Hi All

Wanted to get the opinion of an expert.

Attached is a photo of a customer's window.... as you can see there is a large cold spot above the window... Here's my opinion..am I right?

The large horizontal cold spot is thermal bridging from the double 2x6 or 8 top plate.

DO you agree?  The customer's pain was condensation on the windows.  WIndows were well installed with minimum leakage. The house was very tight, which I believe is the problem..not this.

Tags: ir, windows

Views: 682

Replies to This Discussion

Master shows!

John, Thanks for the review in Home Energy 101.  Sometimes, as auditors, we get so enamored with the technology, we forget the basics.  Comments like this, keep my feet firmly on the ground, and improved my audit results.

 

 

Matthew, this is not thermal bridging or else it would look like the wall studs and the window header. This is a result of running the blower door in a tight house where air coming in at the soffitt vents is pulled into the building through penetrations in the drywall. Take the same shot before the blower door has been run and it will look a lot more normal.

This is not thermal bridging and it has nothing to do with the blower door.  This is the ceiling plane meeting the wall plane, and this is thin insulation at this area combined with possibley a slight breeze blowing or convection causing cold air to ride up under the first couple of inches of attic insulation.  The very dark spot every 2 feet corresponds to the roof trusses/rafters and the week insulation adjacent to them. In the mid-Atlantic we are required to install hurricane clips - metal clips that hold the trusses/rafter down to the top plates.  We see the conducted cold from the metal as a dark spot every 2 feet even if it is not connected between with a dark area.  The blower door would have caused the cold air to come down the wall/ceiling joint into the wall - but this is not the case, and thermal bridging would have made all the studs show as much as the top plates.

Ed Minch

Slight Breeze?  He said the bower door was running. 

Chad

As I said:

"The blower door would have caused the cold air to come down the wall/ceiling joint into the wall - but this is not the case, and thermal bridging would have made all the studs show as much as the top plates."

There is no connection of this area to the blower door through the attic.  The only possible connection is from the bottom of the wall at the baseboard or through receptacles, etc in the wall, then up through the wall to the open wall/ceiling joint where the cold areas are.  If this were happening, the cold would extend down as "icy fingers" into the wall below, but it is not.

Ed

RSS

Discussion Forum

Expert Eye Needed

Started by Matthew P. Last reply by Ed Minch Nov 15, 2014. 17 Replies

Google Thermal View?

Started by Joshua Knittel. Last reply by tedkidd May 31, 2013. 4 Replies

Infrared Image - What is it?

Started by Fluke Thermal Imaging. Last reply by Dale Sherman Apr 26, 2012. 6 Replies

Timber Home with no effective air barrier

Started by Davide Lanzoni. Last reply by Sean Lintow Sr Apr 11, 2012. 1 Reply

Videos

  • Add Videos
  • View All

Latest Activity

Danielle Sass Byrnett liked Diane Chojnowski's blog post Don MacOdrum receives BPI's 2017 Tony Woods Award!
21 minutes ago
Home Energy Magazine's video was featured

#TinyLab Tour Ends: Lessons Learned

Grace and Corbett Lunsford are happy to not be moving every week, like they did on the Proof Is Possible Tour! Hear some of the ups and downs, and what they ...
42 minutes ago
Diane Chojnowski posted a blog post
1 hour ago
Profile IconB.J. Cassell, Scott Gigrich, Saint Xavier and 3 more joined Home Energy Pros
2 hours ago
Horace Douglas Hunt, Jr. posted a status
"#Hers rating system or @_BPI_ and #DOE rating system? Whats your coice? #HVAC #Energy @resnetus #resnet #HomePerformance"
3 hours ago
Horace Douglas Hunt, Jr. posted a status
"#Blowerdoor testing provides an insight into how leaky your home is and where its pulling #contaminants from.If you dont test you dont know!"
3 hours ago
Horace Douglas Hunt, Jr. posted a status
"#Homeperformance = #Control... Home performance diagnostics and repairs can give you the control over your environment you seek! #HVAC #IAQ"
3 hours ago
Horace Douglas Hunt, Jr. replied to Steve's discussion Too many BTU's. Too much horsepower?
"If your space was designed for a 1.5 ton system, i find it hard to believe that you would consider…"
3 hours ago

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service