I got this email from a QA program manager. Looking for feedback. Thanks

 

 

I have a question for you I'm hoping you can shed some light on.

How are we supposed to proceed with getting combustion and worst case depressurization numbers from an area that is inaccessible?

I just ran into this situation over at customer's home with a tankless water heater on his second floor.
The only option to get a flue gas sample is to set up an extension ladder in an alley which doesn't have clearances that are proper for an extension ladder.

Look forward to hearing how you would proceed on this.

Views: 24

Replies to This Discussion

 

You should be able to access the room where the water heater itself is located.  Otherwise if it is in some kind of sealed off space, then it probably doesn't meet code requirements.  So you should be able to do a worst case depressurization test on the CAZ.  Although since it is sealed combustion, it is probably not a big deal. 

 

I think a lot of programs will waive requirements to get a CO reading on the flue gases if the appliance is condensing and/or sealed combustion, and the flue vents out the roof and is not easily accessible. 

 

I'd agree w/ the previous post. When going for a worst case test, you only need to measure presssure difference in the CAZ WRT outside. I'm figuring you can get into the CAZ. If required, Measuring exhaust gas for CO and efficiency on a sealed appliance is done from the outside according to most, though several well known pro's will drill the PVC pipe and sample from there, then seal the pipe with fire rated caulk.   
Thanks folks. The culprit here is an older tankless that is not sealed combustion.

If the tankless water heater is not sealed combustion, then it could be either power vented (one PVC pipe), induced draft (inducer motor and metal pipe), or natural draft (with draft hood).  I am not comfortable drilling a PVC pipe to measure CO, but some will drill it and seal it with silicone caulk.  A metal pipe for an induced draft appliance can be drilled and plugged with a metal plug or taped with metal tape.  If it is natural draft, you can measure the CO by putting the probe down in the heat exchanger from the draft hood.

This is what we do:  The Standards are clear:  No air sealing, dense packing more than 15% of the shell area, duct sealing outside the thermal envelope, if you cannot complete the or combustion testing protocol.  So, if we cannot test all the appliances that might be affected by modified house pressures due to air sealing, than we don't recommend air sealing.  More accurately, we explain the issues on the work order and customer report.  If we get full access to the entire building, so we can create worst case conditions in all CAZ's, and we can test to the Standards, then we include air sealing on the work order (if apporpriate).   Also... yes, we've climbed ladders to take samples from flue gasses... but of course we prefer to drill and fill where allowed!

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner replied to Tony Rigdon's discussion Placement of 5/8" firewall, over or under foam board insulation?
"Found an article that might help …"
4 hours ago
Bud Poll replied to Tony Rigdon's discussion Placement of 5/8" firewall, over or under foam board insulation?
"Hi Tony, what/where is your climate?  Also, how is the rest of the wall constructed? Adding…"
4 hours ago
Sean Lintow Sr replied to Tony Rigdon's discussion Placement of 5/8" firewall, over or under foam board insulation?
"contact the local AHJ for sure - but for "fire" reasons it should be on the outside…"
7 hours ago
Tony Rigdon posted a discussion

Placement of 5/8" firewall, over or under foam board insulation?

I'm adding onto my personal residence and since the house is within five feet of the property line,…See More
8 hours ago
Hal Skinner replied to Hal Skinner's discussion Rooftop A/C units and exposed ductwork in the group The RCC Classroom (Radiant Control Coatings)
"Hi Tom.   As far as media advertising goes for the good RCCs, it really doesnt work well at…"
10 hours ago
Sean Lintow Sr commented on Chris Laumer-Giddens's blog post Mini-Split Heat Pumps are Quirky, Especially their Capacity
"Quick question Chris - the set & forget (for temperature setbacks) is that with any or just…"
12 hours ago
Martin Smith joined Hal Skinner's group
Thumbnail

The RCC Classroom (Radiant Control Coatings)

A group where energy professionals can learn about all the different energy saving aspects of…See More
14 hours ago
Anthony Cox added a discussion to the group Job Board
Thumbnail

PROJECT MANAGER/BUILDING SCIENCE TRAINER Community Housing Partners Christiansburg, VA

We are hiring and below is link to apply for the position we have available at Community Housing…See More
14 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service