Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 42

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Latest Activity

Green ID posted blog posts
2 hours ago
Home Energy Magazine's blog post was featured

The Results Are In: These Are The Most Energy-Efficient Utilities in the US

Our first-ever scorecard of US utilities, released today, reveals striking regional differences and…See More
9 hours ago
Joe Konopacki replied to Brent Shapiro's discussion Investigating 3257KWH monthly usage issue.
"Brent, Using an ammeter, I would measure each 'hot' conductor leaving the fuses. (Find an…"
9 hours ago
Chris Allen is now a member of Home Energy Pros
10 hours ago

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service