Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 28

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Steven Lewis replied to Christopher Talarico's discussion Heating with Tankless Water Heater & Hydronic Air Handler vs. Gas Furnace
"It looks better on paper than in real life applications.  Both Amana and Lennox came out with…"
16 hours ago
Dennis Heidner replied to Christopher Talarico's discussion Heating with Tankless Water Heater & Hydronic Air Handler vs. Gas Furnace
"Rinnai has application note on how to use their tankless hot water heater with a Rinnai water to…"
yesterday
Hal Skinner replied to Hal Skinner's discussion How much heat energy is lost through the floor of a house?
"I found the buildingscience article interesting.  Interesting that they noted the wet bottom…"
yesterday
Bud Poll replied to Hal Skinner's discussion How much heat energy is lost through the floor of a house?
"With conduction that ends at the bottom of the joists and convection that is naturally suppressed…"
yesterday
Hal Skinner replied to Hal Skinner's discussion How much heat energy is lost through the floor of a house?
"Good morning Bud, Took a quick look at the site and a couple others listed on the Yahoo…"
yesterday
Bud Poll replied to Hal Skinner's discussion How much heat energy is lost through the floor of a house?
"Hi Hal, Search "Basecalc basement heat loss".  From memory Canada (nrcan) has/had a…"
yesterday
Michael Dunseith posted photos
Saturday
Hal Skinner replied to Hal Skinner's discussion How much heat energy is lost through the floor of a house?
"II just remembered seeing a report by a federal adency, many years ago, that basically said …"
Saturday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service