Do the following situations and solutions fall in line with what you are doing to comply with IRC 408.3? There seems to be discrepancies between code officials. All I need is the practical solution.

 

Force Air Ducts in Crawlspace

– If 80% Install Louvered Vent to Air Supply, Install 6” External Combustion Air Vent

– If 90% or Air Handler not in Crawl - In the Crawlspace, Install Louvered Vent in Air Supply and Return

Nothing Mechanical in Crawlspace or Seal Combustion Boiler

– Input & Output from Conditioned Space through Two Internal Wall Cavities with Vent Grills

Unsealed Combustion Boiler in Crawlspace

– Install Two 6” External Combustion Air Vents Extended to Boiler

Views: 798

Replies to This Discussion

First, just so everyone is on the same page – the applicable section…

R408.3 Unvented crawl space. Ventilation openings in under-floor spaces specified in Sections R408.1 and R408.2 shall not be required where:

1. Exposed earth is covered with a continuous Class I vapor retarder. Joints of the vapor retarder shall overlap by 6 inches (152 mm) and shall be sealed or taped. The edges of the vapor retarder shall extend at least 6 inches (152 mm) up the stem wall and shall be attached and sealed to the stem wall; and

2. One of the following is provided for the under-floor space:

2.1. Continuously operated mechanical exhaust ventilation at a rate equal to 1 cubic foot per minute (0.47 L/s) for each 50 square feet (4.7m2) of crawlspace floor area, including an air pathway to the common area (such as a duct or transfer grille), and perimeter walls insulated in accordance with Section N1102.2.9;

2.2. Conditioned air supply sized to deliver at a rate equal to 1 cubic foot per minute (0.47 L/s) for each 50 square feet (4.7 m2) of under-floor area, including a return air pathway to the common area (such as a duct or transfer grille), and perimeter walls insulated in accordance with Section N1102.2.9;

2.3. Plenum in existing structures complying with Section M1601.5, if under-floor space is used as a plenum.

Personally 2.1 is a joke, 2.3 is a mess, which leaves one with 2.2 – insulate the Crawl Space walls (Crawl Space wall insulation reqs. vary from a U .477 for climate zones 1 & 2 / .136 for zone 3 / .065 for all others) & add in one supply & 1 return duct sized properly. Now there is nothing that says the grills have to be open, just that it can supply the air to help eliminate any moisture issues. If you are going this route, the HVAC designer needs to know this to appropriately size it when they are doing the JST&D calcs.

As for the AHJ, well they have the final say on what the codes actually mean & what they will accept, but a properly detailed diagram with the calcs should make them happy & alleviate them from pushing for their “rule of thumbs”

Now onto your list - the items you listed do not really fall into this section, and instead fall into the Mechanical section. Personally I don't want anything in the crawl space, but if anything mechanical is in there it would be a sealed combustion unit or electrical only. As for the others, find an area that you can place them, seal it off from the rest of the house, insulate it & supply combustion air from the outside only

Thanks and to clarify some more, I'm taking about sealing the crawlspace from the outside with expanding foam along the rim joists, vinyl faced fiberglass on the walls, and sealed plastic on the floor.
Uh, what? I can see doing some air sealing on the outside, but the rim joist needs to be insulated on the inside of the crawlspace with CC Foam (you can also run some foam on the exterior to cover it, but I would still insulate inside also). Maybe you can get away with FG in your crawls, but I wouldn't recomend it - I would generally  go with sprayed on CC foam or foam panels (assuming all water issues have been dealt with)
Right. Air sealing the keep outside air from coming in. But the foam, insulation, caulk or however you want to do it is on the inside of the crawlspace. My concern is meeting the ventilation requirements of IRC.

RSS

Discussion Forum

Moisture/Mold on rim joist;

Started by John Shillito. Last reply by John Nicholas Jan 10. 6 Replies

Radon - Passive Systems

Started by Sean Lintow Sr. Last reply by Bryan Gabriel Jan 5. 5 Replies

Vented Soffit! DO or DON'T?

Started by Daniel Baur-McGuire. Last reply by Daniel Baur-McGuire Nov 15, 2016. 13 Replies

Water Saver or Gimmick?

Started by Sean Lintow Sr. Last reply by Bob Blanchette Oct 23, 2016. 18 Replies

Duct Testing - is a change in order?

Started by Sean Lintow Sr. Last reply by Sean Lintow Sr Aug 6, 2015. 20 Replies

Videos

  • Add Videos
  • View All

Latest Activity

jackie harsha added a discussion to the group Marketing Energy Efficiency
Thumbnail

Informative video about energy and its implications

Like many, I’ve been struggling with the differences between what consumers say and what they…See More
yesterday
jackie harsha joined James Sayers's group
Thumbnail

Marketing Energy Efficiency

Sharing ideas, tools and examples of promoting energy efficiency to consumersSee More
yesterday
Ajmain Azraf posted blog posts
yesterday
Robert Post added a discussion to the group Job Board
Thumbnail

Hiring Residential BPI BA Energy Auditors In Philadelphia Area

Please reach me if interested and we can plan a call to discuss this opportunity. This is a full…See More
yesterday
Robert Post joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
yesterday
Gerald Shechter liked Quinn Korzeniecki's discussion BPI Supports Strong Consumer Protection in Residential PACE Financing Programs
yesterday
John Fulton posted a photo

Roman Blinds For Living Room

Perfect Blinds to cover Long Window. Roman Blinds for your Drawing Room, Seating Space, Corner…
Friday
Robert Post posted a blog post

Hiring BPI BA Professionals in Philadelphia Area

Please reach me if interested and we can plan a call to discuss this opportunity. This is a full…See More
Thursday

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service