Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 28

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Kurt, check your emails.  Sent you a friend request you need to confirm then I can send you a…"
6 hours ago
Kevin Jordan replied to Kevin Jordan's discussion Does anyone have pointers on approaching real estate induatry.
"thank you sir!! If you have any other tips Id appreciate. I am new in this industry and I go and…"
7 hours ago
Bud Poll replied to Kurt Shafer's discussion Where can I find the best radiant barrier to install under my roof?
"Hi Kurt, You mentioned "On a RESNET discussion some insulation experts agreed that insulation…"
8 hours ago
Kurt Shafer commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Wow, I am very sad to hear about your eyes.  Would have been super to do that comparison. Good…"
8 hours ago
Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"My dads house has an attached garage.  It was converted to living space around 20 years…"
8 hours ago
Kurt Shafer commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Hal, do I see a terrific chance for you to show us all the power of your RCC? Your father's…"
9 hours ago
Hal Skinner replied to Kevin Jordan's discussion Does anyone have pointers on approaching real estate induatry.
"Kevin, Several years ago I worked closely with a general contractor and a real estate…"
9 hours ago
Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"That same RCC, used as paint on the ceiling of living space, will do the same as if it was applied…"
9 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service