Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 28

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

George Kopf posted discussions
1 hour ago
Profile IconSharon Cannizzo, Katrina Ball, Mary Patterson and 1 more joined Home Energy Pros
3 hours ago
Craig Bird replied to Hal Skinner's discussion What this RCC will do on an exterior wall compared to standard paint. in the group The RCC Classroom (Radiant Control Coatings)
"I agree and studies done will agree with you in those cases too - it makes sense when there is…"
13 hours ago
Hal Skinner replied to Hal Skinner's discussion What this RCC will do on an exterior wall compared to standard paint. in the group The RCC Classroom (Radiant Control Coatings)
"You might want to check out this discussion in my…"
17 hours ago
Craig Bird replied to Hal Skinner's discussion What this RCC will do on an exterior wall compared to standard paint. in the group The RCC Classroom (Radiant Control Coatings)
"In this scenario the walls were made of R35 rigid foam. Even if ex-employee of big energy company…"
18 hours ago
Sean Lintow Sr replied to Kevin Jordan's discussion air infiltration total
"Sorry I don't have anything handy but pull a search for EqLA equivalent leakage…"
Sunday
Erik Henson commented on Andrew Navolio's blog post MEEA assists with Home Energy Certification programs
"It seems to me like we are trying to re-invent the wheel.  There are several available…"
Saturday
Egr renovations posted a status
Saturday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service