Hey there,

 

First post on HEP!  Exciting times, indeed.  A question on ACH and N-factors for multifamily:

 

LBNL’s N-factor converts between pressure induced (i.e.- fan measured) and natural air infiltration rates.  The well known N-factor charts max out at 3 story building heights.  In the past, I used these N-factors daily when working on single family homes. 

 

Any idea if there are equivalent N-factors that can be used (or calculated….) for mid/high rise buildings?

 

I would prefer to deal with a natural ACH rate rather than an ACH50, or whatever else.  Any help would be much appreciated.  

 

Thanks a ton,

 

-Grant 

Tags: ACH, factor, n

Views: 484

Replies to This Discussion

Hi Grant,

I checked with our tech support department and here' what they had to say.

The short answer is no. The wind and stack coefficients that are used in the n-factor calculations are empirically determined from many experiments. There is simply not enough data to extrapolate results for taller buildings. It would be recommended to use ACH50, or permeability, or any other accepted result for larger buildings. ACH natural was meant for houses.

Silvie

 

 

Grant,

 

ACHn is irrelevant in a building big enough to have any continuous venilation -- the fans completely change the pressure regime in the building. Many MFBs over three stories (at least in my part of the world) have some sort of continuous ventilation.

Further, the n-factor is fairly local and fairly specific, since it has to take into account stack effect AND wind, across all the weather conditions in the entire year. So the calculation is quite complex, and the n-factor can be significantly different for cities in the same state, with similar HDDs. 

So, when LBL did the original tables, they did them only for low-rise housing. They were (probably) calculated largely to support weatherization work -- and that was entirely focused on single-family, low-rise buildings.

Many mid-rise and high-rise models will accept input based on ACH50 or CFM50. So, if you've actually measured the building, you can use that as a proxy. If not, you just gotta guess, and see what happens when you true-up to actual energy use.

In my part of the world, 1 CFM50 per ft2 of ABOVE GRADE wood-frame envelope is a good guess (even if the building has single-wythe brick cladding). Make it about half that for a masonry-wall building. I don't know WHAT the right number is for buildings in your part of the world.

Thanks folks!

In a past life, I had always used the following formula for determining potential energy savings for reducing infiltration:

 

Q= (1.08 * ACH REDUCTION * [volume/60] * 24 * HDD)/ Boiler Efficiency

Q = annual heat loss due to infiltration

 

Any different formula's recommended for mid/high rise buildings?

 

Thanks.

Hi Grant. This equation should be fine, as a CFM of outside air costs the same to heat/cool regardless of building type. However, I'd recommend considering the cooling costs (sensible + latent) of the associated air leakage as well. Depending on where you are, it could add quite a bit of savings to the pot.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Paul Scheckel posted a blog post

Renewable Rant: Traditional Energy!

Why, when I open up a newsletter or market evaluation report about “traditional energy” markets, do…See More
1 hour ago
Rob Madden, Solar Home Broker's discussion was featured

Indoor Air Quality Monitors and Meters

I'm considering purchasing the AirAdvice for Homes indoor air quality monitor but it seems to have…See More
2 hours ago
Luis Hernandez's discussion was featured

ERV Configuration

Greetings everyone,     I did an energy audit on this new home that is too tight and needs…See More
2 hours ago
Kim Tanner's discussion was featured
2 hours ago
John Nicholas's discussion was featured

Slab Edge Insulation - A Side Thread to Melissa's Question

Melissa Baldridge inquired about installing slab edge insulation on a potential E-Star certified…See More
2 hours ago
Melissa Baldridge's discussion was featured

ENERGY STAR - Slab Insulation

Folks,Let's say I have a client who's building slab on grade and intending to certify E-STAR.  I'm…See More
3 hours ago
Sean Maxwell's discussion was featured

Blower Door Databases: ATTMA and Retrotec rCloud

Hi guys,We're pushing for blower door testing in the building code here in Australia and we think…See More
3 hours ago
Bob Blanchette's discussion was featured

Real World Ceiling Fan CFM

Has anybody done testing on delivered CFM of ceiling fans? Energy star has a test room where the…See More
3 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service