Massachusetts is supposed to adopt the 2012 IECC by July or August, 2013.  When that occurs, ceiling insulation will go to 49, basement or crawl space walls will be at 15 continuous or 19 cavity, and blower door testing will be required.  House tightness increases from 7 ACH50 to 3 ACH50.  That is pretty tight.  Post construction duct tightness goes from 12% Total leakage to 4% Total leakage.  The rough in tightness with no air handler goes from 4% to 3%.

I just tested a small addition this week: 465 square feet.  I tested the ducting on rough-in with no air handler.  At 4% the leakage limit was 18.6 cfm.  Good contractor.  Joints nicely taped.  The leakage was 29 cfm.  That meant that he had to find holes the size of (3) ball point pen diameters!  He did.  And that posed another problem.

At those low leakage numbers, the duct tester couldn't give me a reading.  I had to increase the pressure up to over 50 Pascals before I got an airflow reading.  To get an accurate number at 25 Pascals, I will have to decrease the size of the ring on my duct tester.

The point is that when the requirement drops to 3% at rough in, the flow will be 45 for a 1500 square foot house and that will start to be marginal with the equipment.

But are we ready for 3 ACH50 homes?  Remember that the existing Stretch Code is 7 ACH50.

Views: 37

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Michael Dunseith posted a photo

http://www.prattcenter.net/energy-champions-launch-party

Senator Kevin Parker poses with Pratt Center's Green Jobs Green New York Project Coordinator Elana…
5 hours ago
Michael Dunseith posted a status
5 hours ago
Rob Madden, Solar Home Broker posted a blog post

Phoenix 3rd Quarter Solar Resale Statistics Continue to Impress

Phoenix solar home sales were up during the third quarter of 2014, including the resale of homes…See More
22 hours ago
Everblue posted a status
"Green job alert! Energy Auditor in Baltimore, MD with Advanced Green Home Solutions. Check it out: http://bit.ly/1xhQuXO"
23 hours ago
Chris Clay replied to Isaiah Borel's discussion Blown Cellulose VS Blown Fiberglass in the Attic
"The Cold Climate Housing Research Center in Fairbanks, AK has alot of information about this…"
23 hours ago
Richard L. Sanderson replied to Bud Poll's discussion Inconsistant Local Authority
"Bud: I like the idea of a third party review board. My own experience in local government is that…"
yesterday
Matthew Lutz commented on Kaplan Clean Tech's blog post The Difference Between Home Inspection and Energy Auditing [Infographic]
"I would have to agree with Steve on this.  I am a Certified Energy Manager and have performed…"
yesterday
Matthew Lutz joined Diane Chojnowski's group
Thumbnail

Hall of Shame

In this group, members share an array of images from the field, showing the kinds of issues…See More
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service