    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 38

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Michael Wenzel is now a member of Home Energy Pros
6 hours ago
Stan Harbuck added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

4 Fans, Doors, Gauges, etc. for Sale - 4 Q4E 3300 Retrotec Fans, Doors, Drivers, etc.

4 Rarely used Q4E 3300 Retrotec fan sets (2010/2011) and all related equipment for sale, including…See More
9 hours ago
Stan Harbuck joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
10 hours ago
Amber Vignieri posted a blog post
yesterday
Barbara Smith's video was featured

Weatherization: Crawl Spaces

Crawl Spaces - Training for Weatherization Installers. Re-posted from Seventhwave.org
yesterday
Kelly replied to Colin Genge's discussion What is the value of using a pressure pan to test outlets?
"Hi Colin, I like using the pressure pans at outlets to guide my inspections once I'm in the…"
Thursday
Leo Klisch commented on Home Energy Magazine's blog post Natural Gas is Becoming Less Attractive
"It seems a bit wasteful to use NG for such a low temperature application as space heat. If a heat…"
Thursday
HomeWiz posted photos
Thursday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service