Hello to everyone again -- This is an update on a building I'm working on for a NG furnace.  It's been about a month (a very busy month) since I last posted questions and I have been to the building -- I have some answers and another question about reading LOAD CALCULATIONS. 

The 2052 sq. ft. building has only 1.5" insulated garage door panels for the ceiling as the only insulation (in the attic floor along with 2 part foam on the perimeter walls averaging 2.5" to 4" thick) so I'm looking at blowing cellulose to a depth of 1' in the attic after some air-sealing to bring the heating loss down.  The blower door number was 6275 CFM@50 -- there is a construction flaw where 2 part foam applied to the perimeter's stud bays didn't completely reach up behind a top 2 x 6 band joist (is that what it's called if it's at the ceiling and not at floor level?)  Most bays are pulling air during the BD test.  Also the ceiling garage door panel joints are not caulked.  So I'm hoping to bring the CFM down to some reasonable level by caulking the cracks and using bagged inso stuffed into the stud bays.

I found an HVAC company that gets load calc's done and they gave a bid for a Bryant preferred two stage and ductwork installed inside the envelope (ceiling is 9'3").  They're sizing it at 100,000 BTUs.  

They did two load calc's -- one with minimal insulation (present situation) and one if 1' of cellulose is installed in 2052 sq. ft. of attic floor.

This is the first time I've read/seen an actual load calc so I have a question -- (the HVAC co. has a call into the guy in another city who did the calc and I'm still waiting for his answer) --- The software is "Elite RHVAC Residential HVAC Loads" and approved Manual J and Manual D -- 8th Edition, Version 2

On the first page, the "Project Report" down in the "Check Figures" section the number for square foot room area is correct at 2052 --- the "Volume (ft cubed) of Cond. Space" concerns me.  I would get this number by taking the sq. ft of 2052 and multiplying it by the ceiling height of 9.25' (9'3") for a total of  18,981 cu. ft --- The reports however had two different numbers -- minimal insulation calc being 32,832 and the insualtion added calc's number being 20,520.

Can anybody who knows this software tell me why these numbers are not the basic length x width x height number?

Is there a place on this report where I can see whether they considered all the ductwork is run inside the envelope not up in the attic?

And I don't see where the Blower Door number was addressed at all -- or isn't this the type of calc that uses the BD number?

According to both load calc's (minimal insulation) and ($2,000 more insulation added) I need a 100,000 BTU furnace.

Well -- thanks to everybody in advance for input.

Views: 1276

Replies to This Discussion

Thanks for the input -- I don't mind getting training if I could justify it with business income in my area.  I jsut have to do some more research on this.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

George Matthews replied to George Matthews's discussion Shortridge 8400 Flowhood for A/C airflow testing in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Here are the pics of the flowhood and airdata manometer"
yesterday
Sarah Holloway posted a photo
yesterday
Joe Urycki added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

TEC blower door and UEI combustion analyzer for sale

For sale is one used TEC Minneapolis blower door system: Includes model 3 fan with rings A and B,…See More
yesterday
John Nicholas replied to Kevin Emerson's discussion Studies re: radon mitigation and energy efficiency
"The Nay side is well represented with the links already posted. I presented a neutral side, with…"
yesterday
Ray Lehman replied to Kevin Emerson's discussion Studies re: radon mitigation and energy efficiency
"Hey John, Thanks for the information.  Very good empirical data. While I agree that running…"
yesterday
John Nicholas replied to Kevin Emerson's discussion Studies re: radon mitigation and energy efficiency
"I have no links, just some anecdotal evidence. I had several Blower Door Tests done on my own home.…"
Friday
Chris Laumer-Giddens commented on Chris Laumer-Giddens's blog post Raising the BARrier in North Carolina Mountain Home, Air Tight Ceiling
"@Joe Nagan, We have found this technique to be WAY simpler and A LOT less labor than making a…"
Thursday
Judy Rachel replied to Blake Shurtz's discussion Testing spillage on induced draft furnace?
"I hope the attached picture is clear enough for you to see.  As the caption on the picture…"
Thursday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service