This furnace was installed two years ago in a conditioned basement.  The ductwork is a thin flexible plastic like that of a clothes dryer (but with a 6" diameter).   This is the second one that I've seen in the past year (Oregon).   Is this up to code?

 

Views: 227

Replies to This Discussion

The plastic would need to be rated for the temps the furnace delivers.  Is there a tag on the plastic?  The maufacturer would have the specs as to temp and application.  It isnt pretty but it is functional.  The specs on the plastic will give you the information you need but you might have to call the manufacturer.  I personally would be very suspect about it.   Have you performed a Temp Rise on the furnace?
This is crap work and should be redone, but is allowed by code.
I agree that the quality of work on this radial system can be called into question. But I a, very surprised to hear this would meet code. Based on the 2009 IECC, that ductwork being in unconditioned space should have a minimum R-value. Here is MA and RI, inspectors hold the contractor to this spec, R-8 outside the building envelope and R-6 for inside - in a basement like this for example. This may be a place to start regarding this particular job, looks pretty recent...
I agree that the quality of work on this radial system can be called into question. But I am very surprised to hear this would meet code. Based on the 2009 IECC, that ductwork being in unconditioned space should have a minimum R-value. Here is MA and RI, inspectors hold the contractor to this spec, R-8 outside the building envelope and R-6 for inside - in a basement like this for example. This may be a place to start regarding this particular job, looks pretty recent...

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Steven Lewis replied to Bob Blanchette's discussion How does Cycles Per Hour affect real world AFUE?
"In my opinion you are trying to get very detailed about equipment that is designed to perform in a…"
13 hours ago
Brad Brenner posted a blog post
14 hours ago
Bob Blanchette commented on Dale Stephens's blog post LED Lighting 24-month update 18,240 hours & counting
"I'm also in the process of upgrading from CFL to LED. Energy cost difference gets "lost…"
16 hours ago
Bob Blanchette commented on Dale Stephens's blog post LED Lighting 24-month update 18,240 hours & counting
"A couple questions on your power bills:1: All-Electric house or gas heat/water…"
17 hours ago
Bob Blanchette replied to Bud Poll's discussion Basing air exchange on house volume??
"Where to you live that has all these air exchangers. I have NEVER seen one installed in a house.…"
17 hours ago
Bob Blanchette commented on Jeff Parks's photo
Thumbnail

Heat Exchanger

"Short cycling will rust them out every time. You have at least 4 burners there, most likely a WAY…"
17 hours ago
Al Tibbs commented on Al Tibbs's photo
Thumbnail

vermiculite_insul

"Tom. I am not sure what R-value is for this product. I think it is pretty low. This particular…"
yesterday
Marc Tannenbaum posted a discussion

Industry Veteran Michelle Knaszak Joins Dr. Energy Saver

Dr. Energy Saver is pleased to announce that Michelle Knaszak has joined the company as our…See More
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service