Client is complaining that their bonus room above their garage is always hot during summer and cold during winter. They feel there in no insulation in the garage ceiling.They have a huge south facing dbl pane metal window and 3 small windows facing west. They do not want to change out the windows.

 I checked and there is insulation in the garage ceiling but not in the garage walls.  The water heater is in the garage and they also have vents in the walls for make up air. There is some issue about the amount of airflow to that room, which we can fix. Do you have other ideas to fix this problem. Thanks for the advice.

Judi SHE BUILDS "GREEN"

Views: 46

Replies to This Discussion

Insulation may not be the issue here, but check the kneewalls for plywood or rigid foam board on the backside of the wall and if it is air sealed. (foam and/or tape at the seams.

 From past experience & without seeing the house I would guess that this room is the furthermost from the HVAC unit and you are not getting adequate CFM out of the supply to this point.

If the garage is not conditioned then this is also an issue.

Measure the air flow at different delivery registers in the home along with the temp difference.

There are booster fans on the market that can be placed at the problem registers to help alleviate this problem.

Air seal duct system if excisable will boost cfm/btu's. Caution with booster fans that sit on registers I've done flow hood testing and have seen a reduction in cfm's not including wasted energy/money

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Todd St.Clair joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
1 hour ago
Todd St.Clair replied to Jim Falakos's discussion Treat Software in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"How long ago did you buy this, if it was good for 5 months? And how much would you take for this."
1 hour ago
Bud Poll replied to Bud Poll's discussion Basing air exchange on house volume??
"Hi Sean, yes I am struggling with this and that is why I opened the discussion, so a definite…"
3 hours ago
Lynda Wright is now a member of Home Energy Pros
3 hours ago
Sean Lintow Sr replied to Bud Poll's discussion Basing air exchange on house volume??
"Sorry Bud but I think you need to clarify your issues with using volumes to calculate ACH As for…"
14 hours ago
Profile IconWes Anderson, Jean-Paul and Bryan joined Home Energy Pros
Friday
Dennis Heidner commented on Dale Stephens's blog post LED Lighting 24-month update 18,240 hours & counting
"Dale, good write up. For the landscaping bulbs,  if they had been T3 12V wedge bulbs,  I…"
Friday
Brett Little commented on Tom White's video
Thumbnail

The Future of Housing - And How Airtightness Can Help

"It's very true! So many people and contractors have tons of insulated attics but no air seal…"
Thursday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service