Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 42

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Latest Activity

Green ID posted blog posts
3 hours ago
Home Energy Magazine's blog post was featured

New Report Shows Big Jump in Net-Zero Energy Homes

Net-zero energy homes seem to be growing their way out of a purely niche market. The number of zero…See More
4 hours ago
Home Energy Magazine posted a blog post

New Report Shows Big Jump in Net-Zero Energy Homes

Net-zero energy homes seem to be growing their way out of a purely niche market. The number of zero…See More
5 hours ago
Mihaita commented on Chris Laumer-Giddens's blog post What do Ducted Mini-Splits Look Like?
"Amazing, i bought my AC here."
12 hours ago

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service