The infrared image below was taken by John Snell of The Snell Group. The structure had recently been insulated with blown in cellulose. What is wrong with this picture, and what's the solution? What steps should the contractor and installation crew have taken to avoid this?

Photo Courtesy of The Snell Group


Tags: BPI, Chump, Group, Snell, Stump, The, camera, cellulose, infrared, insulation, More…the

Views: 289

Replies to This Discussion

It is best to list the conditions when the image was taken and the palette used- I will assume winter time with a heated interior because of the warm areas around the windows and the 38.5 degree tag:

This appears to be balloon framing - note the lack of a band area showing between the upper and lower row of windows.

It also appears that there are fireblocks in the wall - specifically for one problem, there is a row of fireblocks between the two upper left windows.  If this is the case, the insulator did a ridiculously poor job - he did not fill the cavity above the fireblock and he did not fill the cavity below the fireblock.  Look to the immediate right of the right upper window - there appears to be a cup full of insulation in the upper of the two cavities.  Look at he right of the upper left window - missed virtually all of the cavities there.

If he were trained in proper densepack techniques he would have a better chance of getting good fill.  And using a scanner after insulating (temperature and time permitting) is the perfect training tool for a couple of dozen jobs.

To correct the situation now, put a Post-It note on the wall at the center of every defect you want repaired, then have someone do the repairs that knows how to insulate.

Congratulations to Bo Jespersen of The Breathable Home in Manchester, Maine who clearly knows his way around blown in cellulose, and maybe chicken coops too! We received many great responses to last month's stumper, but Bo sent us the most accurate diagnosis and complete solution.

Says Bo: "This picture shows the kind of situation that keeps me up at night. I own an insulation company and this type of installation is what we would deem unacceptable in anything other than a chicken coop! What we have here is cellulose installed in a wall that has both settled, and in some areas, been missed altogether."

Bo explains that the installer used the drill-and-fill method by drilling a small hole (or two) in each stud cavity, inserting a small nozzle, and blowing the cellulose directly against the finished wall. "The problem with this method is you can never be sure of the density of the finished product, or that full coverage isn't being prevented by a block or obstruction."

This technique has been used for many years, and until the advent of IR cameras, was assumed to be sufficient. The picture however, is what we see more often than not with this technique, whether in a home that was insulated last week or 30 years ago.

The solution lies in first installing the insulation correctly, and then verifying that it completely filled the cavity. Says Bo, "We have found that the best way to install cellulose is to drill a larger hole in each stud bay (3"), insert a fill tube that reaches both the top and bottom plate, and use an insulation machine that is calibrated to 3.5 lbs. per cubic foot. Finally, before any holes are plugged, we inspect each bay for complete coverage via an IR camera. The density of the cellulose assures it will not settle like it did in the picture, and the IR camera makes sure that all areas are filled."

Bo adds that all is not lost for the property owner. "The building can most likely be re-insulated with dense pack cellulose if they use the above technique - we have to do it all the time!"

 

RSS

Videos

  • Add Videos
  • View All

Latest Activity

Quinn Korzeniecki added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Call for Nominations: Tony Woods Award and Building Performance Hall of Fame

The Building Performance Institute, Inc. (BPI) is seeking nominations for the 2017 Tony Woods Award…See More
11 minutes ago
Horace Douglas Hunt, Jr. posted a status
"In the end, isn't it about our #legacy? i haven't left mine yet, have you? #morningthoughts #real"
3 hours ago
Horace Douglas Hunt, Jr. posted a status
"Q = 0.03A + 7.5(N+1) = if you know it, why isn't anyone incorporating it into their installation? #HVAC @accausa @_BPI_ #ASHRAE #6222016"
3 hours ago
Michael Dunseith commented on Kirsten Richnavsky's group Retrotec, Inc
"Congratulations on your new postion. Looking forward to working with you in the near future. Best…"
19 hours ago
Michael Dunseith joined Kirsten Richnavsky's group
19 hours ago
Wayne Melancon replied to Wayne Melancon's discussion What's the Most Profitable HVAC Job for Your Company?
"I'll agree with you there Ken. We'll get shopped by residential when the customer already…"
yesterday
Horace Douglas Hunt, Jr. commented on Horace Douglas Hunt, Jr.'s photo
Thumbnail

IMG_3138

"and....this was the best looking spot in the air handler. Seal the unit if you want to have any…"
yesterday
Horace Douglas Hunt, Jr. commented on Horace Douglas Hunt, Jr.'s photo
Thumbnail

IMG_3139

"Beginnings of mold....due in some part to leaks in air handler pulling hot humid air from…"
yesterday

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service