I am involved in a QC program that straddles two of the four zones BPI uses to identify LBL "N" factors. Has anyone ever seen a map with enough resolution that could help determine whether a project lands in one zone or another? My area of concern is the division between zones 3 and 4 in southern California.  

Has anyone correlated the LBL N-factor zones with California Energy Commission climate zones?

With a requirement to meet ASHRAE standards, the 15% factor difference between zones could be significant.

Views: 1364

Replies to This Discussion

If you are in doubt, just use the middle value common to both zone 3 and 4:  23. 

 

The whole formula isn't all that precise anyways.  The N factors for each zone are a range of four numbers - that should tell you something.  Using the lower number will allow you to seal up a house tighter without having to do ASHRAE 1989.   But to meet ASHARE 62.2 - 2010, you probably have to install some kind of ventilation anyways - the only question is what cfm rate to set the fan at.

 

If you want to be more precise, use ASTM 779 and ASHRAE Standards 119 and 136 to calculate your own N factor instead of using that burry map.

 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Bijou Lulla posted a blog post

ENERGY EFFICIENCY RETROFITS.....IN NUMBERS WE TRUST

There has been much ado about the recent paper published by E2e; Do Energy Efficiency Investments…See More
11 hours ago
Mariusz Chorazy posted a blog post

Here are a few tips to keep your air conditioning bill low

TAKE GOOD CARE OF YOUR AIR CONDITIONER – Like any major appliance, your AC requires regular…See More
yesterday
Dale Pickard replied to Rod Fox's discussion Does altitude affect AFUE? or just the input/output BTUs?
"Morgan, I got this below from the Knight installation manual. I note a few things, -These…"
yesterday
Dale Pickard replied to Rod Fox's discussion Does altitude affect AFUE? or just the input/output BTUs?
"Hans, The car manufacturer's are doing it with mass flow sensors and oxygen sensors…"
Saturday
Dale Pickard replied to Rod Fox's discussion Does altitude affect AFUE? or just the input/output BTUs?
"I was trying to avoid naming manufacturers, but I was going by the published information for the…"
Saturday
Eric Kjelshus replied to Rod Fox's discussion Does altitude affect AFUE? or just the input/output BTUs?
"I look at this not about AFUE,  but flue gas dewpoint.  If your burn rate is rotting the…"
Saturday
Bob Blanchette replied to Kirsten Richnavsky's discussion Crawl spaces and attics: OSHA to implement new rule on confined spaces
"Keeping HVAC equipment out of attics should be part of the new code. "
Saturday
Linda Wigington replied to Linda Wigington's discussion Weigh in - Honorable Mention? 2nd Base? Half-Way There? 50% Better? On the Path? in the group 1000 Home Challenge
"Nickie -  Good points. I think it is easy enough to flag or designate projects that achieve…"