Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 31

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Steven Lewis replied to William Fisher's discussion Can tankless water heaters provide hot water even when the groundwater is fairly cold?
"Look at reducing the ambient humidity in the home.  The dew point is the key to the…"
yesterday
Olivia Taylor posted blog posts
yesterday
norman farwell replied to Bryan Pringle's discussion Dense packed cellulose in basement?
"Ha, we're on the same wavelength.  That's the big question--I'm still thinking…"
Thursday
Bryan Pringle replied to Bryan Pringle's discussion Dense packed cellulose in basement?
"Thanks Norm, we'll have a couple of case studies when all is said and done. Just curious, do…"
Thursday
norman farwell replied to Bryan Pringle's discussion Dense packed cellulose in basement?
"Bryan,  I am trying the same thing for most of the same reasons and also against advice to the…"
Thursday
Morgan M Audetat commented on Sean McLoughlin's blog post Programming in-floor electric radiant heat, is it worth it?
"You would need a large bathroom to see the difference. We install them both ways depending on the…"
Thursday
Dennis Heidner commented on Sean McLoughlin's blog post Programming in-floor electric radiant heat, is it worth it?
"The key is that this is the bathroom.  Occupancy is not constant.  It is more likely used…"
Thursday
Charles Cormany commented on Sean McLoughlin's blog post Programming in-floor electric radiant heat, is it worth it?
"I have seen resistance floor heaters add nearly $100 per month to an electric bill. Since most…"
Thursday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service