Tags: HVAC, IAQ, energy, motors
Permalink Reply by A. Tamasin Sterner on December 2, 2010 at 9:20am
Permalink Reply by Bruce Gold on December 4, 2010 at 12:08pm Great topic for discussion here, TJ. The answer is that you should NOT leave the fan in the ON position. It will cost a lot more in electricity, as Michael Blasnik said. If the house has unbalanced duct leakage, it will also cost extra in heating and cooling because of the added air leakage.
Yes, having an HVAC system that runs longer has benefits, but you want to achieve that by having a properly sized system and, if you can afford it, a variable speed blower with an ECM. As has been mentioned by others, running the fan in the cooling season in a humid climate will increase the humidity in the house because it will evaporate moisture from the coil and drain pan.
If you want cleaner air, filtration is the last step you take, so your point number 3 isn't valid either. First you get bad stuff out of the house and seal the air leaks and duct leakage so you don't bring more bad stuff in.
It sounds like a mouse, I've removed dozens from the blades of furnace blowers. If you have to cut the flue to remove the fan that's a poor install. The blower assembly is actually easy to remove, take the control board off and tie it out of the way, then find the 2 screws in the flange of the housing, remove them and slide the whole assembly out. It sounds like the tech didn't want to cut the flue, so he couldn't smell anything.
The other problem it might be is a plugged condensate drain. This would cause condensate to back up into the combustion fan which will cause the furnace to shut down. You can check this by removing the drain line at the bottom of the hx.
Permalink Reply by John Nicholas on December 4, 2010 at 1:42pm
Permalink Reply by Steven Lewis on December 4, 2010 at 2:42pm
Permalink Reply by Bruce Gold on December 4, 2010 at 3:52pm Bruce,
I would have a different company send a technician. From your description, the furnace will have to make way to look at the blower. Is the smell just in the furnace area, or is it throughout the house? Might make a difference, you could look at the draft assist fan first.
I also refer to my post earlier about failure of blowers in many furnaces I operated. I disagree with the weight you are giving the "Mean Time Before Failure" in this situation.
Permalink Reply by Bruce Gold on December 4, 2010 at 4:07pm Since your furnace is a down or counterflow, you should be able to remove the filter (located in the return duct above the furnace?) and look down at the blower motor. All counterflow furnaces, regardless of manufacturer, are a pain to get into to see the blower motor. Yor XV furnace has a Variable speed motor and they use a lot less electricity when they run (not Start- that is a small amount) than a regular PSC motor. The motor will also change speed to provide better comfort as the furnace operates at first and 2nd stage heat. It will also remove more humidity in the summer and increase the efficiency of the A/C as well.
Did the service person remove the baffle and inspect the motor? I have found that the filter can be sucked out of the rack (if not changed often) and can lay on top of the motor causing higher than normal heat rise.
As to the odor. Diagnosing without an exam is malpractice if you are a DR. If you are unsure about the installing company, call someone else. The high pitch noise sound like something rubbing in or on the fan. I would look at the motor. You may have to cut the flue pipes to do this and reseal them with rubber hub connectors (use the clamps)
Sorry you are having a problem with the Trane furnace. The main issue may be the furnace or maybe how it was installed. I sell them and have had few problems with them. Trane (our distributor) has been very supportive if there has been a problem. Look at trane.com and you should be able to send them an email with your problem. The area distributor will have people on staff who can help you. Send me an email if you need more help. lewis_htg_clg@sbcglobal.net and I will get you what I can
Permalink Reply by Steven Lewis on December 4, 2010 at 5:22pm
Permalink Reply by Bruce Gold on December 5, 2010 at 7:23am The higher the MERV # the more restrictive the filter is to airflow. You need to balance filtration with performance/airflow. You need to know the static pressure in the supply and return duct and then add in the furnace and evap coil pressure drops. The total static pressure is then applied to the airflow chart in the installation packet with the furnace. As the static pressure goes up the delivered airflow goes down. ECM fans will deliver better airflow against resistance but will only do so to a certain extent. When you add in the resistance of a high efficiency filter you can eceed the temp rise of the furnace. Have someone take the static pressures or you can take the temp rise. Find out the airflow settings your furnace is set to. Should be dip switch settings on the control board then look at the temp rise for that aiflow and you can get an idea of your true airflow.
To low temp rise and moisture can form in the main heat exchanger and cause premature failure. To high temp rise causes more rapid cycling of the burner limit switch that can impact operating costs and cause premature failure of the ignitor, limits and heat exchanger.
HE is for high efficiency VS is for variable speed. There are two variable speed fans the main blower that we are discussing and the variable speed inducer motor. That is the small motor assembly that starts when there is a call for heat from the thermostat. The installation instructions should have a sequence of operation listed in them so you can look at them for your information as to proper operation.
if the contractor didnt leave them with you, I can get you a copy. need the model and serial no's
Permalink Reply by Bruce Gold on December 5, 2010 at 10:12am
Steven Lewis said:The higher the MERV # the more restrictive the filter is to airflow. You need to balance filtration with performance/airflow. You need to know the static pressure in the supply and return duct and then add in the furnace and evap coil pressure drops. The total static pressure is then applied to the airflow chart in the installation packet with the furnace. As the static pressure goes up the delivered airflow goes down. ECM fans will deliver better airflow against resistance but will only do so to a certain extent. When you add in the resistance of a high efficiency filter you can eceed the temp rise of the furnace. Have someone take the static pressures or you can take the temp rise. Find out the airflow settings your furnace is set to. Should be dip switch settings on the control board then look at the temp rise for that aiflow and you can get an idea of your true airflow.
To low temp rise and moisture can form in the main heat exchanger and cause premature failure. To high temp rise causes more rapid cycling of the burner limit switch that can impact operating costs and cause premature failure of the ignitor, limits and heat exchanger.
HE is for high efficiency VS is for variable speed. There are two variable speed fans the main blower that we are discussing and the variable speed inducer motor. That is the small motor assembly that starts when there is a call for heat from the thermostat. The installation instructions should have a sequence of operation listed in them so you can look at them for your information as to proper operation.
if the contractor didnt leave them with you, I can get you a copy. need the model and serial no's
The contractor left me nothing but a bill and a headache.
What you just explained about the the MERV is exactly what the Trane Rep told me, almost exactly word for word.
So now I am thinking this guy who came out is pretty clueless about all he told me and the work he performed.
Is this VS motor that you are talking about, is that the DC motor that is mounted on the front, that has been replaced 3 times? If not, what does that DC motor do? If not, please don't tell me this VS motor is also behind the guts of the furnace, meaning behind the circuit board?
Either you or John suggested checking the baffle, can you tell me where this is located? I am having my next door neighbor come over today and he used to be in the HVAC business years ago. When I asked him about the baffle, he had no idea what I was talking about (he has been out of the business at least 15 years) and asked me to ask you where
this is located and what it's function is?
The house yesterday was not as bad, I could smell it a little, but not as bad as the past few days. Had girlfriend over last night for dinner and she is very sensitive to odors. About 8pm she came out of one of the rooms, I am on the phone with my neighbor who had smelled it too, the furnace kicked in, GF said she could smell something, I could start smelling it too. I can only say it's an oily, metallic odor that you can almost taste and once you breath it in, it stays with you meaning I got into my car and could still smell it, my neighbor went home and she could still smell it. It eventually goes away and all is well, even when the furnace is running again. I think my next step is to get a priest over here and perform and exorcism on this furnace.
I can't tell you how much I appreciate your input and sticking with me on this. I truly owe you a big thanks.
Permalink Reply by John Nicholas on December 5, 2010 at 11:41am
Permalink Reply by Bruce Gold on December 5, 2010 at 12:08pm Bruce,
If you smell a slight gas smell like this and it persists, call the gas company. It could be a lot of things. They will come check. This is not about venting! This is safety.
The small DC motor in front everything you are referring to is what I called the draft assisted fan. It is not VS. It comes on to improve the draft of the furnace at the beginning of the cycle, before the chimney has had time to warm up. This is primarily an efficiency measure. The older 60 AFUE furnaces do not have them and are atmospherically vented, like a hot water heater. A furnace with this type of fan is at least 78 AFUE.
Quite an increase.
The VS motor Steven is referring to is your blower motor.
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
David Eakin commented on Elisa Wood's blog post Momentum builds for energy efficiency...but is the wolf at the door?
Egr renovation posted a status
Egr renovation posted a status
Meagan Foster posted events
Meagan Foster updated an event
Meagan Foster updated an event
Meagan Foster updated an event
Meagan Foster updated an event© 2013 Created by Lawrence Berkeley National Laboratory.