Hi All

Wanted to get the opinion of an expert.

Attached is a photo of a customer's window.... as you can see there is a large cold spot above the window... Here's my opinion..am I right?

The large horizontal cold spot is thermal bridging from the double 2x6 or 8 top plate.

DO you agree?  The customer's pain was condensation on the windows.  WIndows were well installed with minimum leakage. The house was very tight, which I believe is the problem..not this.

Tags: ir, windows

Views: 544

Replies to This Discussion

Master shows!

John, Thanks for the review in Home Energy 101.  Sometimes, as auditors, we get so enamored with the technology, we forget the basics.  Comments like this, keep my feet firmly on the ground, and improved my audit results.

 

 

Matthew, this is not thermal bridging or else it would look like the wall studs and the window header. This is a result of running the blower door in a tight house where air coming in at the soffitt vents is pulled into the building through penetrations in the drywall. Take the same shot before the blower door has been run and it will look a lot more normal.

This is not thermal bridging and it has nothing to do with the blower door.  This is the ceiling plane meeting the wall plane, and this is thin insulation at this area combined with possibley a slight breeze blowing or convection causing cold air to ride up under the first couple of inches of attic insulation.  The very dark spot every 2 feet corresponds to the roof trusses/rafters and the week insulation adjacent to them. In the mid-Atlantic we are required to install hurricane clips - metal clips that hold the trusses/rafter down to the top plates.  We see the conducted cold from the metal as a dark spot every 2 feet even if it is not connected between with a dark area.  The blower door would have caused the cold air to come down the wall/ceiling joint into the wall - but this is not the case, and thermal bridging would have made all the studs show as much as the top plates.

Ed Minch

Slight Breeze?  He said the bower door was running. 

Chad

As I said:

"The blower door would have caused the cold air to come down the wall/ceiling joint into the wall - but this is not the case, and thermal bridging would have made all the studs show as much as the top plates."

There is no connection of this area to the blower door through the attic.  The only possible connection is from the bottom of the wall at the baseboard or through receptacles, etc in the wall, then up through the wall to the open wall/ceiling joint where the cold areas are.  If this were happening, the cold would extend down as "icy fingers" into the wall below, but it is not.

Ed

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Evan Mills replied to Sandra K. Adomatis, SRA's discussion Green Mortgage Appraisal Roundtable
"Would love see your slides, but the AI site requires login.  Can you post them here or email…"
6 hours ago
Colin Genge posted a blog post

What needs to be done to get builders to follow Code for duct and envelope leakage?

“Have you been ripped off for $100,000 by your builder?  Let us help you get what you paid for! …See More
12 hours ago
Green Training USA posted an event
Thumbnail

Proctor’s Without Borders at Online

July 29, 2015 to August 7, 2015
Complete your training at your own pace and take exams when you want and where you want. No…See More
20 hours ago
Gar Swaffar commented on Gar Swaffar's blog post Cost of using a BPI QCI?
"Ip.s., I would presume there will be a difference between the Left Coast and nearly everywhere else."
yesterday
Gar Swaffar posted a blog post

Cost of using a BPI QCI?

I'd like to find out if there is a consensus on a rule of thumb cost of a QCI onsite for…See More
yesterday
Gar Swaffar is now a member of Home Energy Pros
yesterday
Colin Genge posted an event

Infiltration and Duct Leakage with BPI at Online

July 30, 2015 from 1pm to 2pm
Blower door and duct test requirementsCalculating resultsCertification optionsTest preparation and…See More
yesterday
Stacy Hunt posted an event

Volunteers needed for the upcoming U.S. Department of Energy Solar Decathlon in Irvine, CA at Orange County Great Park

October 8, 2015 at 11am to October 18, 2015 at 7pm
Volunteer for the upcoming U.S. Department of Energy Solar Decathlon 2015, taking place Oct. 8-18…See More
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service