I have my first Energy Star home that has sprinkler piping installed in the attic.  The pipes run about 6 inches above the drywall.  The sprinkler company says there must be an insulation void between the ceiling top and the piping to avoid freezing, so the insulator placed fiberglass batts over the piping to keep the blown fiberglass away from the pipes, which will leave (roughly) a 6-inch by 24-inch air gap directly above the drywall at each pipe run.  This, of course, violates the Energy Star insulation-to-air barrier alignment guideline.  I don't have a good solution to offer, but I'm wondering if removing the batts and blowing the insulation (R-38) directly around the piping, which would leave roughly R-18 over them, would suffice.  Has anyone else dealt with this issue yet?  This will be the norm for all new homes in PA.

Views: 206

Attachments:

Replies to This Discussion

I believe the Sprinkler Company has a problem not stated.  NFPA does not allow any thing to rest on a sprinkler pipe.  Blowing insulation around the pipe would not allow the required periodic visual inspections.  Resting batts on the pipes also prohibits visual inspection and additionally cause the potential for the pipes to deflect. Deflection changes the water flow - think flex duct bends etc.

With a wet sprinkler system install in the attic, you are pretty much stuck with installing the insulation on the roof deck.  The sprinkler has to be able to spray water on the roof deck as well as below. Prior to my certification as a HERS Rater, I was  administrator of a medical facility that was sprinkled.  The batt insulation was installed on the roof deck. It sags, looses contact with the deck, drops out, lands on sprinkler pipe and other places you don't want it.

How high is the attic space?  I am slightly surprised there are not sprinkler heads along the roof deck also.

Since there is little choice except to include the entire attic within the thermal envelope - I believe the long term solution is to foam the roof deck

Your install is subject to local fire inspection.  I would keep all of the above in mind, and visit with them.  Start at the Fire Dept.  They like tight houses.  Explain how you do tight shell, and see what they say.  Then approach the actual building inspector.

 

 

We run into this problem a lot in North Carolina. An alternative to foaming the roof deck & gable ends is creating a horizontal boxed chase for the sprinkler lines. Typically, our builders keep the top of boxed chase lower than the ceiling insulation so there isn't a need for a 6-sided wall assembly. The box (built with drywall, plywood, Thermax or equivalent) is air sealed with an appropriate material (mastic, caulk, foam). I also recently found this Literature Review from the NFPA to acknowledge that there is a conflict in sprinkler freeze protection and ENERGY STAR. The article also offers a variety of solutions. http://www.nfpa.org/assets/files//pdf/research/rfsprinklerinsulatio...

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Dennis Heidner replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"Ben,  the German highway system concept actually started BEFORE Nazi Germany during  the…"
1 hour ago
Stan Kuhn replied to Patrick Michaelyan's discussion Hot Upper Stories
"You note overheating on the south side (naturally.)  Assuming the typical roof overhang of…"
7 hours ago
Patrick Michaelyan replied to Patrick Michaelyan's discussion Hot Upper Stories
"Thanks a lot Ed. And thanks to all who have added their two cents. I think I know where to take…"
8 hours ago
Ed Minch replied to Patrick Michaelyan's discussion Hot Upper Stories
"We have successfully treated this same problem in perhaps 1000 of this same house in the…"
9 hours ago
Craig Savage commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Hello Tom We are working with A.O. Smith, GE and Stiebel Eltron on a Building America task to…"
10 hours ago
Tom Delconte commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Craig: I was serious, since my propane price jumped from .98 to 1.85! according to everyone the GE…"
11 hours ago
Ben Jacobs replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"I think that government support for good ideas results in major benefits over the long haul. Please…"
11 hours ago
Craig Savage commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Hello Tom Not sure if you are being sarcastic, but a serious answer would be that GE is selling…"
14 hours ago
Tom Delconte commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Craig: do you have a diagram of one that will run longer than one year? They don't really seem…"
14 hours ago
Cory Chovanec replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"All good points brought up. My advice is not to leave the lights. When you said halogen I think…"
16 hours ago
Jon Haehnel replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"The first 2 answers by Tom and Sean jive with my thinking and experience. Thank you Don for…"
16 hours ago
Tom Smith replied to Patrick Michaelyan's discussion Hot Upper Stories
"The most bang for your buck will come from airsealing the attic plane and sealing the…"
17 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service