Tags: HVAC, IAQ, energy, motors
Permalink Reply by Steven Lewis on December 6, 2010 at 3:07pm
Permalink Reply by David Mileusnich on December 8, 2010 at 9:01am
Permalink Reply by Bruce Gold on December 8, 2010 at 9:38am Good question. My home is 20 years old and so far it looks like the discussion regarding electricity costs being higher but what about the overall cost of energy. The last two days I did a test one with the fan set to auto and the next with the fan set to on. The first day the high was 19 and the low was 8 degrees. The heat was on for 14 hours. The next day at 6:00 AM (when I had the idea), I switched the fan to on. The hight for that day was 19 with a low of 7 degrees which is fairly consistent with the previous day. For that day, the heat was on for only 8 hours. So while I was using more electricity running the fan, the natural gas usage was cut dramatically. I don't know if that is typical or how this impacts the overall energy costs between the two scenarios.
Permalink Reply by David Mileusnich on December 8, 2010 at 10:17am
David Mileusnich said:Good question. My home is 20 years old and so far it looks like the discussion regarding electricity costs being higher but what about the overall cost of energy. The last two days I did a test one with the fan set to auto and the next with the fan set to on. The first day the high was 19 and the low was 8 degrees. The heat was on for 14 hours. The next day at 6:00 AM (when I had the idea), I switched the fan to on. The hight for that day was 19 with a low of 7 degrees which is fairly consistent with the previous day. For that day, the heat was on for only 8 hours. So while I was using more electricity running the fan, the natural gas usage was cut dramatically. I don't know if that is typical or how this impacts the overall energy costs between the two scenarios.
David,
I am here in the Chicago area and had pretty much the same temp as you. Question #1 You say the heat was on all day, does that mean that you counted how many times it shut down and started back up? This was in your auto position. Question #2 when you switched to fan, are you saying the furnace did not run as often, did you count how many times it went off and on?
When I put mine in auto, it seemed to have run all day, maybe off for a few minutes then back on. When I put the fan on, I did not notice any change, it ran all day, but not sure how often.
So, I tend to agree with you...if you keep the fan on all the time, wouldn't it make sense that when the furnace called for heat, and since the blower is already running, wouldn't it take less energy to get that blower motor to get to it's first stage.
And yep, if you saved on that....did you electricity bill just go up? :)
Thanks for your input, much appreciated
Permalink Reply by Bruce Gold on December 8, 2010 at 10:41am Bruce,
We live in the same Chicagoland area. Regarding question #1, it would seem that about a minute later the system would kick back on in the auto mode. For the usage on both days, all I'm going off of is the usage stats on the thermostat. Since I'm only day two with the fan running continuously, I don't know where the energy bills will end up. As the temp warms up to around 30, I may switch it back to auto. I'm not sure how many Therms I"m using during both of these days. Knowing that would be useful to extrapolate any costs increases/decreases.
Bruce Gold said:
David Mileusnich said:Good question. My home is 20 years old and so far it looks like the discussion regarding electricity costs being higher but what about the overall cost of energy. The last two days I did a test one with the fan set to auto and the next with the fan set to on. The first day the high was 19 and the low was 8 degrees. The heat was on for 14 hours. The next day at 6:00 AM (when I had the idea), I switched the fan to on. The hight for that day was 19 with a low of 7 degrees which is fairly consistent with the previous day. For that day, the heat was on for only 8 hours. So while I was using more electricity running the fan, the natural gas usage was cut dramatically. I don't know if that is typical or how this impacts the overall energy costs between the two scenarios.
David,
I am here in the Chicago area and had pretty much the same temp as you. Question #1 You say the heat was on all day, does that mean that you counted how many times it shut down and started back up? This was in your auto position. Question #2 when you switched to fan, are you saying the furnace did not run as often, did you count how many times it went off and on?
When I put mine in auto, it seemed to have run all day, maybe off for a few minutes then back on. When I put the fan on, I did not notice any change, it ran all day, but not sure how often.
So, I tend to agree with you...if you keep the fan on all the time, wouldn't it make sense that when the furnace called for heat, and since the blower is already running, wouldn't it take less energy to get that blower motor to get to it's first stage.
And yep, if you saved on that....did you electricity bill just go up? :)
Thanks for your input, much appreciated
Permalink Reply by Allison A. Bailes III on December 9, 2010 at 5:37am
Permalink Reply by Bruce Gold on December 9, 2010 at 6:21am David, you can check your gas consumption at the meter. If you had measured that for the two days of your experiment, I'll bet the numbers would show a very different result than your 14 hours vs. 8 hours of furnace run time that you read off the thermostat.
I have to go with this one, since when I had my fan on auto, the furnace would run as much as when the fan was in auto.
The only thing I felt was the house cooling off faster in run, then it did in auto. I think my next experiment is to have the ceiling fan blowing down in slow, since heat rises ( actually, heat does not rise but get pushed up from cold air) maybe that might make a difference.
Any comments?
I have a lot of difficulty believing that keeping the fan switch set to on will cut your heating almost in half. The only way this could happen is if you had (1) a very tight house, (2) ducts inside the envelope, (3) poor distribution of heated air in the house, and (4) a thermostat in the coldest part of the house.
In houses, you lose heat through the building envelope. Keeping your fan on doesn't decrease the amount of heat loss you have there, which means you still have to keep adding as much heat as you're losing. For the reasons below, what's more likely to happen is that you increase your heat loss and have to add more heat, not less.
Keeping the fan on is likely to increase infiltration because of unbalanced duct leakage. That means you lose heat even more quickly.
Keeping the fan on is likely to send more of your heated air outside and bring in more cold air because of duct leakage. Even if you have the same amount of leakage in the supply ducts as in the returns, you're throwing out heat and bringing in cold air through those leaks. The only way to avoid this is to have NO duct leakage outside the envelope, which is only possible if all the ducts are inside the envelope.
Keeping the fan on is going to cool off your indoor air if your ducts are outside the envelope. When you run 70° air through a duct with R-4, R-6, or R-8 insulation in a space that's 20°, 40°, or more cooler, that air inside the ducts will lose heat by conduction to the surroundings.
If you go back and read some of the earlier comments (Michael Blasnik's, mine, and A. Tamasin Sterner's on the first page), you'll see that there are other good reasons not to keep the fan in the on position, too.
If you have data that you think prove that your house is an exception to the principles of building science, I'd like to see them. If your data show that you save money by keeping the fan in the on position, I'm sure an experienced building science pro could find out what the real problem is and how you can save even more money by fixing it.
Permalink Reply by David Mileusnich on December 17, 2010 at 5:53am Just received my gas bill. This is just additional information and I don't have exact day for day analysis but on the days that were very cold I just left the fan on. Otherwise, I switched it back to auto. For 11/16/-12/16, the number of therms was 184 which is higher than last year but last year was much warmer. The average temp for this period just finished was 22 degress. Last December's average was 29 but January's was 23. January's therms were ~250. So it looks like a potential difference of around 60 therms if I go by average recorded temperature. I haven't received my electric bill yet.
Permalink Reply by David Mileusnich on December 17, 2010 at 7:40am Correction. That was an estimate from NiCor. The actual value is 190 Therms more for the month or a net 130 increase.
Permalink Reply by Allison A. Bailes III on December 9, 2010 at 9:07am
Permalink Reply by David Mileusnich on December 9, 2010 at 12:20pm
Permalink Reply by Bruce Gold on December 14, 2010 at 2:36am
Bruce Gold said:
Steven Lewis said:Trane will get back to you. They are more responsive than most companies but it will have to go to several people first. They may send it to the local distributer to handle so be patient if you can.
If the furnace is 4 yrs old the parts should be covered under warranty (5 yr ) The complete motor is VERY EXPENSIVE but you probably wont need the entire assembly. The main parts can be replaced without replacing the entire motor. Bearings can be replaced easily as well as the control module located on the back of the motor, armature and I see no reason why you would ever need to replace the magnets.
The labor will not be warrantied unless you have an extended warranty purchased at the time of sale.
Gas smells are not normal unless you eat beans
I have your address in IL if you didnt falsify your profile. Click on the name of the person replying and then click on their pic and it will take you to their profile on this site. So I know the general area you are in
Hopefully they Trane will respond quickly since it was installed, looks like 3/06.
Didn't falsify anything, that way I get to keep my gun permit. :)
Threw a bucket of water down the drain by the furnace...gas smell seems to have gotten better, so not sure if it was really gas or just stale water sitting in the trap that was causing the gas fumes.
I am going to have my neighbors come over again tonight to see if they can still smell....THE SMELL!!!! I can, but not as much, but furnace has been running all day. I believe this is day number 6 with problem. Saturday my girlfriend told me to get some parakeets (like they did for mines), I told her that's why I invited her over for dinner...my arm is still sore.
So first move is to wait for Trane...if you have any pull or strings with them, the sooner the better.
So now, I go and click on your name then picture...here goes.
Again,Thanks. And I am assuming you are an HVAC tech. I will have at least one last question for you probably tomorrow.Steven, Hope your still there, since I have a new question.What problems would my furnace have if it is pitched back. Meaning, from the top, the furnace goes back slightly until it get to the bottom, then it is at least 1/2 off...meaning back from the top.Had a new blower motor installed, now they are coming out today to install a inducer motor for the 3 time.Now just getting the run around from this company about when they will fix this pitch problem. This is going on almost 5 years and believe now, they will not come out to fix this until they get all their installs done leaving me with new parts and yet a badly pitched furnace.Any help would be appreciated
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Johnny Ritzo posted a discussion
Eric Kjelshus replied to Patrick Michaelyan's discussion Hot Upper Stories
Bud Poll replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Sean Lintow Sr replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Bachi Brunato posted a discussion
Dennis Heidner replied to Patrick Michaelyan's discussion Hot Upper Stories
Bob Blanchette replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
Bob Blanchette replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
Dennis Heidner replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
Edward Foskey commented on Edward Foskey's blog post Preparing to Update the Heat Pump© 2013 Created by Lawrence Berkeley National Laboratory.