Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 25

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Christopher Morin posted a blog post

5 Things New Energy Efficiency HVAC Contractors Need to Know

1. Do not sell on Price! Use 'Simple Payback'The price of High-efficient equipment will undoubtedly…See More
4 hours ago
David Eggleton commented on David Eggleton's group Considering Permaculture &/or Transition
"In August 2014, in Minnesota, there's another unprecedented opportunity to meet and mix with a…"
11 hours ago
Glen Gallo commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"Nate, RE: Duct test On my own home and a rental I have tested more than once over the last many…"
11 hours ago
Profile Iconangela hines and Charles Goldman joined Home Energy Pros
16 hours ago
Jeff Flaherty joined Diane Chojnowski's group
Thumbnail

Tools of the Trade

A hammer and a saw used to be the key tools for home contractors. Today, the best-in-breed also use…See More
yesterday
Jeff Flaherty joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
yesterday
Debra Little joined David Eggleton's group
Thumbnail

Considering Permaculture &/or Transition

Some who work to increase energy efficiency and intelligent/wise use of energy are, and some will…See More
yesterday
Jim Gunshinan commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"Thanks for all the comments. Yes, it is interesting how the duct leakage grew over the years. Maybe…"
yesterday
Ed Minch commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"What sort of energy bill do you have now, what is  your target bill, and what will it cost to…"
yesterday
Nate Adams commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"I look forward to hearing more about the inside of the program! The big question that came to mind…"
yesterday
Glen Gallo commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"It is curious to see a 15% difference in the duct test from the test out of 2007 to the current…"
yesterday
John Proctor commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"So Jim, any idea as to how your ducts sprung another 15% leakage between 2007 and 2014? You also…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service