Hey there,
First post on HEP! Exciting times, indeed. A question on ACH and N-factors for multifamily:
LBNL’s N-factor converts between pressure induced (i.e.- fan measured) and natural air infiltration rates. The well known N-factor charts max out at 3 story building heights. In the past, I used these N-factors daily when working on single family homes.
Any idea if there are equivalent N-factors that can be used (or calculated….) for mid/high rise buildings?
I would prefer to deal with a natural ACH rate rather than an ACH50, or whatever else. Any help would be much appreciated.
Thanks a ton,
-Grant
Hi Grant,
I checked with our tech support department and here' what they had to say.
The short answer is no. The wind and stack coefficients that are used in the n-factor calculations are empirically determined from many experiments. There is simply not enough data to extrapolate results for taller buildings. It would be recommended to use ACH50, or permeability, or any other accepted result for larger buildings. ACH natural was meant for houses.
Silvie
Grant,
ACHn is irrelevant in a building big enough to have any continuous venilation -- the fans completely change the pressure regime in the building. Many MFBs over three stories (at least in my part of the world) have some sort of continuous ventilation.
Further, the n-factor is fairly local and fairly specific, since it has to take into account stack effect AND wind, across all the weather conditions in the entire year. So the calculation is quite complex, and the n-factor can be significantly different for cities in the same state, with similar HDDs.
So, when LBL did the original tables, they did them only for low-rise housing. They were (probably) calculated largely to support weatherization work -- and that was entirely focused on single-family, low-rise buildings.
Many mid-rise and high-rise models will accept input based on ACH50 or CFM50. So, if you've actually measured the building, you can use that as a proxy. If not, you just gotta guess, and see what happens when you true-up to actual energy use.
In my part of the world, 1 CFM50 per ft2 of ABOVE GRADE wood-frame envelope is a good guess (even if the building has single-wythe brick cladding). Make it about half that for a masonry-wall building. I don't know WHAT the right number is for buildings in your part of the world.
Permalink Reply by Grant Salmon on December 1, 2011 at 11:04am Thanks folks!
In a past life, I had always used the following formula for determining potential energy savings for reducing infiltration:
Q= (1.08 * ACH REDUCTION * [volume/60] * 24 * HDD)/ Boiler Efficiency
Q = annual heat loss due to infiltration
Any different formula's recommended for mid/high rise buildings?
Thanks.
Permalink Reply by Isaac Savage on February 12, 2012 at 8:35am Hi Grant. This equation should be fine, as a CFM of outside air costs the same to heat/cool regardless of building type. However, I'd recommend considering the cooling costs (sensible + latent) of the associated air leakage as well. Depending on where you are, it could add quite a bit of savings to the pot.
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Craig Savage commented on Craig Savage's video
Tom Delconte commented on Craig Savage's video
Cory Chovanec replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Jon Haehnel replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
Tom Smith replied to Patrick Michaelyan's discussion Hot Upper Stories
John Rising replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Isaac Savage's event was featured
Craig Savage's video was featured
Nick Helmholdt replied to Joshua Knittel's discussion Google Thermal View? in the group INFRARED THERMOGRAPHY USERS© 2013 Created by Lawrence Berkeley National Laboratory.