REMRate calculates a whole house Manual J.

When you have a home with 3 HVAC systems, how do you split the area for REM and get the individual area breakdowns for specifying new equipment?


Views: 83

Replies to This Discussion

You can't do that with REM, John. You'd have to enter everything at least on a zone by zone basis, and REM gives you no way to do that. You have to use Manual J software for that info, like Right J by Wrightsoft or RHVAC by Elite.
Allison,

Can I copy the REM file into three files. Delete the other two zones. and then be half way close. I have a client with 6575 sf. 3 zones. His actual heating capacity is 235K. The whole house number from REM is 141k. I'd like to be able to provide some simple guidance as to Right Sizing when he gets to replacement time. The newest furnace is 3 years old. It is 80 AFUE 110K input for 859 sf 2nd floor. His house is good for the age. I can't work on infiltration until he installs mechanical ventilation. With the blower door numbers he should do that anyway. I can recommend additional insulation for attic and foundation walls.
Yes, I think you could split it up into three different files, John, but I don't trust REM for sizing equipment. I've seen some pretty big discrepancies (> 50%) between the results from REM and a true Manual J program. I don't completely trust Manual J programs either because more often than not, they oversize equipment even when you specify everything correctly.

The bigger issue here, though, is the question of providing guidance on HVAC. You open yourself up to more liability by venturing into HVAC consulting, so I recommend really understanding as much about HVAC as possible before you go down that road. I got myself into a couple of sticky situations early on by providing sizing guidance based on REM results.

The equipment size needed depends not only on the loads of the house but also a properly designed and installed duct system with the correct air flow. In most houses, the equipment is oversized, and it needs to be because the ducts are undersized. Can you reduce the size of equipment without changing the ducts? Probably, but you have to be careful when doing so because you might reduce the air flow too much to properly cool and heat the house.

I'm not trying to discourage you from giving HVAC advice. I'm just cautioning you that it's a tricky business and requires you to know a lot more than you get from your HERS and BPI classes.
Allison,

Thanks for the words of wisdom. I finished modeling a home tonight. The home has been great with a geothermal unit, sized at 52.2K REM says 105K.

Is that the kind of discrepancy you are referring to?


What do you do when you can't trust your tools? REM has discrepancies, so get WrightSoft. These have discrepancies so what then?

Sounds like what you are telling me is - practice, practice, practice! Get experience. Read.

In the meantime, I'm doing audits and specing equipment replacements. What kind of assurance do I have that the advice is right? I am already using this: These whole house calculations are completed in Manual J. if your Manual J calculations require different sizing, please attach your complete calculations, including design inputs for review by Energy Auditor and Efficiency Kansas,

Ideas???
John, who sized the system at 52.2 kBtuh, and how did they come up with that number? The difference I was talking about is not between equipment capacity and load but between load from REM and load from a Manual J program.

What to do when you can't trust your tools is a key question in this field. The answer is that with enough experience, you start to get a feel for the precision of your results and what kinds of things you need to adjust for. A few years ago, for example, Right J underestimated the cooling load from ducts in attics. They seem to have fixed it now, but if you weren't aware of that problem when it existed, you could end up with a system that didn't cool enough in some cases.

Another thing you need to be careful of is specing equipment size without doing a full duct design. I almost created a serious problem for myself by doing that 6 years ago. The HVAC contractor installed ducts that didn't move enough air, and the house wouldn't cool off.

The right way to do this is to do the full design process: Manuals J, S, T, & D. Here's an article I wrote about this a while back: HVAC Design Done Right - Manual J, S, T, & D http://hub.am/dAXJmk.

If you're serious about doing this kind of consulting, I recommend getting either Wrigtsoft's or Elite's HVAC design software packages and take some classes on the subject, too. ACCA and Wrightsoft offer classes, and I'm sure Elite does, too.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Eric Kjelshus replied to Johnny Ritzo's discussion Selecting a Water Heater
"I have been using  Rheem or State or Brad/white PVC flued tank type hot water heater…"
3 hours ago
Bachi Brunato replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"As it turns out, we have 10 Halo 99RT housings with Halo 998P Eyeball trim in the kitchen. The trim…"
5 hours ago
Bachi Brunato's discussion was featured

Boxing and Insulating Around Non-ICAT Cans

I have a client with 16) 4" halogen recessed light fixtures in the attic.I'd like to cover the cans…See More
7 hours ago
Johnny Ritzo's discussion was featured

Selecting a Water Heater

I am looking at updating the heating and water heating systems in a rental home I recently…See More
7 hours ago
George Kopf's discussion was featured

Misting Aeroseal in Pressurized Home = Amazing Air Sealing Innovation

As a training program manager for a non-profit, I am often too busy managing my program to catch…See More
7 hours ago
Tom Delconte's blog post was featured
7 hours ago
Christopher Morin's blog post was featured

Selling with Rebates: The Simple Payback

  The easiest way to show a homeowner how their investment in high-efficient equipment will help…See More
7 hours ago
Edward Foskey's blog post was featured
7 hours ago
Mike Rogers's blog post was featured

HOMES Act introduced with Bi-Partisan Sponsorship

We don't see a lot of bi-partisan bills in Congress these days. Here's one focusing on home…See More
7 hours ago
Mike Rogers posted a blog post

HOMES Act introduced with Bi-Partisan Sponsorship

We don't see a lot of bi-partisan bills in Congress these days. Here's one focusing on home…See More
11 hours ago
David Eggleton replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"That varies, as policies are different from state to state."
11 hours ago
Orvil D Boyer replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I have a Fluke TIR 32.  Used aproximately 10 times 1.5 yrs old.  This is the first…"
11 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service