Here is your chance!

Thanks to Bo Jespersen, President of The Breathable Home in Manchester, Maine for contributing February's home performance head scratcher.

Bo was stumped after his company was hired to install some spray foam insulation in a second story bedroom side attic.

When Bo arrived, he noticed that the work was exclusively on the north slope of the home, and that the owner had installed three layers of 2" thick rigid foam in-between the rafters, and applied one-part spray foam along the edges (where some stuffed fiberglass was found as well). A small air channel was left between the top of the foam and the bottom of the roof sheathing. The ridge beam was exposed and required ending the rigid foam to the southern slope to make it air tight.

Keep reading...

Tags: BPI, Chump, Newsletter, Stump, the

Views: 110

Replies to This Discussion

The moisture problem with the home in question that Bo Jespersen's company, The Breathable Home is encountering in the Stump the Chump article this month is likely due to warm moist air from inside the house (as described in the article) coming in contact with a cold roof deck.  Frost is probably not even forming.  When this happens, water vapor in the air condenses and causes the described situation where moisture drips down into the room below.
The fix would be to create access to the air gap above the the rigid insulation and completely fill that gap with foam as well as seal the gaps at the top of the rigid insulation near the ridge beam. That would eliminate any possibility of warm moist air from contacting the cold roof sheathing.

The solution to this problem is to prevent warm moist air from contacting a condensing surface.  This is difficult, because it is nearly impossible to create a perfect air barrier – especially one that maintains a seal over time in a climate with large temperature swings and between materials that have different coefficients of thermal expansion. 

One solution would be to pull up the roofing material (singles, slate, whatever), and add rigid insulation underneath, overlapped (2-3in), then add lathe and sheathing (the space between the lathe creates an air channel) and then add the roofing material.   The insulation will need to be thick enough so that the air under the sheathing won't reach the dew point even during the coldest nights.  This option is expensive.  

A cheaper option would be to remove the rigid foam, spray the underside of the roof deck with foam, and then place the rigid board back in while the foam is still nice and gooey, essentially as a continuation of the foam.  That will get rid of the air space where condensation can occur.  It would be nice if the foams had the same thermal expansion coefficients, and there weren’t air bubbles at the interface, but that is probably inevitable.   The risk here is that there isn’t enough vapor permeability through the foam and that any water that gets under the roof deck from roof leaks will stay there.  This is a risk with all under roof deck foam applications, and demands a good job maintaining the roof once the under-deck insulation is installed.    

To just solve the water issue, a ridge vent could be installed and the soffit area could be re-done to create an air channel under the roof deck, but this would mean continued air leakage.  Far from ideal.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Tom Mallard just added their location.
(via Member Map)

2 hours ago
Profile IconDon Hughes, Julian Sark, James Hatheway and 4 more joined Home Energy Pros
4 hours ago
Meagan Foster posted events
5 hours ago
Meagan Foster updated an event

EnergyLogic's RaterFest! at Black Hawk, CO

September 13, 2013 at 10am to September 15, 2013 at 12pm
Join us for one of the best home energy conferences available!  This retreat will provide…See More
5 hours ago
Meagan Foster updated an event

Homes 401: Green Rater Training at Berthoud, CO

June 25, 2013 to June 26, 2013
This highly interactive workshop builds upon the material presented in the online course, further…See More
5 hours ago
Meagan Foster updated an event

HERS Rater Training - Online at Online

July 1, 2013 to July 26, 2013
NEW - our great RESNET HERS Rater online training is now completely self-paced, so you can start at…See More
5 hours ago
Meagan Foster updated an event

BPI Building Analyst Training - Online at Online

June 3, 2013 to June 28, 2013
Join the EnergyLogic Academy for our BPI BA online training - we just went to a completely open…See More
5 hours ago
Anna Svensson posted a discussion

Looking for residential building and remodeling experts

Making sure you residential building and remodeling professionals out there are aware of the call…See More
6 hours ago
Bryce Cramer joined Leslie McDowell, BPI's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
9 hours ago
Bryce Cramer replied to Mike Kandel's discussion June's Stump the Chump: What's Wrong with this Picture? in the group Building Performance Institute (BPI)
"Key is this was done in warm weather. The back wall of the room was also uninsulated, but the lower…"
9 hours ago
James Hatheway added a discussion to the group Job Board
Thumbnail

Quality Assurance Verification Specialist - Little Rock, Arkansas

CLEAResult (clearesult.com) is looking for a QA Verification professional who wants to leverage…See More
11 hours ago
Profile IconJames Hatheway and Mike Wallis joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
11 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service