I got this email from a QA program manager. Looking for feedback. Thanks

 

 

I have a question for you I'm hoping you can shed some light on.

How are we supposed to proceed with getting combustion and worst case depressurization numbers from an area that is inaccessible?

I just ran into this situation over at customer's home with a tankless water heater on his second floor.
The only option to get a flue gas sample is to set up an extension ladder in an alley which doesn't have clearances that are proper for an extension ladder.

Look forward to hearing how you would proceed on this.

Views: 43

Replies to This Discussion

 

You should be able to access the room where the water heater itself is located.  Otherwise if it is in some kind of sealed off space, then it probably doesn't meet code requirements.  So you should be able to do a worst case depressurization test on the CAZ.  Although since it is sealed combustion, it is probably not a big deal. 

 

I think a lot of programs will waive requirements to get a CO reading on the flue gases if the appliance is condensing and/or sealed combustion, and the flue vents out the roof and is not easily accessible. 

 

I'd agree w/ the previous post. When going for a worst case test, you only need to measure presssure difference in the CAZ WRT outside. I'm figuring you can get into the CAZ. If required, Measuring exhaust gas for CO and efficiency on a sealed appliance is done from the outside according to most, though several well known pro's will drill the PVC pipe and sample from there, then seal the pipe with fire rated caulk.   
Thanks folks. The culprit here is an older tankless that is not sealed combustion.

If the tankless water heater is not sealed combustion, then it could be either power vented (one PVC pipe), induced draft (inducer motor and metal pipe), or natural draft (with draft hood).  I am not comfortable drilling a PVC pipe to measure CO, but some will drill it and seal it with silicone caulk.  A metal pipe for an induced draft appliance can be drilled and plugged with a metal plug or taped with metal tape.  If it is natural draft, you can measure the CO by putting the probe down in the heat exchanger from the draft hood.

This is what we do:  The Standards are clear:  No air sealing, dense packing more than 15% of the shell area, duct sealing outside the thermal envelope, if you cannot complete the or combustion testing protocol.  So, if we cannot test all the appliances that might be affected by modified house pressures due to air sealing, than we don't recommend air sealing.  More accurately, we explain the issues on the work order and customer report.  If we get full access to the entire building, so we can create worst case conditions in all CAZ's, and we can test to the Standards, then we include air sealing on the work order (if apporpriate).   Also... yes, we've climbed ladders to take samples from flue gasses... but of course we prefer to drill and fill where allowed!

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Bud Poll posted a discussion

How do we pay for the grid?

Ok, so some electric utilities are charging some form of up front and/or monthly added charge for…See More
1 hour ago
Colin Genge's video was featured

Passive House Testing Webinar (Feb 13, 2014)

We covered: - Measuring air leakage in a tight house; - New passive house testing equipment; - Powered flow hoods for accurate measurement of HRV ERV flow ra...
4 hours ago
Colin Genge posted events
11 hours ago
John Nicholas replied to Sean Lintow Sr's discussion Duct Testing - is a change in order? in the group Best Practices (Residential)
"Yes,  I was connected to the AH cabinet.  I find it easier in this area, given the common…"
13 hours ago
Colin Genge replied to Kim Tanner's discussion Blower Door Applications Guide in the group Multifamily Buildings
"This is a great guide that anyone testing with multiple fans should get hold  of. "
14 hours ago
Colin Genge added a discussion to the group Multifamily Buildings
Thumbnail

Just posted a lot of Multi-Family oriented blower door videos.

Just posted a lot of Multi-Family oriented blower door videos. Everything to do with Multi-Fan…See More
14 hours ago
Colin Genge joined Norm Bourassa's group
Thumbnail

Multifamily Buildings

For too long there has been relatively little EE focus on multifamily, but some new programs have…See More
14 hours ago
Colin Genge replied to Sean Lintow Sr's discussion Duct Testing - is a change in order? in the group Best Practices (Residential)
"I would assume you tested that high air leakage from the equipment cabinet and not on a flex…"
14 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service