

Q= (1.08 * ACH REDUCTION * [volume/60] * 24 * HDD)/ Boiler Efficiency

Q = annual heat loss due to infiltration

 

Any different formula's recommended for mid/high rise buildings?

 

Thanks.

Hi Grant. This equation should be fine, as a CFM of outside air costs the same to heat/cool regardless of building type. However, I'd recommend considering the cooling costs (sensible + latent) of the associated air leakage as well. Depending on where you are, it could add quite a bit of savings to the pot.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Craig Foley posted an event
Thumbnail

NESEA BuildingEnergy '15 at Seaport World Trade Center, Boston

March 4, 2015 from 10:30am to 12:30pm
High-Performance, Green Homes in Residential Real EstateInstructor Craig Foley will present three…See More
yesterday
Casey Gesell posted a video

ThermalDry® Insulated Floor Decking!

Larry Janesky, owner and founder of Dr. Energy Saver is once again On the Job insulating and finishing a basement in the northeast – and introducing a brand new insulation product: ThermalDry Insulated Floor Decking. ThermalDry Floor Decking was…
yesterday
Profile IconBergen Heat, Travis Thom and Amita Singh joined Home Energy Pros
Friday
Tom White's video was featured

U.S. Department of Education Webinar for HVACR Educators

Rebroadcast from On April 30, 2013 Sharon Miller and Robin Utz of the U.S. Department of Education conducted a one hour webinar for HVACR educators to provide them firsthand information from Washington. Highlights include: * A blueprint to revise…
Friday
Tom White posted a video

U.S. Department of Education Addresses HVACR Educators 4-30-2013

Rebroadcast from On April 30, 2013 Sharon Miller and Robin Utz of the U.S. Department of Education conducted a one hour webinar for HVACR educators to provid...
Friday
Nate Adams's discussion was featured
Friday
Bud Poll replied to Bud Poll's discussion CO poisoning in Yarmouth Maine
"Hi Chad, I sure would like to hear the follow-up on what caused the CO issue down there.  As…"
Friday
Chad Mcaulife replied to Bud Poll's discussion CO poisoning in Yarmouth Maine
"I got a call yesterday from a homeowner who had a direct vent furnace installed a year ago and she…"
Friday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service