Hi All

Wanted to get the opinion of an expert.

Attached is a photo of a customer's window.... as you can see there is a large cold spot above the window... Here's my opinion..am I right?

The large horizontal cold spot is thermal bridging from the double 2x6 or 8 top plate.

DO you agree?  The customer's pain was condensation on the windows.  WIndows were well installed with minimum leakage. The house was very tight, which I believe is the problem..not this.

Tags: ir, windows

Views: 637

Replies to This Discussion

Master shows!

John, Thanks for the review in Home Energy 101.  Sometimes, as auditors, we get so enamored with the technology, we forget the basics.  Comments like this, keep my feet firmly on the ground, and improved my audit results.

 

 

Matthew, this is not thermal bridging or else it would look like the wall studs and the window header. This is a result of running the blower door in a tight house where air coming in at the soffitt vents is pulled into the building through penetrations in the drywall. Take the same shot before the blower door has been run and it will look a lot more normal.

This is not thermal bridging and it has nothing to do with the blower door.  This is the ceiling plane meeting the wall plane, and this is thin insulation at this area combined with possibley a slight breeze blowing or convection causing cold air to ride up under the first couple of inches of attic insulation.  The very dark spot every 2 feet corresponds to the roof trusses/rafters and the week insulation adjacent to them. In the mid-Atlantic we are required to install hurricane clips - metal clips that hold the trusses/rafter down to the top plates.  We see the conducted cold from the metal as a dark spot every 2 feet even if it is not connected between with a dark area.  The blower door would have caused the cold air to come down the wall/ceiling joint into the wall - but this is not the case, and thermal bridging would have made all the studs show as much as the top plates.

Ed Minch

Slight Breeze?  He said the bower door was running. 

Chad

As I said:

"The blower door would have caused the cold air to come down the wall/ceiling joint into the wall - but this is not the case, and thermal bridging would have made all the studs show as much as the top plates."

There is no connection of this area to the blower door through the attic.  The only possible connection is from the bottom of the wall at the baseboard or through receptacles, etc in the wall, then up through the wall to the open wall/ceiling joint where the cold areas are.  If this were happening, the cold would extend down as "icy fingers" into the wall below, but it is not.

Ed

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Amber Vignieri posted a blog post
2 hours ago
Evan Mills posted a blog post

Looking Back and Looking Forward: Home Energy Pros at 5 and 5000

Over the past five years, the Home Energy Pros social network has grown from a twinkle in our eyes…See More
3 hours ago
tedkidd replied to Diane Chojnowski's discussion Poll: How confident do you feel about the future of home performance?
"Thank you for sharing this trend! Full disclosure, I did NOT ask Bob to post that! If you have 2…"
3 hours ago
Bob Blanchette replied to Diane Chojnowski's discussion Poll: How confident do you feel about the future of home performance?
"I see fixed monthly grid charges continuing to increase while cost per therm/kwh/gallon remain…"
3 hours ago
Quinn Korzeniecki posted a discussion

Vent Cap Systems and SENSIT Technologies Products Added to BPI Product List

The Building Performance Institute, Inc. (BPI) has recognized four new products in its …See More
6 hours ago
Simon joined Diane Chojnowski's group
Thumbnail

Online Training

Online training coursesIf you provide ongoing online training for home performance or…See More
yesterday
Simon added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Wanted - Blower and door frame kit for Minneapolis system

Hi everyone,I'm new to this line of work and have bought some equipment (Minneapolis blower door…See More
yesterday
Simon replied to Steve Mann's discussion TEC Blower Door Frame in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi, I'm interested, but could you send to UK?,I'd pay shipping of course. My email is :-…"
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service