Hey there,

 

First post on HEP!  Exciting times, indeed.  A question on ACH and N-factors for multifamily:

 

LBNL’s N-factor converts between pressure induced (i.e.- fan measured) and natural air infiltration rates.  The well known N-factor charts max out at 3 story building heights.  In the past, I used these N-factors daily when working on single family homes. 

 

Any idea if there are equivalent N-factors that can be used (or calculated….) for mid/high rise buildings?

 

I would prefer to deal with a natural ACH rate rather than an ACH50, or whatever else.  Any help would be much appreciated.  

 

Thanks a ton,

 

-Grant 

Tags: ACH, factor, n

Views: 235

Replies to This Discussion

Hi Grant,

I checked with our tech support department and here' what they had to say.

The short answer is no. The wind and stack coefficients that are used in the n-factor calculations are empirically determined from many experiments. There is simply not enough data to extrapolate results for taller buildings. It would be recommended to use ACH50, or permeability, or any other accepted result for larger buildings. ACH natural was meant for houses.

Silvie

 

 

Grant,

 

ACHn is irrelevant in a building big enough to have any continuous venilation -- the fans completely change the pressure regime in the building. Many MFBs over three stories (at least in my part of the world) have some sort of continuous ventilation.

Further, the n-factor is fairly local and fairly specific, since it has to take into account stack effect AND wind, across all the weather conditions in the entire year. So the calculation is quite complex, and the n-factor can be significantly different for cities in the same state, with similar HDDs. 

So, when LBL did the original tables, they did them only for low-rise housing. They were (probably) calculated largely to support weatherization work -- and that was entirely focused on single-family, low-rise buildings.

Many mid-rise and high-rise models will accept input based on ACH50 or CFM50. So, if you've actually measured the building, you can use that as a proxy. If not, you just gotta guess, and see what happens when you true-up to actual energy use.

In my part of the world, 1 CFM50 per ft2 of ABOVE GRADE wood-frame envelope is a good guess (even if the building has single-wythe brick cladding). Make it about half that for a masonry-wall building. I don't know WHAT the right number is for buildings in your part of the world.

Thanks folks!

In a past life, I had always used the following formula for determining potential energy savings for reducing infiltration:

 

Q= (1.08 * ACH REDUCTION * [volume/60] * 24 * HDD)/ Boiler Efficiency

Q = annual heat loss due to infiltration

 

Any different formula's recommended for mid/high rise buildings?

 

Thanks.

Hi Grant. This equation should be fine, as a CFM of outside air costs the same to heat/cool regardless of building type. However, I'd recommend considering the cooling costs (sensible + latent) of the associated air leakage as well. Depending on where you are, it could add quite a bit of savings to the pot.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Craig Savage commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Hello Tom We are working with A.O. Smith, GE and Stiebel Eltron on a Building America task to…"
1 hour ago
Tom Delconte commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Craig: I was serious, since my propane price jumped from .98 to 1.85! according to everyone the GE…"
2 hours ago
Ben Jacobs replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"I think that government support for good ideas results in major benefits over the long haul. Please…"
2 hours ago
Craig Savage commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Hello Tom Not sure if you are being sarcastic, but a serious answer would be that GE is selling…"
5 hours ago
Tom Delconte commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Craig: do you have a diagram of one that will run longer than one year? They don't really seem…"
5 hours ago
Cory Chovanec replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"All good points brought up. My advice is not to leave the lights. When you said halogen I think…"
6 hours ago
Jon Haehnel replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"The first 2 answers by Tom and Sean jive with my thinking and experience. Thank you Don for…"
7 hours ago
Tom Smith replied to Patrick Michaelyan's discussion Hot Upper Stories
"The most bang for your buck will come from airsealing the attic plane and sealing the…"
8 hours ago
John Rising replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"Hi Bachi, We have done many projects where we have installed boxes around recessed lights to…"
8 hours ago
Isaac Savage's event was featured
10 hours ago
Craig Savage's video was featured

What is a Heat Pump Water Heater

A simple animation describing how a heat pump water heater works
10 hours ago
Profile IconJeff Pello, Maxmam, Barbara Hall and 1 more joined Home Energy Pros
10 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service