The infrared image below was taken by John Snell of The Snell Group. The structure had recently been insulated with blown in cellulose. What is wrong with this picture, and what's the solution? What steps should the contractor and installation crew have taken to avoid this?

Photo Courtesy of The Snell Group


Tags: BPI, Chump, Group, Snell, Stump, The, camera, cellulose, infrared, insulation, More…the

Views: 258

Replies to This Discussion

It is best to list the conditions when the image was taken and the palette used- I will assume winter time with a heated interior because of the warm areas around the windows and the 38.5 degree tag:

This appears to be balloon framing - note the lack of a band area showing between the upper and lower row of windows.

It also appears that there are fireblocks in the wall - specifically for one problem, there is a row of fireblocks between the two upper left windows.  If this is the case, the insulator did a ridiculously poor job - he did not fill the cavity above the fireblock and he did not fill the cavity below the fireblock.  Look to the immediate right of the right upper window - there appears to be a cup full of insulation in the upper of the two cavities.  Look at he right of the upper left window - missed virtually all of the cavities there.

If he were trained in proper densepack techniques he would have a better chance of getting good fill.  And using a scanner after insulating (temperature and time permitting) is the perfect training tool for a couple of dozen jobs.

To correct the situation now, put a Post-It note on the wall at the center of every defect you want repaired, then have someone do the repairs that knows how to insulate.

Congratulations to Bo Jespersen of The Breathable Home in Manchester, Maine who clearly knows his way around blown in cellulose, and maybe chicken coops too! We received many great responses to last month's stumper, but Bo sent us the most accurate diagnosis and complete solution.

Says Bo: "This picture shows the kind of situation that keeps me up at night. I own an insulation company and this type of installation is what we would deem unacceptable in anything other than a chicken coop! What we have here is cellulose installed in a wall that has both settled, and in some areas, been missed altogether."

Bo explains that the installer used the drill-and-fill method by drilling a small hole (or two) in each stud cavity, inserting a small nozzle, and blowing the cellulose directly against the finished wall. "The problem with this method is you can never be sure of the density of the finished product, or that full coverage isn't being prevented by a block or obstruction."

This technique has been used for many years, and until the advent of IR cameras, was assumed to be sufficient. The picture however, is what we see more often than not with this technique, whether in a home that was insulated last week or 30 years ago.

The solution lies in first installing the insulation correctly, and then verifying that it completely filled the cavity. Says Bo, "We have found that the best way to install cellulose is to drill a larger hole in each stud bay (3"), insert a fill tube that reaches both the top and bottom plate, and use an insulation machine that is calibrated to 3.5 lbs. per cubic foot. Finally, before any holes are plugged, we inspect each bay for complete coverage via an IR camera. The density of the cellulose assures it will not settle like it did in the picture, and the IR camera makes sure that all areas are filled."

Bo adds that all is not lost for the property owner. "The building can most likely be re-insulated with dense pack cellulose if they use the above technique - we have to do it all the time!"

 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Todd Collins replied to Patrick Michaelyan's discussion Vinyl Siding with Integral Insulation
"might want to consider vapor permeability.   Need to move the dew point out far enough to…"
1 hour ago
bill lazar replied to robert jones's discussion Should your local weatherization company be required to have someone BPI certified on their staff?
"all this will be clarified soon with the new SWS guidelines mandated by DOE- but just WZ…"
1 hour ago
Glen Gallo replied to Brady Mills's discussion Can someone recommend a whole home water filtration system?
"I was in the business of cleaning up water at one point. We produced spot free pressure washers of…"
3 hours ago
Patrick Michaelyan replied to Casey Gesell's discussion Looking for home improvement companies to join our dealer network!
"Casey I'm in Arlington, VA."
6 hours ago
Patrick Michaelyan replied to Patrick Michaelyan's discussion Vinyl Siding with Integral Insulation
"Thanks for the input Dennis!"
6 hours ago
Patrick Michaelyan replied to Patrick Michaelyan's discussion Vinyl Siding with Integral Insulation
"It's about time! I love Hardie products but I had my reservations in the part when installing…"
6 hours ago
Patrick Michaelyan replied to Patrick Michaelyan's discussion Vinyl Siding with Integral Insulation
"Great, thanks Craig. I read up on Tyvek's Stucco Wrap many moons ago and completely forgot…"
6 hours ago
Dennis Heidner replied to Patrick Michaelyan's discussion Vinyl Siding with Integral Insulation
"If you are using Hardie on a building,   James Hardie recently released a note that says in…"
6 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service