Hi All
Wanted to get the opinion of an expert.
Attached is a photo of a customer's window.... as you can see there is a large cold spot above the window... Here's my opinion..am I right?
The large horizontal cold spot is thermal bridging from the double 2x6 or 8 top plate.
DO you agree? The customer's pain was condensation on the windows. WIndows were well installed with minimum leakage. The house was very tight, which I believe is the problem..not this.
Permalink Reply by John Nicholas on March 17, 2011 at 7:54pm Good start! What is the direction of the wall? Time of day? Sun loading. Delta T? Is the Blower Door running or if it is after the Blower Door test, how long?
Permalink Reply by Matthew P on March 18, 2011 at 4:06am
Permalink Reply by John Nicholas on March 18, 2011 at 4:46am If you were 11 AM on a south wall, and there was no external shading (another building) then you had solar loading.
I hate it when my images come out like this. The focus point appears to be Finial on the Lamp. That puts the wall out of focus.
I would agree the colder areas along the ceiling line are more to do with construction techniques and thermal bridging then they represent a problem you can deal with. Is the wall insulated? FG batts? If so, it appears they may have pulled away, in the rounded corners, or perhaps are installed compressed, or out of contact with the drywall. This is harder because of the focus.
Let's see what the others have to say.
Permalink Reply by Henry Borysewicz on March 18, 2011 at 9:11am
Permalink Reply by Rod Hoff on March 18, 2011 at 10:17am
Permalink Reply by David Meiland on March 18, 2011 at 5:25pm
Permalink Reply by Matthew P on March 18, 2011 at 5:58pm
Permalink Reply by t hardy on March 24, 2011 at 11:43am Could you send me a copy of file with this pic as well?
Thanks.
Permalink Reply by David Meiland on March 24, 2011 at 11:45am Matthew, I never received the file... david at meiland dot com
Thanks
Permalink Reply by David Meiland on March 24, 2011 at 7:57pm Same image in the Ironbow palette....
My guess is that if you took off the drywall, you would find fiberglass batts jammed into the stud bays and not in contact with the drywall at the top. The double top plate is cold!

Permalink Reply by t hardy on March 24, 2011 at 8:42pm It's hard to tell from just the one pic - do you have a shot before the BD was run??
Since the BD was running, if it's the top floor or equivalent, I could make a case for no baffling and poor or no alignment of the thermal envelope - in other words wind washing at the eaves all to heck and gone.
What does master J. Snell say?
Thanks for the "master" plug! I hope I can meet expectations. Jeezopeets! Anyway, it certainly appears to be a header. There may be an air space associated with it. Did you take other images before you depressurized with a blower door? That might help show you if it is just an uninsulated header or if there is also an air leakage pathway around it. There certainly seems to be air leakage along the top plate! What is the source of that?
I'd suggest your saying "The house was very tight, which I believe is the problem" is actually not accurate. The house has humidity too high for the temperature conditions. Either reduce RH or increase window temperature to reduce condensation. I often see condensation in bedrooms (people like them cold) and sometimes there is no easy fix. It would not surprise me to hear there is staining or even mold on the wall along the cold top plate.
What is the RH? Anything between 30-50% is "normal," but if the bedroom is colder (it appears it is), RH will continue to increase there. I'd suggest you check for obvious sources of moisture—poorly vented dryer, bathroom vent fans, crawlspace with no ground cover, etc.—to see if moisture can be reduced at the source. If not, consider adding a continuous, low-velocity vent fan or heat exchanger.
One last thing, when you need to view your IR image, I'd suggest you not have picture-in-picture. Reformat it in the software so it is FULL IR and you'll often have an easier time seeing what is going on. Very easy to change it back and forth to other fusion modes. And, if I can be just a bit picky (:-)), work on sharpening focus/image freezing. So speaks The Master!
THANKS!
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Nick Helmholdt replied to Joshua Knittel's discussion Google Thermal View? in the group INFRARED THERMOGRAPHY USERS
Paul Scheckel posted a blog post
Tom Delconte posted a blog post
Joe Huang posted a discussion
Joseph Lamy commented on Jim Gunshinan's blog post The Universe Is Made of Stories
J.C. Martel replied to J.C. Martel's discussion Disasters & sustainable energy© 2013 Created by Lawrence Berkeley National Laboratory.