Passive venting solution needed.
How do you manage the air flow to properly ventilate an attic when one soffit is low and the other somewhere in between low and high? I have a cape with an almost full length dust pan on the rear. Original venting from back in 79 included 2 small (12" x 12") gable vents and 4 each front and read rectangular (12" x 3") vents in the soffits. Ice dams have always been a problem so now the old shoe maker is finally going to fix the problem. You know, the shoe maker's children have no shoes, well energy auditors suffer from a similar affliction:).
Now that I'm slowly making improvements I find myself halfway between the old design and a new design, which was going to be lots of soffit venting and a full ridge vent, and I would probably keep some gable venting, TBD. The new siding went on the front a year ago with extended rafter tails with a full 10" perforated vinyl soffit, about 30 times the previous vent area, take that Mr. ice dam.
Currently I've extended the rear rafter tails and have the fascia and soffits removed, but the roof with its ridge vent will be delayed until next year. Then I started thinking, are those little gable vents going to be adequate for this winter with all of this additional soffit venting? A quick trip up onto the rear staging with some smoke confirmed my fears. The rear soffits are exhausting warm air, Arghh! That is definitely not what I want for ice season.
Note, I have some known heat loss and air leakage issues inside I can address which will certainly help.
My problem is two part. One, I need a temporary solution to get me through this winter, and two, what is the best design for a final solution, and hopefully incorporate as much of the temporary work into the final product, I'm cheap?
Let's review the problem. With my rear soffit vents just a couple of feet below my undersized gable vents, the new excessive ventilation area in my low front soffits (9' below my gable vents) has shifted my neutral pressure plane (NPP) below those rear vents. Remember, as you increase a leakage area, or vent area, the NPP moves towards the increased opening. So, following Dr. Joseph Lstiburek's advice is not working in my situation.
"3) Put more vents down low than up high
This is where the code tends to have it wrong. You want more entry points at the perimeter than exit points at the top."
http://www.greenbuildingadvisor.com/blogs/dept/building-science/lst...
It's not that Dr. Joe's advice is wrong, it is just that it doesn't apply to mixed height soffit vents and I'm assuming the problem gets even more complex when you add in multiple height exhaust vents such as ridge, gable, or other.
Here's my proposed solution, which I can patch in for temporary and incorporate into my completed project. This isn't cast in concrete, that's why I'm here. The now oversized front soffit vents enter mostly into two accessible small front attics, separated by a set of stairs. I can add an upper vent to the gable ends of each of these small attic spaces and then a restrictor in each rafter bay to limit the air flow up through the slope to the top attic. By limiting the air flow, I will shift the NPP upwards. These slopes are well insulated and have minimal leakage areas so a reduced air flow should be fine. I will also replace the two existing small gable vents with large triangular gables vents, trying to maximize the high vent area, again, shifting the NPP upwards. I will then do another smoke test to confirm whether or not I have achieved my goal of cold air flow into those rear soffits. Comes spring and a new roof, I would like to use a single sided ridge vent to minimize rain issues and further shift the NPP towards the top adding some margin to my venting strategy. Basically, I'm being forced to put the majority of my high vent area well above my low vent area and restrict my lowest of my low vents.
The searching/reading I have done has provided no guidance for how to balance the venting when multiple intake and exhaust heights are involved, beyond isolating attic areas so each area can function by itself. But, even that solution doesn't deal well with a cape such as mine or the typical salt boxes out there.
Any suggestions or comments?
Bud
Permalink Reply by Bob Blanchette on January 5, 2013 at 10:01am The 12" aluminum externally braced whirlybirds go for about $50 each, not unreasonable at all. They don't rust and come with high quality bearings. Rarely do they leak, the spinning action of the turbine sheds water off the vanes. If a few drops of rain do get in they normally end up on the low side of the duct and drip out on top of the shingles. This is why no sealant is applied to the lower side of the flashing. Figure one per 500sqft of attic floor area, although it's common practice to install 2 regardless of house size.
"Ventilation towers" were common in older buildings, they were designed as miniature steeples. Gable style vents were then applied to the sides of the miniature steeples.
Permalink Reply by Bob Blanchette on January 5, 2013 at 9:08am If homeowners aren't willing to have whirlybirds installed, large "turtle vents" can be an effective solution. They are about the size of a typical attic fan, but have no motor or blade. Using several of them can prove an effective "high point" solution. Large dormer or gable vents also can be effective when combined with oversized soffit venting. Oversizing soffit venting also helps when there is any wind, the hot air will EXIT out of the downwind soffit vents.
Permalink Reply by Sean Lintow Sr on January 5, 2013 at 9:07am I got to disagree somewhat with "air cannot" - air seeks the path of least resistance & yes it will exit via ridge vents (some better than others, of course). Are they my favorite item, no but they can & do work in many situations. You got to remember the purpose of venting is simply to allow excess heat & moisture to exit the attic assembly
Yeah I do like whirlybirds & yes Bud it is a "passive" system system that works whether or not there is wind or not - if there is wind it does work a lot better. Now would I use these up in an area with lots of snow - no, probably not
Permalink Reply by Bob Blanchette on January 5, 2013 at 9:20am Fair enough. Air will exit ridge vents, but at an insignificant rate. There is simply not enough pressure difference to force much air through the filter. On windy days an external baffle may help the ridge vent pull air through the filter.
Permalink Reply by Bud Poll on January 22, 2013 at 10:44am
Permalink Reply by Bob Blanchette on January 22, 2013 at 4:18pm We're talking about the surface same area as two 20x20 HVAC filters. 360CFM through a 20x20 HVAC filter will give a higher static pressure than 1 Pascal. Ridge vent filters aren't made of some magical material, light passes through them at about the same rate as a standard HVAC filter.
The filter may be open when new, but flow 720CFM through a 720sqin air filter and it will quickly become dirty. Just think of a HVAC unit with continuous fan for 90 days. Now you expose this to dusty attic air. Have you ever seen the screens clog on soffit vents? IMHO if the dust can clog those relatively coarse vents it will clog a HVAC filter that much quicker.
Net free area claimed by the manufacture does not take into account the increased static pressure created by "equivalent duct length" of the sharp turn the air has to make at the ridge and the baffles.
However all that being said I don't have a thermal imaging gun, I'd like to see the results. Shot a couple of wind turbines for me while you're at it ;) Maybe even throw and electric attic fan in just for good measure. I'd love to find an unbiased test of all the attic ventilation methods commonly used.
Here's an article on ridge vents from "ask the builder"
Permalink Reply by Bud Poll on January 22, 2013 at 5:10pm
Permalink Reply by Bob Blanchette on January 22, 2013 at 5:37pm About 250 pascals in 1" of water column. HVAC filter operation at a typical 0.1" @ 125FPM So we're at 25 pascals, not 1. Huge difference when talking about relying on air to simply "float out" of a ridge vent. I have a hard time believing if you were to put 40' of ridge vent against a blower moving 720CFM that the static pressure would only be 1 pascal or 1/250 of an inch. 0.1" sounds much more realistic, but it will never happen on natural convention alone.
Here's another video:
http://www.roofingcontractorreview.com/Attic-Ventilation-Help/Attic...|-Cooling-a-hot-attic-space.html
Yes there are cobwebs near the ridge, telling me at least some air has been going through the vent at some point since it's installation. Could have been on a windy day when the filter was clean. A typical attic fan pulls 1400CFM, 720CFM passively floating out of an attic through an air filter I don't see happening. If the ridge vent were that open you would see some air being pulled through it in the video.
Agreed, Tim does have some learning to do about neutral pressure planes. However I don't doubt his smoke test. IMHO wind is the primary mover of air through the attic, which in Oklahoma we have no shortage of. Wind will even come OUT of the soffit vents on the "back side" of the building. The ideology of air coming evenly through the soffits and gently floating out the top of the attic is another thing I've questioned. IMHO the wind is so much stronger of an influence of how the air actually flows in an attic since the pressures are much greater.
Then there is the question of which brand/type of ridge vents we're talking about. To read it from manufacturers tests they all claim theirs works the best. Independent testing? Good luck finding it ;) Also notice for powered ventilators, plain static vents and roof turbines none of them tend to perform tests against other brands. It's like they are OK with their products published specs, and one brand doesn't deliver more than another. The only possible exception are the solar attic fans which claim ridiculous CFM ratings out of tiny motors. Is there a particular brand/style of ridge vent you are considering?
Permalink Reply by Bud Poll on January 22, 2013 at 6:48pm
Permalink Reply by Bob Blanchette on January 22, 2013 at 7:10pm .57 pascals is a low pressure, not enough to overcome the resistance of the filter at any significant airflow rate. Oddly the .57 pascals is enough to operate a wind turbine, even with no wind. A wind turbine must have an extremely low resistance for this to work.
Seeing as I live in a climate where cooling is the primary reason for attic venting, I will say it takes LOTS of airflow to significantly reduce the high attic temperatures caused by solar gain. Passive solutions simply aren't effective, you need something that uses electrical power or can take advantage of the wind. In winter ice dams are primarily caused by heat leaking from the structure, not solar gain, not much airflow required. 50CFM or so provided by 40' of ridge vent may be enough to do the job. You're just trying to prevent ice dams, not reduce summer heat gain, a simple static vent the size of an electric attic fan will do the same job. Happens all the time, fan doesn't run in winter, yet no ice dams form.
Permalink Reply by Bud Poll on January 22, 2013 at 7:39pm
Permalink Reply by Bob Blanchette on January 23, 2013 at 4:34am Since you are primarily interested in reducing ice dams, a new article you might want to see:
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
yangxiaohua posted a blog post
Judi Lyall joined allen p tanner's group
Judi Lyall replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase
Tom Maides commented on Jim Gunshinan's blog post The Universe Is Made of Stories
Laurie DiDonato posted an event
Tom Delconte posted a blog post
Jim Gunshinan commented on Jim Gunshinan's blog post The Universe Is Made of Stories
Edward Foskey commented on Jim Gunshinan's blog post The Universe Is Made of Stories© 2013 Created by Lawrence Berkeley National Laboratory.