Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 29

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Eric Kjelshus commented on Jeremy Begley's blog post The Home Envelope : Does it Really Matter in a Heat Loss Caculation
"IT all matters,  I lot of sealing,  A lot of air barrier.  A lot of "R" A…"
11 hours ago
Michael Dunseith posted a status
"BPI Infiltration and Duct leakage (IDL) Certified"
16 hours ago
Jeremy Begley posted a blog post
19 hours ago
Kim Burnett joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
19 hours ago
Kent Mitchell commented on Adam Swain's blog post Top Worst Crawl Space Insulation Ideas
"Hi Adam - It sounds like you may be referring to enclosed crawlspaces - Here in the NW we've…"
22 hours ago
peter chang replied to Damien Greenfield's discussion Is there is cost saving for you in having a tankless water heater?
"I think it is quite possible the greatest savings will be realized by the lowest volume users. I…"
22 hours ago
Marie Fuentes is now a member of Home Energy Pros
22 hours ago
peter chang replied to peter chang's discussion Programmable tstat for electric baseboard?
"Good plan, thanks. That looks pretty much like how I used to program mine (when I had one). Maybe…"
23 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service