Client is complaining that their bonus room above their garage is always hot during summer and cold during winter. They feel there in no insulation in the garage ceiling.They have a huge south facing dbl pane metal window and 3 small windows facing west. They do not want to change out the windows.

 I checked and there is insulation in the garage ceiling but not in the garage walls.  The water heater is in the garage and they also have vents in the walls for make up air. There is some issue about the amount of airflow to that room, which we can fix. Do you have other ideas to fix this problem. Thanks for the advice.

Judi SHE BUILDS "GREEN"

Views: 64

Replies to This Discussion

Insulation may not be the issue here, but check the kneewalls for plywood or rigid foam board on the backside of the wall and if it is air sealed. (foam and/or tape at the seams.

 From past experience & without seeing the house I would guess that this room is the furthermost from the HVAC unit and you are not getting adequate CFM out of the supply to this point.

If the garage is not conditioned then this is also an issue.

Measure the air flow at different delivery registers in the home along with the temp difference.

There are booster fans on the market that can be placed at the problem registers to help alleviate this problem.

Air seal duct system if excisable will boost cfm/btu's. Caution with booster fans that sit on registers I've done flow hood testing and have seen a reduction in cfm's not including wasted energy/money

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Profile IconBenney Dornevil, Mike Norvell Sr and Jen Loomis joined Home Energy Pros
10 hours ago
Joanie Minor posted a status
"Home Performance Institute now offers OSHA 10 and Confined Space Classes. Call 203-536-2151 to register."
11 hours ago
Joanie Minor posted a photo
11 hours ago
John Kaye posted a blog post

FREE Home Efficiency & Safety Assessments in the Los Angeles County area.

Since last June I have been qualifying homeowners in the Los Angeles County for the Home Upgrade…See More
16 hours ago
Eric Kjelshus replied to Rod Fox's discussion Does calcification affect electric water heater aquastat temperature sensor performance?
"Those 240 Volt aquastats shut off and then on kinda quick back on.  The older the tank the…"
21 hours ago
Rod Fox replied to Rod Fox's discussion Does calcification affect electric water heater aquastat temperature sensor performance?
"Well I'd love to tell you folks I found an answer, but I did not... I went to my…"
yesterday
Rod Fox replied to Kevin Eigel's discussion What is the best energy auditing software?
"I've been trying to answer this question for many years and have not yet found an answer.…"
yesterday
Jerry Lawrence posted events
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service