This furnace was installed two years ago in a conditioned basement.  The ductwork is a thin flexible plastic like that of a clothes dryer (but with a 6" diameter).   This is the second one that I've seen in the past year (Oregon).   Is this up to code?

 

Views: 219

Replies to This Discussion

The plastic would need to be rated for the temps the furnace delivers.  Is there a tag on the plastic?  The maufacturer would have the specs as to temp and application.  It isnt pretty but it is functional.  The specs on the plastic will give you the information you need but you might have to call the manufacturer.  I personally would be very suspect about it.   Have you performed a Temp Rise on the furnace?
This is crap work and should be redone, but is allowed by code.
I agree that the quality of work on this radial system can be called into question. But I a, very surprised to hear this would meet code. Based on the 2009 IECC, that ductwork being in unconditioned space should have a minimum R-value. Here is MA and RI, inspectors hold the contractor to this spec, R-8 outside the building envelope and R-6 for inside - in a basement like this for example. This may be a place to start regarding this particular job, looks pretty recent...
I agree that the quality of work on this radial system can be called into question. But I am very surprised to hear this would meet code. Based on the 2009 IECC, that ductwork being in unconditioned space should have a minimum R-value. Here is MA and RI, inspectors hold the contractor to this spec, R-8 outside the building envelope and R-6 for inside - in a basement like this for example. This may be a place to start regarding this particular job, looks pretty recent...

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Don Fitchett commented on Tom White's video
Thumbnail

Alliant Energy's PowerHouse TV: Sealing Leaky Ductwork

"Very educational. thanks for sharing Tom."
1 hour ago
Hal Skinner posted a discussion

How much heat energy is lost through the floor of a house?

I am asking this as I do not recall anyone speaking of any study to this end.  Many comments about…See More
1 hour ago

Mike Braun just added their location.
(via Member Map)

2 hours ago
Bud Poll replied to Bud Poll's discussion Another benefit from air sealing
"From my work in NY City many years ago, the critters I saw would never have fit through a quarter…"
5 hours ago
Barbara Smith replied to Bud Poll's discussion Another benefit from air sealing
"Eliminating quarter sized holes can impede rats from entering a building, in areas where rats tend…"
6 hours ago
Casey Murphy is now a member of Home Energy Pros
7 hours ago
Walter Ahlgrim replied to James White's discussion What happened to Home Energy Pro's website?
"Try downloading Google Chrome web browser https://www.google.com/chrome/browser/ I had similar…"
23 hours ago
Stacy Hunt posted an event

Building America Webinar: Multifamily Ventilation Strategies and Compartmentalization Requirements at Virtual

September 24, 2014 from 3pm to 4:30pm
The Building America Program is hosting a no-cost, webinar-based training on Multifamily…See More
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service