Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 35

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Photos

Loading…
  • Add Photos
  • View All

Latest Activity

Juan is now a member of Home Energy Pros
4 minutes ago
Caoimhin P Connell replied to Rodney Fox's discussion Radon: Truth vs. Myth
"Good morning, Mr. Cullen – As I mentioned in another post – for the purposes under…"
15 minutes ago
tedkidd replied to Rodney Fox's discussion Radon: Truth vs. Myth
"If putting the house under positive pressure using fresh air helps mitigate not just radon, but…"
1 hour ago
Rich Manning replied to Rodney Fox's discussion Radon: Truth vs. Myth
"Tell them the truth as you know it, and back it up with the facts!!"
1 hour ago
Rich Manning replied to Charles Ryan Weitzel's discussion Oil Fired Boiler Being Used as the Heating Source in Two Air Handlers of a Historic Home
"Yes, its a Hydro-air system. It uses one boiler to supply hot water to the coil in the supply side…"
1 hour ago
tedkidd replied to Rodney Fox's discussion Radon: Truth vs. Myth
";) I love uncovering absuedities... Funny how creatively and vehemently people will argue against…"
1 hour ago
Rich Manning replied to Rodney Fox's discussion Radon: Truth vs. Myth
"Ted, you did it again! I would say that there's nothing like explaining the facts, but that…"
1 hour ago
Rodney Fox liked Rodney Fox's discussion Radon: Truth vs. Myth
2 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service