Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 42

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Latest Activity

Chad Nicholson is now a member of Home Energy Pros
Friday
Eric Kjelshus replied to Energy Wise Solutions's discussion What causes a temperature plane in a home
"Hot air goes up and cool air goes down.   I put in returns high and low.  In summer use…"
Friday
John Nicholas replied to Luis Hernandez's discussion Solar panel leasing
"The variables in buying a solar panel installation: Equipment -  Length of all Guarantees,…"
Friday
Richard Drohan liked Brian Sipp's discussion Minneapolis Duct Blaster System with DG-700 For Sale
Thursday

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service