Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 11

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

tedkidd replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"Pat, I think you and I agree on a LOT of things.   One thing I don't want to see is more…"
7 hours ago
tedkidd commented on Tom Delconte's blog post Robert Shiller Says Retrofits Are Never Worth It!
"Bob B.   Buying a home is a good investment because it is forced savings more than a good…"
9 hours ago
Joe Huang posted a discussion

White Box Technologies launches Web-based weather data for building energy simulations

White Box Technologies is pleased to announce under agreement with ASHRAE the launch of WBT Weather…See More
9 hours ago
Tom Delconte commented on Tom Delconte's blog post Lykans $29, Vampires $0 !
"Bill: these are available for free at www.freeenergy.com . Just ask for Jen Guarater! I…"
10 hours ago
Joseph Lamy commented on Jim Gunshinan's blog post The Universe Is Made of Stories
"My life changed when I got 'ductalatored' - became familiar with proper sizing guides for…"
10 hours ago
J.C. Martel replied to J.C. Martel's discussion Disasters & sustainable energy
"Thanks Dennis."
11 hours ago
Judi Lyall joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
yesterday
Judi Lyall replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi there I am selling my equipment and have a great Fluke TIR for sale for 3600.00    If…"
yesterday
William H Nickerson commented on Tom Delconte's blog post Lykans $29, Vampires $0 !
"66 watts a/sec  -3960 w/min   237600 w/hr   5702400  w/day …"
yesterday
tedkidd commented on Jim Gunshinan's blog post The Universe Is Made of Stories
"I think Tom is busting your chops Jim.  The "drivel" part may not have been well…"
yesterday
Tom Maides commented on Jim Gunshinan's blog post The Universe Is Made of Stories
"Some of the best scientists of the previous 1000 years were also leaders in the Church.  Aside…"
yesterday
Laurie DiDonato posted an event

HERS Rater Training in Massachusetts at Maki Building Center

June 3, 2013 to June 8, 2013
6-Day HERS Rater Training- The first step to becoming a HERS RaterLast Week To Register!Your Cost…See More
yesterday

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service