I am participating in a DOE Better Buildings  program in southwest Ohio that is in its infancy stages. During discussions while setting the technical standards of the program, the topic of proper sizing vs 2 stage equipment came up.  Many of the "seasoned HVAC contractors" involved in this conversation including the director of operations for the program adamantly were advocating for the standard to be" 2 stage trumps sizing".  Meaning if you cant find a 2 stage piece of equipment in the correct size as specified by your manual j then go to the next available size.  (Most 2 stage equipment is not available in 1/2 ton sizes.)   For reasons discussed in this and other threads, I was in favor of forgoing the 2 stage piece of equipment for the piece of equipment closer to the proper size.  I was hoping I could get some input from this thread on reasoning for or against up-sizing in this situation especially taking in to consideration our geographic location.

Views: 66

Replies to This Discussion

Keep in mind that the MAJORITY of operation time is going to be at part-load conditions. More than likely, the larger unit running on its first-stage would be more appropriately sized, for more operating hours, that the "correctly" sized machine in a single-stage model (it would only be properly sized under the design conditions).

 

Manual-S states that the equipment selected must be able to satisfy both the sensible and latent loads. If you're wanting the benefit of a 2-stage machine (lower power consumption during part load conditions, ability to zone more effectively, etc.), you should just pick the smallest size that is available which also meets the design load. The first stage will handle the part-load conditions with the occasional help from the second stage. If an aggressive Manual-J is done, and the house effectively manages moisture, this should not be problematic.

 

If you use a program like Wrightsoft, you can look at the BIN data reports to see the number of estimated operating hours on first/second stages to help you make a decision like this.

Will you be installing heat pump only, with electric back-up or will the units be dual fuel - heat pump with gas back-up?

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Bryce Cramer joined Leslie McDowell, BPI's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
2 hours ago
Bryce Cramer replied to Mike Kandel's discussion June's Stump the Chump: What's Wrong with this Picture? in the group Building Performance Institute (BPI)
"Key is this was done in warm weather. The back wall of the room was also uninsulated, but the lower…"
2 hours ago
James Hatheway added a discussion to the group Job Board
Thumbnail

Quality Assurance Verification Specialist - Little Rock, Arkansas

CLEAResult (clearesult.com) is looking for a QA Verification professional who wants to leverage…See More
4 hours ago
Profile IconJames Hatheway and Mike Wallis joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
4 hours ago
Profile IconJames Hatheway, Malcolm Gray, Perry Ning and 2 more joined Home Energy Pros
4 hours ago
tedkidd commented on Mike Rogers's blog post HOMES Act introduced with Bi-Partisan Sponsorship
"% savings programs suck.  Ask the folks in CA.  When your incentive structure pits…"
6 hours ago
Emilian Karchev joined Michael Stuart's group
Thumbnail

INFRARED THERMOGRAPHY USERS

This group is dedicated to knowledge sharing and discussion of infrared thermography for building…See More
12 hours ago
Emilian Karchev replied to Tim Marlett's discussion Removal of bad smells from mold contaminated attic
"I think to have mold, then there is moisture and is good if you can look at and make a…"
12 hours ago
Jack Sadyak commented on Jack Sadyak's blog post Why Getting a Quantum Heat Pump is a Better Choice?
"Hello Tom, Don't worry I will let you know everything you can contact me at Heat Pumps…"
14 hours ago
Dennis Heidner commented on Macie Melendez's blog post Passive Proponent—Q&A with Brandon Weiss
"Don't forget Build America program from…"
17 hours ago
John Wes joined James Sayers's group
Thumbnail

Marketing Energy Efficiency

Sharing ideas, tools and examples of promoting energy efficiency to consumersSee More
18 hours ago
John Wes joined Tom White's group
Thumbnail

Weatherization

Share your concerns and successes as a weatherization professional, or information for this…See More
18 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service