I am participating in a DOE Better Buildings  program in southwest Ohio that is in its infancy stages. During discussions while setting the technical standards of the program, the topic of proper sizing vs 2 stage equipment came up.  Many of the "seasoned HVAC contractors" involved in this conversation including the director of operations for the program adamantly were advocating for the standard to be" 2 stage trumps sizing".  Meaning if you cant find a 2 stage piece of equipment in the correct size as specified by your manual j then go to the next available size.  (Most 2 stage equipment is not available in 1/2 ton sizes.)   For reasons discussed in this and other threads, I was in favor of forgoing the 2 stage piece of equipment for the piece of equipment closer to the proper size.  I was hoping I could get some input from this thread on reasoning for or against up-sizing in this situation especially taking in to consideration our geographic location.

Views: 60

Replies to This Discussion

Keep in mind that the MAJORITY of operation time is going to be at part-load conditions. More than likely, the larger unit running on its first-stage would be more appropriately sized, for more operating hours, that the "correctly" sized machine in a single-stage model (it would only be properly sized under the design conditions).

 

Manual-S states that the equipment selected must be able to satisfy both the sensible and latent loads. If you're wanting the benefit of a 2-stage machine (lower power consumption during part load conditions, ability to zone more effectively, etc.), you should just pick the smallest size that is available which also meets the design load. The first stage will handle the part-load conditions with the occasional help from the second stage. If an aggressive Manual-J is done, and the house effectively manages moisture, this should not be problematic.

 

If you use a program like Wrightsoft, you can look at the BIN data reports to see the number of estimated operating hours on first/second stages to help you make a decision like this.

Will you be installing heat pump only, with electric back-up or will the units be dual fuel - heat pump with gas back-up?

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

yangxiaohua posted a blog post
53 minutes ago

John Abdo just added their location.
(via Member Map)

1 hour ago
Nick Helmholdt replied to Joshua Knittel's discussion Google Thermal View? in the group INFRARED THERMOGRAPHY USERS
"Any bets on how long it will take this company to land in court? A local energy efficiency group in…"
7 hours ago
Matthew Redmond posted a photo
8 hours ago
Matthew Redmond posted a status
"Full house for NYSWDA's ASHRAE 62.2 course today. A lot of discussion on implementing this standard on NY State's diverse housing stock."
8 hours ago
Paul Scheckel posted a blog post

Less oil, more courage: Energy and Art

Hard to admit, but I'm not all fun-facts all the time. Sometimes I even pay attention to things…See More
9 hours ago
Tom Delconte posted a blog post
11 hours ago
Profile IconBarbara Hall and Adam brown joined Home Energy Pros
15 hours ago
tedkidd replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"Pat, I think you and I agree on a LOT of things.   One thing I don't want to see is more…"
yesterday
tedkidd commented on Tom Delconte's blog post Robert Shiller Says Retrofits Are Never Worth It!
"Bob B.   Buying a home is a good investment because it is forced savings more than a good…"
yesterday
Joe Huang posted a discussion

White Box Technologies launches Web-based weather data for building energy simulations

White Box Technologies is pleased to announce under agreement with ASHRAE the launch of WBT Weather…See More
yesterday
Joseph Lamy commented on Jim Gunshinan's blog post The Universe Is Made of Stories
"My life changed when I got 'ductalatored' - became familiar with proper sizing guides for…"
yesterday

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service