Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 40

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Videos

  • Add Videos
  • View All

Latest Activity

Walter Ahlgrim replied to Steve's discussion Too many BTU's. Too much horsepower?
"The 5 ton system you have is not 500 hp racecar engines they are 500 hp truck engines. The duct…"
7 hours ago
Daniel James Grundy replied to Daniel James Grundy's discussion Stack/wind pressure and flow networks.
"So I wanted to start with a basic who can help then go into more detail later. But yes find…"
11 hours ago
Daniel James Grundy replied to Daniel James Grundy's discussion Stack/wind pressure and flow networks.
"My tutor got back to me and while areas don't quite feel right a little to much assumptions…"
11 hours ago
Brennan Less replied to Daniel James Grundy's discussion Stack/wind pressure and flow networks.
"Daniel, I'm assuming you're trying to predict the airflows through the different openings…"
13 hours ago
Martin Newmark joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
15 hours ago
John Nicholas replied to Brad Cook's discussion BDT with vermiculite in hollow CMU walls?
"If the drywall is in good shape, you should have little worries about the 50pa depressurization…"
17 hours ago
tedkidd replied to Steve's discussion Too many BTU's. Too much horsepower?
"Does the house ever feel clammy? Do you have to keep the thermostat below 74 to be comfortable? Is…"
19 hours ago
Danielle Sass Byrnett liked Diane Chojnowski's blog post Don MacOdrum receives BPI's 2017 Tony Woods Award!
20 hours ago

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service