Massachusetts is supposed to adopt the 2012 IECC by July or August, 2013.  When that occurs, ceiling insulation will go to 49, basement or crawl space walls will be at 15 continuous or 19 cavity, and blower door testing will be required.  House tightness increases from 7 ACH50 to 3 ACH50.  That is pretty tight.  Post construction duct tightness goes from 12% Total leakage to 4% Total leakage.  The rough in tightness with no air handler goes from 4% to 3%.

I just tested a small addition this week: 465 square feet.  I tested the ducting on rough-in with no air handler.  At 4% the leakage limit was 18.6 cfm.  Good contractor.  Joints nicely taped.  The leakage was 29 cfm.  That meant that he had to find holes the size of (3) ball point pen diameters!  He did.  And that posed another problem.

At those low leakage numbers, the duct tester couldn't give me a reading.  I had to increase the pressure up to over 50 Pascals before I got an airflow reading.  To get an accurate number at 25 Pascals, I will have to decrease the size of the ring on my duct tester.

The point is that when the requirement drops to 3% at rough in, the flow will be 45 for a 1500 square foot house and that will start to be marginal with the equipment.

But are we ready for 3 ACH50 homes?  Remember that the existing Stretch Code is 7 ACH50.

Views: 47

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Amber Vignieri posted a blog post
1 hour ago
Evan Mills posted a blog post

Looking Back and Looking Forward: Home Energy Pros at 5 and 5000

Over the past five years, the Home Energy Pros social network has grown from a twinkle in our eyes…See More
2 hours ago
tedkidd replied to Diane Chojnowski's discussion Poll: How confident do you feel about the future of home performance?
"Thank you for sharing this trend! Full disclosure, I did NOT ask Bob to post that! If you have 2…"
3 hours ago
Bob Blanchette replied to Diane Chojnowski's discussion Poll: How confident do you feel about the future of home performance?
"I see fixed monthly grid charges continuing to increase while cost per therm/kwh/gallon remain…"
3 hours ago
Quinn Korzeniecki posted a discussion

Vent Cap Systems and SENSIT Technologies Products Added to BPI Product List

The Building Performance Institute, Inc. (BPI) has recognized four new products in its …See More
5 hours ago
Simon joined Diane Chojnowski's group
Thumbnail

Online Training

Online training coursesIf you provide ongoing online training for home performance or…See More
yesterday
Simon added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Wanted - Blower and door frame kit for Minneapolis system

Hi everyone,I'm new to this line of work and have bought some equipment (Minneapolis blower door…See More
yesterday
Simon replied to Steve Mann's discussion TEC Blower Door Frame in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi, I'm interested, but could you send to UK?,I'd pay shipping of course. My email is :-…"
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service