    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 29

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Todd St.Clair joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
49 minutes ago
Todd St.Clair replied to Jim Falakos's discussion Treat Software in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"How long ago did you buy this, if it was good for 5 months? And how much would you take for this."
49 minutes ago
Bud Poll replied to Bud Poll's discussion Basing air exchange on house volume??
"Hi Sean, yes I am struggling with this and that is why I opened the discussion, so a definite…"
2 hours ago
Lynda Wright is now a member of Home Energy Pros
3 hours ago
Sean Lintow Sr replied to Bud Poll's discussion Basing air exchange on house volume??
"Sorry Bud but I think you need to clarify your issues with using volumes to calculate ACH As for…"
14 hours ago
Profile IconWes Anderson, Jean-Paul and Bryan joined Home Energy Pros
Friday
Dennis Heidner commented on Dale Stephens's blog post LED Lighting 24-month update 18,240 hours & counting
"Dale, good write up. For the landscaping bulbs,  if they had been T3 12V wedge bulbs,  I…"
Friday
Brett Little commented on Tom White's video
Thumbnail

The Future of Housing - And How Airtightness Can Help

"It's very true! So many people and contractors have tons of insulated attics but no air seal…"
Thursday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service