I am participating in a DOE Better Buildings  program in southwest Ohio that is in its infancy stages. During discussions while setting the technical standards of the program, the topic of proper sizing vs 2 stage equipment came up.  Many of the "seasoned HVAC contractors" involved in this conversation including the director of operations for the program adamantly were advocating for the standard to be" 2 stage trumps sizing".  Meaning if you cant find a 2 stage piece of equipment in the correct size as specified by your manual j then go to the next available size.  (Most 2 stage equipment is not available in 1/2 ton sizes.)   For reasons discussed in this and other threads, I was in favor of forgoing the 2 stage piece of equipment for the piece of equipment closer to the proper size.  I was hoping I could get some input from this thread on reasoning for or against up-sizing in this situation especially taking in to consideration our geographic location.

Views: 142

Replies to This Discussion

Keep in mind that the MAJORITY of operation time is going to be at part-load conditions. More than likely, the larger unit running on its first-stage would be more appropriately sized, for more operating hours, that the "correctly" sized machine in a single-stage model (it would only be properly sized under the design conditions).

 

Manual-S states that the equipment selected must be able to satisfy both the sensible and latent loads. If you're wanting the benefit of a 2-stage machine (lower power consumption during part load conditions, ability to zone more effectively, etc.), you should just pick the smallest size that is available which also meets the design load. The first stage will handle the part-load conditions with the occasional help from the second stage. If an aggressive Manual-J is done, and the house effectively manages moisture, this should not be problematic.

 

If you use a program like Wrightsoft, you can look at the BIN data reports to see the number of estimated operating hours on first/second stages to help you make a decision like this.

RSS

Photos

Loading…
  • Add Photos
  • View All

Latest Activity

Joe Crisara posted a blog post

Give Your False Assumptions a Knockout Punch

By Derek LauberWe face seemingly unlimited obstacles when trying to manage and grow our…See More
5 hours ago
Profile IconJoe Crisara, Earth Advantage, Sydney G. Roberts and 6 more joined Home Energy Pros
5 hours ago
Jonny Fisher added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Minneapolis Blower Doors and Duct Blaster for sale

I have two Minneapolis Blower Doors + DG 700, duct blaster with manometer and some other…See More
5 hours ago
Jonny Fisher replied to Hamed Ghanbari's discussion Need a Minneapolis Blower Door + DG 700 in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I have two Minneapolis blower doors with DG 700.  I also have some other used equipment if you…"
5 hours ago
Nolan Walker replied to Hamed Ghanbari's discussion Need a Minneapolis Blower Door + DG 700 in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi Hamed, I have an extra Minneapolis blower door system - nolanwalker@gmail.com for more…"
6 hours ago
Mike Burton replied to Hamed Ghanbari's discussion Need a Minneapolis Blower Door + DG 700 in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I have a Minneapolis Bloor Door + DG700 I am wanting to sell. Please contact me at…"
9 hours ago
Hamed Ghanbari added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Need a Minneapolis Blower Door + DG 700

Looking to buy a Minneapolis Blower Door + DG 700, any assistant would be greatly appreciated.…See More
9 hours ago
Sandra K. Adomatis, SRA posted a status
"See my latest blog on "Appraiser Competency-The Simple Version" https://adomatis.wordpress.com/"
9 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service