Hi All

Wanted to get the opinion of an expert.

Attached is a photo of a customer's window.... as you can see there is a large cold spot above the window... Here's my opinion..am I right?

The large horizontal cold spot is thermal bridging from the double 2x6 or 8 top plate.

DO you agree?  The customer's pain was condensation on the windows.  WIndows were well installed with minimum leakage. The house was very tight, which I believe is the problem..not this.

Tags: ir, windows

Views: 689

Replies to This Discussion

Master shows!

John, Thanks for the review in Home Energy 101.  Sometimes, as auditors, we get so enamored with the technology, we forget the basics.  Comments like this, keep my feet firmly on the ground, and improved my audit results.

 

 

Matthew, this is not thermal bridging or else it would look like the wall studs and the window header. This is a result of running the blower door in a tight house where air coming in at the soffitt vents is pulled into the building through penetrations in the drywall. Take the same shot before the blower door has been run and it will look a lot more normal.

This is not thermal bridging and it has nothing to do with the blower door.  This is the ceiling plane meeting the wall plane, and this is thin insulation at this area combined with possibley a slight breeze blowing or convection causing cold air to ride up under the first couple of inches of attic insulation.  The very dark spot every 2 feet corresponds to the roof trusses/rafters and the week insulation adjacent to them. In the mid-Atlantic we are required to install hurricane clips - metal clips that hold the trusses/rafter down to the top plates.  We see the conducted cold from the metal as a dark spot every 2 feet even if it is not connected between with a dark area.  The blower door would have caused the cold air to come down the wall/ceiling joint into the wall - but this is not the case, and thermal bridging would have made all the studs show as much as the top plates.

Ed Minch

Slight Breeze?  He said the bower door was running. 

Chad

As I said:

"The blower door would have caused the cold air to come down the wall/ceiling joint into the wall - but this is not the case, and thermal bridging would have made all the studs show as much as the top plates."

There is no connection of this area to the blower door through the attic.  The only possible connection is from the bottom of the wall at the baseboard or through receptacles, etc in the wall, then up through the wall to the open wall/ceiling joint where the cold areas are.  If this were happening, the cold would extend down as "icy fingers" into the wall below, but it is not.

Ed

RSS

Welcome to Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

Blogs

First-Ever Comprehensive National Standard Practice Manual is Updated Guidebook for Energy Efficiency Cost-Benefit Analysis

Posted by Home Energy Magazine on May 23, 2017 at 9:30am 0 Comments

The first-ever comprehensive national guide for utility-funded energy efficiency programs is now available to help utilities, regulators and other interested…

Continue

New Video and Course on Solar PV in Real Estate

Posted by Amber Vignieri on May 16, 2017 at 11:31am 0 Comments

Real estate professionals who understand the basics of solar and know how to market the benefits of an installation will have a market edge. For most real estate agents and appraisers, assessing the value of solar is a new…

Continue

What Happen to Energy Upgrade California?

Posted by Will johnson on May 15, 2017 at 11:43am 0 Comments

Energy Upgrade California offers rebates up to $6,500.00 in SDGE territory.  Up to $4,500 in other territories.  Unfortunately they don't/won't promote it.  I can't get straight candid answers from the contractors supporting the program.  Only…

Continue

Latest Activity

robert jones posted a status
"I have energy auditing equipment for sale. I'm in the 518. 518-209-5912"
19 hours ago
Home Energy Magazine posted a blog post
19 hours ago
Home Energy Magazine posted a video

Gary Nelson, The Energy Conservatory

Gary Nelson- Home Energy Magazine's "Legends of Home Performance" video series. Interviews with pioneer pathfinders of energy and water efficiency.
19 hours ago
Kelly Vaughn posted a blog post
20 hours ago

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service