    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 30

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

john bustos posted photos
26 minutes ago
john bustos posted an album

Items/Issues Found In Attics

Pics of deficiencies we have come across.
30 minutes ago
Benjamin Gromicko posted blog posts
38 minutes ago
Profile IconAvi Yashchin, Nick Semon, David McCann and 1 more joined Home Energy Pros
48 minutes ago
Craig Lane posted photos
12 hours ago
David Snell replied to Patrick Michaelyan's discussion Mold on exterior walls
"I have dealt with mold on multiple occasions.. ​As a Mold Inspector Charlotte NC, i recommend…"
12 hours ago
Chad Mcaulife replied to Bart Nicholson's discussion Minneapolis Blower Door and Duct Blaster for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I would be interested in the blaster!!!"
23 hours ago
Chad Mcaulife replied to Matthew P's discussion Needed: Gas Detector and CO Detector. What do you recommend?
"The new BPI standards require a Gas Sniffer which has a read out of the LEL.  The cheapest I…"
23 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service