Massachusetts is supposed to adopt the 2012 IECC by July or August, 2013.  When that occurs, ceiling insulation will go to 49, basement or crawl space walls will be at 15 continuous or 19 cavity, and blower door testing will be required.  House tightness increases from 7 ACH50 to 3 ACH50.  That is pretty tight.  Post construction duct tightness goes from 12% Total leakage to 4% Total leakage.  The rough in tightness with no air handler goes from 4% to 3%.

I just tested a small addition this week: 465 square feet.  I tested the ducting on rough-in with no air handler.  At 4% the leakage limit was 18.6 cfm.  Good contractor.  Joints nicely taped.  The leakage was 29 cfm.  That meant that he had to find holes the size of (3) ball point pen diameters!  He did.  And that posed another problem.

At those low leakage numbers, the duct tester couldn't give me a reading.  I had to increase the pressure up to over 50 Pascals before I got an airflow reading.  To get an accurate number at 25 Pascals, I will have to decrease the size of the ring on my duct tester.

The point is that when the requirement drops to 3% at rough in, the flow will be 45 for a 1500 square foot house and that will start to be marginal with the equipment.

But are we ready for 3 ACH50 homes?  Remember that the existing Stretch Code is 7 ACH50.

Views: 38

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Steve Waclo posted a discussion

Underperforming? Energy Efficiency of HVAC Equipment Suffers Due to Poor Installation

Hello all,A search of the site seems to indicate this recently published study from NIST has not…See More
3 hours ago
Steve Waclo joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
3 hours ago
Bob Blanchette posted a discussion

Dual Fuel Systems, at what point do they make sense?

Heat Pump with furnace backup. These make no sense in our area with local NG rates, but they do…See More
17 hours ago
Bob Blanchette joined Hal Skinner's group
Thumbnail

The RCC Classroom (Radiant Control Coatings)

A group where energy professionals can learn about all the different energy saving aspects of…See More
17 hours ago
Shashank Kirloskar posted a blog post

Important Facts about Solar Energy

“I’d put my money on the sun and solar energy. What a source of power! I hope we don’t have to wait…See More
Thursday
reflintorm replied to Dennis McCarthy's discussion Solid state lighting - saves lives- and it improves life .
"In my observation, In most of the lightning appliances led bulbs are used because of their…"
Thursday
Chad Mcaulife posted photos
Wednesday
Bob Blanchette commented on Jeremy Begley's blog post The Home Envelope : Does it Really Matter in a Heat Loss Calculation
"Infiltration makes a HUGE difference. Look at the heat loads on a windy day vs. a calm one. On a…"
Wednesday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service