Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 30

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Ben Jacobs replied to Mike Kandel's discussion Have you heard!? BPI's BSP Certificate Approved as Home Energy Score Prerequisite!
"I am very pleased to see the collaboration between the Building Performance Institute (BPI) and the…"
17 hours ago
Profile IconComly Wilson, Pete Stoermer, Billy Ray Griffin and 1 more joined Home Energy Pros
18 hours ago
Stan Kuhn replied to Mike Kandel's discussion Have you heard!? BPI's BSP Certificate Approved as Home Energy Score Prerequisite in the group Building Performance Institute (BPI)
"Mike, are there any statistics on the number of HES ratings performed, by all providers?"
21 hours ago
Mike Kandel added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Have you heard!? BPI's BSP Certificate Approved as Home Energy Score Prerequisite

The Building Performance Institute's Building Science Principles (BSP) Certificate of Knowledge has…See More
21 hours ago
Mike Kandel posted a discussion

Have you heard!? BPI's BSP Certificate Approved as Home Energy Score Prerequisite!

The Building Performance Institute's Building Science Principles (BSP) Certificate of Knowledge has…See More
21 hours ago
Shawna Henderson posted a status
"New Blog Post @HomeEnergyMag Why I like Dumb, Do-Nothing Houses http://shar.es/1WSOIX"
21 hours ago
Larry Gorman posted a discussion

Hobo Data loggers for sale

I have recently retired and no longer have need of these, which are all in like new condition.  I…See More
22 hours ago
Laurel Elam posted a blog post

Over 146,000 Homes in the U.S. were HERS Rated and issued a HERS Index Score in 2014

In 2014 there were 146,860 homes in the United States that were energy rated by certified RESNET…See More
23 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service