REMRate calculates a whole house Manual J.

When you have a home with 3 HVAC systems, how do you split the area for REM and get the individual area breakdowns for specifying new equipment?


Views: 172

Replies to This Discussion

You can't do that with REM, John. You'd have to enter everything at least on a zone by zone basis, and REM gives you no way to do that. You have to use Manual J software for that info, like Right J by Wrightsoft or RHVAC by Elite.
Allison,

Can I copy the REM file into three files. Delete the other two zones. and then be half way close. I have a client with 6575 sf. 3 zones. His actual heating capacity is 235K. The whole house number from REM is 141k. I'd like to be able to provide some simple guidance as to Right Sizing when he gets to replacement time. The newest furnace is 3 years old. It is 80 AFUE 110K input for 859 sf 2nd floor. His house is good for the age. I can't work on infiltration until he installs mechanical ventilation. With the blower door numbers he should do that anyway. I can recommend additional insulation for attic and foundation walls.
Yes, I think you could split it up into three different files, John, but I don't trust REM for sizing equipment. I've seen some pretty big discrepancies (> 50%) between the results from REM and a true Manual J program. I don't completely trust Manual J programs either because more often than not, they oversize equipment even when you specify everything correctly.

The bigger issue here, though, is the question of providing guidance on HVAC. You open yourself up to more liability by venturing into HVAC consulting, so I recommend really understanding as much about HVAC as possible before you go down that road. I got myself into a couple of sticky situations early on by providing sizing guidance based on REM results.

The equipment size needed depends not only on the loads of the house but also a properly designed and installed duct system with the correct air flow. In most houses, the equipment is oversized, and it needs to be because the ducts are undersized. Can you reduce the size of equipment without changing the ducts? Probably, but you have to be careful when doing so because you might reduce the air flow too much to properly cool and heat the house.

I'm not trying to discourage you from giving HVAC advice. I'm just cautioning you that it's a tricky business and requires you to know a lot more than you get from your HERS and BPI classes.
Allison,

Thanks for the words of wisdom. I finished modeling a home tonight. The home has been great with a geothermal unit, sized at 52.2K REM says 105K.

Is that the kind of discrepancy you are referring to?


What do you do when you can't trust your tools? REM has discrepancies, so get WrightSoft. These have discrepancies so what then?

Sounds like what you are telling me is - practice, practice, practice! Get experience. Read.

In the meantime, I'm doing audits and specing equipment replacements. What kind of assurance do I have that the advice is right? I am already using this: These whole house calculations are completed in Manual J. if your Manual J calculations require different sizing, please attach your complete calculations, including design inputs for review by Energy Auditor and Efficiency Kansas,

Ideas???
John, who sized the system at 52.2 kBtuh, and how did they come up with that number? The difference I was talking about is not between equipment capacity and load but between load from REM and load from a Manual J program.

What to do when you can't trust your tools is a key question in this field. The answer is that with enough experience, you start to get a feel for the precision of your results and what kinds of things you need to adjust for. A few years ago, for example, Right J underestimated the cooling load from ducts in attics. They seem to have fixed it now, but if you weren't aware of that problem when it existed, you could end up with a system that didn't cool enough in some cases.

Another thing you need to be careful of is specing equipment size without doing a full duct design. I almost created a serious problem for myself by doing that 6 years ago. The HVAC contractor installed ducts that didn't move enough air, and the house wouldn't cool off.

The right way to do this is to do the full design process: Manuals J, S, T, & D. Here's an article I wrote about this a while back: HVAC Design Done Right - Manual J, S, T, & D http://hub.am/dAXJmk.

If you're serious about doing this kind of consulting, I recommend getting either Wrigtsoft's or Elite's HVAC design software packages and take some classes on the subject, too. ACCA and Wrightsoft offer classes, and I'm sure Elite does, too.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner replied to Richard Beyer's discussion Spontaneous Combustion and Flash Fire regarding Spray Foam Insulation
"Richard, here is something else that might be pertinent. In my hundreds of conversations with our…"
6 hours ago
Trip posted a discussion

Starting a Home Weatherization Business. Considering it...

I am considering starting a home weatherization business. (I live in Southeast Alabama)  Currently…See More
6 hours ago
Jim Gunshinan commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"To all, one thing I don't lack is advice from the experts! Thanks for the input, challenges,…"
7 hours ago
tedkidd commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"Jim, I'm glad you are open, that's great!  We all learn best when we are open! The…"
8 hours ago
David Eakin commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"Jim, Well, as the editor of Home Energy you should already know that the order of remediation is…"
8 hours ago
Greg Labbe posted a blog post

Technical Tape Desecration

Lets face it – building science is pushing the performance of adhesive tapes to a new levels and…See More
10 hours ago
Stacy Hunt posted an event

High Performance Enclosure Strategies: Part II, New Construction at Online

August 13, 2014 from 1pm to 2:30pm
Please join the Building America Program for our free webinar: High Performance Enclosure…See More
11 hours ago
Richard Beyer replied to Howard Katzman's discussion UV lights on filters
"Howard, There are numerous manufacturer's who swear these systems work and then you have the…"
20 hours ago
Christopher Morin posted a blog post

How do You Test a TXV?

  Thermostatic Expansion Valves (TEV or TXV), one of the most popular metering devices for…See More
23 hours ago
Howard Katzman posted a discussion

UV lights on filters

I recently saw UV bulb installations in 2 HVAC systems in a home. Each system had the Lennox…See More
yesterday
Don Fitchett joined Michael Stuart's group
Thumbnail

INFRARED THERMOGRAPHY USERS

This group is dedicated to knowledge sharing and discussion of infrared thermography for building…See More
yesterday
Don Fitchett commented on Diane Chojnowski's group Pinterest
"While most of our (BIN95.com) energy post and boards are industrial related, there are crossovers…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service