Massachusetts is supposed to adopt the 2012 IECC by July or August, 2013.  When that occurs, ceiling insulation will go to 49, basement or crawl space walls will be at 15 continuous or 19 cavity, and blower door testing will be required.  House tightness increases from 7 ACH50 to 3 ACH50.  That is pretty tight.  Post construction duct tightness goes from 12% Total leakage to 4% Total leakage.  The rough in tightness with no air handler goes from 4% to 3%.

I just tested a small addition this week: 465 square feet.  I tested the ducting on rough-in with no air handler.  At 4% the leakage limit was 18.6 cfm.  Good contractor.  Joints nicely taped.  The leakage was 29 cfm.  That meant that he had to find holes the size of (3) ball point pen diameters!  He did.  And that posed another problem.

At those low leakage numbers, the duct tester couldn't give me a reading.  I had to increase the pressure up to over 50 Pascals before I got an airflow reading.  To get an accurate number at 25 Pascals, I will have to decrease the size of the ring on my duct tester.

The point is that when the requirement drops to 3% at rough in, the flow will be 45 for a 1500 square foot house and that will start to be marginal with the equipment.

But are we ready for 3 ACH50 homes?  Remember that the existing Stretch Code is 7 ACH50.

Views: 41

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Profile Iconrichard m, Steve Taylor, John Ferrado and 2 more joined Home Energy Pros
27 minutes ago
Taylor Tomita posted a blog post
51 minutes ago
robert jones replied to Judy Rachel's discussion Equipment for Sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hello, is this equipment still available?"
2 hours ago
robert jones replied to CHRISTOPHER PETERSEN's discussion Complete Energy Auditing Kit For Sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hello. Are these items still there?"
2 hours ago
Kurtis Pender joined Diane Chojnowski's group
Thumbnail

Hall of Shame

In this group, members share an array of images from the field, showing the kinds of issues…See More
3 hours ago
Kurtis Pender joined Leslie McDowell, BPI's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
3 hours ago
Profile IconKurtis Pender and Colin Genge joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
3 hours ago
Kurtis Pender joined Michael Stuart's group
Thumbnail

INFRARED THERMOGRAPHY USERS

This group is dedicated to knowledge sharing and discussion of infrared thermography for building…See More
3 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service