Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 28

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Kurt Shafer replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Reading the Invisco description you will find that it is designed to be surrounded by cellulose to…"
10 hours ago
Glen Gallo replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Kurt, I think cost of operation is always a factor but I am not sure I would leave it just cfm.…"
10 hours ago

Paul DelVaglio just added their location.
(via Member Map)

11 hours ago
Paul DelVaglio posted a photo
12 hours ago
reflintorm replied to Jamie Kaye's discussion Flickering LED lights
"I think, Better to replace the dimmer switch if it is not recovered then once go through the…"
16 hours ago
Kurt Shafer replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Glen,  You are the first person who has ever told me they prefer lower CFM. What you left out…"
yesterday
Glen Gallo replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Tamarack has lower CFM than typical fans and has a insulated lid that automatically closes when fan…"
yesterday
Tom Conlon's discussion was featured

Whole House Fans - Love 'Em or Not?

I just searched this forum for "Whole House Fan", but I didn't find much about them (except …See More
yesterday
Tom White shared Brandon Walton's blog post on Twitter
yesterday
Brandon Walton's blog post was featured

12 Things Every Home Performance Contractor Should Have on Their Work Truck

Every home is unique and differs from the last. It would be a perfect world (from a project…See More
yesterday
Griffin Hagle replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
yesterday
Griffin Hagle replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Kurt, Whoops, looks like I got my links mixed up. Thanks for pointing that out. Here's the…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service