I have my first Energy Star home that has sprinkler piping installed in the attic.  The pipes run about 6 inches above the drywall.  The sprinkler company says there must be an insulation void between the ceiling top and the piping to avoid freezing, so the insulator placed fiberglass batts over the piping to keep the blown fiberglass away from the pipes, which will leave (roughly) a 6-inch by 24-inch air gap directly above the drywall at each pipe run.  This, of course, violates the Energy Star insulation-to-air barrier alignment guideline.  I don't have a good solution to offer, but I'm wondering if removing the batts and blowing the insulation (R-38) directly around the piping, which would leave roughly R-18 over them, would suffice.  Has anyone else dealt with this issue yet?  This will be the norm for all new homes in PA.

Views: 664

Attachments:

Replies to This Discussion

I believe the Sprinkler Company has a problem not stated.  NFPA does not allow any thing to rest on a sprinkler pipe.  Blowing insulation around the pipe would not allow the required periodic visual inspections.  Resting batts on the pipes also prohibits visual inspection and additionally cause the potential for the pipes to deflect. Deflection changes the water flow - think flex duct bends etc.

With a wet sprinkler system install in the attic, you are pretty much stuck with installing the insulation on the roof deck.  The sprinkler has to be able to spray water on the roof deck as well as below. Prior to my certification as a HERS Rater, I was  administrator of a medical facility that was sprinkled.  The batt insulation was installed on the roof deck. It sags, looses contact with the deck, drops out, lands on sprinkler pipe and other places you don't want it.

How high is the attic space?  I am slightly surprised there are not sprinkler heads along the roof deck also.

Since there is little choice except to include the entire attic within the thermal envelope - I believe the long term solution is to foam the roof deck

Your install is subject to local fire inspection.  I would keep all of the above in mind, and visit with them.  Start at the Fire Dept.  They like tight houses.  Explain how you do tight shell, and see what they say.  Then approach the actual building inspector.

 

 

We run into this problem a lot in North Carolina. An alternative to foaming the roof deck & gable ends is creating a horizontal boxed chase for the sprinkler lines. Typically, our builders keep the top of boxed chase lower than the ceiling insulation so there isn't a need for a 6-sided wall assembly. The box (built with drywall, plywood, Thermax or equivalent) is air sealed with an appropriate material (mastic, caulk, foam). I also recently found this Literature Review from the NFPA to acknowledge that there is a conflict in sprinkler freeze protection and ENERGY STAR. The article also offers a variety of solutions. http://www.nfpa.org/assets/files//pdf/research/rfsprinklerinsulatio...

The real solution is to say to the sprinkler guy - "I will not force the insulator to take responsibility for your pipes freezing - install them in the walls so all pipes are inside the heated shell"

Ed Minch

Tried it; I might as well have asked for sacrifice of his first born.  The builder has the final say, and they were OK with it.  I disclaimed any responsibliity for when the pipes freeze, and they signed the ceiling insulation item of the checklist.  I don't care for the provision for them to be able to sign off on several items, but I am thankful for it in the case of sprinklers.

We air seled some condos a few years back and their sprinklers were in a cathedral ceiling with scissors trusses.  One of techs was smart enough to take a picture and tell the job super there there was on pipe that was especially vulnerable - he didn't like the answer he got so he emailed the picture and a note.  Wouldn't you know, it broke and soaked all three units in the stack.  We were named in a lawsuit, but were immediately let out when the judge saw the e-mail.

Now we take lost of picture

We have 50/50 success in getting pipes out of the attic

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Rick Karg replied to Carly@AirCycler's discussion The (Small) Cost of Ventilation Without Recovery
"As a member of the ASHRAE 62.2 committee (and president of Residential Energy Dynamics, the author…"
Friday
Bradford E. White replied to Elizabeth Guinn's discussion ERV in need of backflow preventer.
"I would use an in-line backdraft damper such as Artis Industries or the ones made by Fantech and…"
Thursday
Kim Tanner posted a video

Wireless Air Leakage Testing

This webinar will discuss the use of WiFi technology to conduct and document blower door and duct leakage tests for compliance with local energy codes. The s...
Thursday
Profile IconPerry Grossman, Daniel Pate and Ottawa Furnace Filters joined Home Energy Pros
Thursday
Kirsten Richnavsky added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Breaking the link between unhealthy homes and unhealthy kids

Listen in on IAQ Radio to a discussion on reducing the household triggers that cause asthmaattacks…See More
Thursday
Kirsten Richnavsky posted a discussion

Breaking the link between unhealthy homes and unhealthy kids

Listen in on IAQ Radio to a discussion on reducing the household triggers that cause asthmaattacks…See More
Thursday
Kim Tanner posted events
Thursday
Ottawa Furnace Filters posted a blog post

Some Useful Information about Furnace Air Filters

There is not much we can do about the air pollution outside of a house in Ottawa, Canada, but we…See More
Thursday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service