I got this email from a QA program manager. Looking for feedback. Thanks

 

 

I have a question for you I'm hoping you can shed some light on.

How are we supposed to proceed with getting combustion and worst case depressurization numbers from an area that is inaccessible?

I just ran into this situation over at customer's home with a tankless water heater on his second floor.
The only option to get a flue gas sample is to set up an extension ladder in an alley which doesn't have clearances that are proper for an extension ladder.

Look forward to hearing how you would proceed on this.

Views: 43

Replies to This Discussion

 

You should be able to access the room where the water heater itself is located.  Otherwise if it is in some kind of sealed off space, then it probably doesn't meet code requirements.  So you should be able to do a worst case depressurization test on the CAZ.  Although since it is sealed combustion, it is probably not a big deal. 

 

I think a lot of programs will waive requirements to get a CO reading on the flue gases if the appliance is condensing and/or sealed combustion, and the flue vents out the roof and is not easily accessible. 

 

I'd agree w/ the previous post. When going for a worst case test, you only need to measure presssure difference in the CAZ WRT outside. I'm figuring you can get into the CAZ. If required, Measuring exhaust gas for CO and efficiency on a sealed appliance is done from the outside according to most, though several well known pro's will drill the PVC pipe and sample from there, then seal the pipe with fire rated caulk.   
Thanks folks. The culprit here is an older tankless that is not sealed combustion.

If the tankless water heater is not sealed combustion, then it could be either power vented (one PVC pipe), induced draft (inducer motor and metal pipe), or natural draft (with draft hood).  I am not comfortable drilling a PVC pipe to measure CO, but some will drill it and seal it with silicone caulk.  A metal pipe for an induced draft appliance can be drilled and plugged with a metal plug or taped with metal tape.  If it is natural draft, you can measure the CO by putting the probe down in the heat exchanger from the draft hood.

This is what we do:  The Standards are clear:  No air sealing, dense packing more than 15% of the shell area, duct sealing outside the thermal envelope, if you cannot complete the or combustion testing protocol.  So, if we cannot test all the appliances that might be affected by modified house pressures due to air sealing, than we don't recommend air sealing.  More accurately, we explain the issues on the work order and customer report.  If we get full access to the entire building, so we can create worst case conditions in all CAZ's, and we can test to the Standards, then we include air sealing on the work order (if apporpriate).   Also... yes, we've climbed ladders to take samples from flue gasses... but of course we prefer to drill and fill where allowed!

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Evan Mills replied to Sandra K. Adomatis, SRA's discussion Green Mortgage Appraisal Roundtable
"Would love see your slides, but the AI site requires login.  Can you post them here or email…"
2 hours ago
Colin Genge posted a blog post

What needs to be done to get builders to follow Code for duct and envelope leakage?

“Have you been ripped off for $100,000 by your builder?  Let us help you get what you paid for! …See More
8 hours ago
Green Training USA posted an event
Thumbnail

Proctor’s Without Borders at Online

July 29, 2015 to August 7, 2015
Complete your training at your own pace and take exams when you want and where you want. No…See More
17 hours ago
Gar Swaffar commented on Gar Swaffar's blog post Cost of using a BPI QCI?
"Ip.s., I would presume there will be a difference between the Left Coast and nearly everywhere else."
yesterday
Gar Swaffar posted a blog post

Cost of using a BPI QCI?

I'd like to find out if there is a consensus on a rule of thumb cost of a QCI onsite for…See More
yesterday
Gar Swaffar is now a member of Home Energy Pros
yesterday
Colin Genge posted an event

Infiltration and Duct Leakage with BPI at Online

July 30, 2015 from 1pm to 2pm
Blower door and duct test requirementsCalculating resultsCertification optionsTest preparation and…See More
yesterday
Stacy Hunt posted an event

Volunteers needed for the upcoming U.S. Department of Energy Solar Decathlon in Irvine, CA at Orange County Great Park

October 8, 2015 at 11am to October 18, 2015 at 7pm
Volunteer for the upcoming U.S. Department of Energy Solar Decathlon 2015, taking place Oct. 8-18…See More
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service