Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 31

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Profile IconAmanda Hallock, Kalvis, Tyler Grubbs and 6 more joined Home Energy Pros
20 minutes ago
Corbett Lunsford posted videos
58 minutes ago
Sean Lintow Sr replied to randy tolowski's discussion Another unvented roof question
2 hours ago
randy tolowski posted discussions
3 hours ago
Todd Collins replied to Tom Strumolo's discussion Ancient (70's) wall foam insulation, now a powder.
"What did you find about the dust?  "
7 hours ago
Susan E. Buchan commented on Shawna Henderson's blog post Drainwater Heat Recovery Units & Water Efficiency
"Makes sense, Shawna. Thanks"
7 hours ago
Shawna Henderson commented on Shawna Henderson's blog post Drainwater Heat Recovery Units & Water Efficiency
"Susan, I'm not sure that insulation on the unit would be of great benefit, as the drainwater…"
7 hours ago
Susan E. Buchan posted events
7 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service