Hey there,

 

First post on HEP!  Exciting times, indeed.  A question on ACH and N-factors for multifamily:

 

LBNL’s N-factor converts between pressure induced (i.e.- fan measured) and natural air infiltration rates.  The well known N-factor charts max out at 3 story building heights.  In the past, I used these N-factors daily when working on single family homes. 

 

Any idea if there are equivalent N-factors that can be used (or calculated….) for mid/high rise buildings?

 

I would prefer to deal with a natural ACH rate rather than an ACH50, or whatever else.  Any help would be much appreciated.  

 

Thanks a ton,

 

-Grant 

Tags: ACH, factor, n

Views: 442

Replies to This Discussion

Hi Grant,

I checked with our tech support department and here' what they had to say.

The short answer is no. The wind and stack coefficients that are used in the n-factor calculations are empirically determined from many experiments. There is simply not enough data to extrapolate results for taller buildings. It would be recommended to use ACH50, or permeability, or any other accepted result for larger buildings. ACH natural was meant for houses.

Silvie

 

 

Grant,

 

ACHn is irrelevant in a building big enough to have any continuous venilation -- the fans completely change the pressure regime in the building. Many MFBs over three stories (at least in my part of the world) have some sort of continuous ventilation.

Further, the n-factor is fairly local and fairly specific, since it has to take into account stack effect AND wind, across all the weather conditions in the entire year. So the calculation is quite complex, and the n-factor can be significantly different for cities in the same state, with similar HDDs. 

So, when LBL did the original tables, they did them only for low-rise housing. They were (probably) calculated largely to support weatherization work -- and that was entirely focused on single-family, low-rise buildings.

Many mid-rise and high-rise models will accept input based on ACH50 or CFM50. So, if you've actually measured the building, you can use that as a proxy. If not, you just gotta guess, and see what happens when you true-up to actual energy use.

In my part of the world, 1 CFM50 per ft2 of ABOVE GRADE wood-frame envelope is a good guess (even if the building has single-wythe brick cladding). Make it about half that for a masonry-wall building. I don't know WHAT the right number is for buildings in your part of the world.

Thanks folks!

In a past life, I had always used the following formula for determining potential energy savings for reducing infiltration:

 

Q= (1.08 * ACH REDUCTION * [volume/60] * 24 * HDD)/ Boiler Efficiency

Q = annual heat loss due to infiltration

 

Any different formula's recommended for mid/high rise buildings?

 

Thanks.

Hi Grant. This equation should be fine, as a CFM of outside air costs the same to heat/cool regardless of building type. However, I'd recommend considering the cooling costs (sensible + latent) of the associated air leakage as well. Depending on where you are, it could add quite a bit of savings to the pot.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Ed Minch commented on Tom White's video
Thumbnail

Measured Home Performance: Assessment with a Infrared Camera

"I find it best to scan one time before the Blower Door is used to check for insulation and…"
yesterday
Profile IconLarry Kinney and teplie_poly joined Home Energy Pros
Saturday
Dan Antonioli replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"Okay, a couple of things. The 1.0 kW per square meter reference is only under the most ideal lab…"
Saturday
Hans Joachim Preiss replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"Dan, Let me attempt to compare apples with apples: My solar thermal system is located in…"
Friday
Dan Antonioli replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"Hi Hans, I don't know where you're located but where I am a 2.5 kw pv system costs closer…"
Friday
Hans Joachim Preiss replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"I use the combination of solar PV and heatpump water heaters in the vast majority of net-zero…"
Friday
Amber Vignieri posted a blog post
Friday
William Zwack added a discussion to the group Job Board
Thumbnail

Residental Energy Specialist: Washington, DC (or possibly telework)

Position Summary: CSRA Incorporated is searching for a Sr. Residential Building Energy Efficiency…See More
Friday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service