Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 28

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Craig Bird commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Correct, that is exactly what I said"
34 minutes ago
Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"At 1.7% enterng the structure, that Radiant barrier is now going to allow the R-rated insulation/s…"
1 hour ago
Craig Bird commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"And how much of that 1.7% of the suns energy that got through the RB or RCC gets into the house,…"
1 hour ago
Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"OK.  This might be rudamentary here.  I want to make sure everyone understands how SOLAR…"
1 hour ago
Craig Bird commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Hal - I would disagree that radiant heat "goes through" fibrous insulation. Radiant heat…"
1 hour ago
Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Hi KLurt. I would isagree with the comment that the attic floor is heated by the…"
2 hours ago
Craig Bird commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Now back to your question - the best data for radiant barriers is the DOE studies from the ORNL.…"
2 hours ago
Kevin Jordan posted a discussion

Does anyone have pointers on approaching real estate induatry.

Hello All!!I am figuring on approaching the real estate and low income housing industries here in…See More
2 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service