Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 31

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Don Fitchett posted a blog post
11 hours ago
Benny hani replied to Benny hani's discussion Software
"Thank you so much for your help."
12 hours ago
Sean Lintow Sr replied to Benny hani's discussion Software
"At minimum a personal CO detector, 1 blower door, 1 duct tester, 2 manometers - other equipment…"
17 hours ago
Greg Hannah posted a blog post
18 hours ago
Richardson Fred posted a discussion
yesterday
Benny hani replied to Benny hani's discussion Software
"Hello Sean I am about to purchase the equiptments needed to Start my business. I am going to be…"
yesterday
romeo traian replied to w d's discussion AERC testing and Solar Grates update
"w d, i visited your site... interesting... could you please say something more... re the…"
yesterday
Chie Kawahara replied to Linda Wigington's discussion Weigh in - Honorable Mention? 2nd Base? Half-Way There? 50% Better? On the Path? in the group 1000 Home Challenge
"Hi Linda, Using the word "evergreen" I intended to convey the notion of topics that are…"
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service