Slides 38 - 42 show data from 55 duct systems - Air handler performance varies from 6.5 to 2 CFM Per Watt

 

Forced air distribution systems–ducts–can contribute to unanticipated energy use in a variety of ways: through duct leakage, pressure effects, conductive and radiant heat gain, and insufficient airflow. Ducts provide a great opportunity to demonstrate system effects.

Often, when one part of the system is addressed, unanticipated problems may occur. ECM motors appear to offer significant efficiency and performance improvements over the old PCS motors that have been the workhorses for heating and cooling equipment for years.

 As part of routine inspections through the Performance Tested Comfort System program,  (http://ptcsnw.com) Mark Jerome (KAM Energy, Roseburg, Oregon) collected measured airflow and amp draw data on 55 systems that he was installing or inspecting. The attached PDF is his presentation of that data, given this July at Data, Not Dogma, in Goldendale, Washington. One thing to note is that these systems were installed by trained contractors as part of a program that has a focus on performance. One may suspect wider diversity of results in a sample of installations outside of the program’s influence.

It takes energy to move air. What are the implications for the design and installation of new space conditioning systems? What happens when we install central cooling and ECM motors into pre-existing duct systems? What are potential unexpected consequences of furnace filter replacement and duct sealing in systems with ECM motors?

In Thousand Home Challenge projects, the energy it takes to move air in combustion venting systems, spot and central ventilation, as well as heating and cooling can be a significant portion of a home’s threshold allowance. It is critical to reexamine our assumptions: how can we achieve exceptional air quality and comfort at a fraction of the energy used in most homes today?

 

Share your data so we can better understand the opportunity to reduce the energy use of blowers and fans.

 

Tags: CFM, CFM Per Watt, ECM Blowers, ESP, Forced Air Distribution, Thousand Home Challenge, external static pressure, field data, performance, residential

Views: 661

Attachments:

Replies to This Discussion

Interesting. 

 

Unfortunately this is a slideshow that requires a presenter, some issues are not clear in silent mode.  One issue that did not make itself clear to me is the purported "problem of low static / low airflow issues".  This is something I've never seen cause problems, so I'm unfamiliar with the problems it causes.  What should I be looking out for?  

Here is Bruce Manclark's response:

 

Low static seems to confuse the infinty system into delivering low cfm

 

And Bob Davis's response to Bruce:

 

Bruce is right but Mark [Jerome] can give a more complete description.  The very short answer is that if there isn't enough resistance for the fan controller to work against, it can end up supplying not enough air.

Thanks Linda!  That's really helpful!  

 

Bob/Bruce/Mark, I haven't had a problem with that.  Can you tell me the circumstances you've seen that occur?  All my systems are operating well under .5, particularly at lower stages, and I've had only great reports from homeowners.  

Response from Bob Davis, Ecotope:

 

In the NW, we've seen this happen several times with newer heat pumps outfitted with ECM air handlers.  If the duct system is sized so that external static ends up being below .2 or .3" WC, the ECM controller ends up "hunting" for the right RPM and settles (typically) on a very low flow (generally about 250 CFM/ton or even lower).  Installers have had to change out control boards or even add more restriction to the duct system to get desired flow rates.

 

Response from Mark Jerome, KAM Energy:

 

The issue with low airflow low static is not very common, approx. 20 sites in the Pacific Northwest. I have personally seen it around 12 of these sites with 8 others I have discussed with contractors contacting me by phone.
 
Specifically low return static and or low supply static with total external static pressure at or lower than .3" WC has normally been the issue. Short supply plenums or nonexistence return air plenums, and a few return air of a mobile/modular home plenums, seem to be the biggest culprit. This issue has been across all manufactures which leads me to believe this is certainly a motor problem combined with a duct sizing problem. Homes that have been weatherized or right sized with a new heat pump to match the load of the home (heat pumps sized smaller from a larger heat pump or other forced air system) would be the probable cause.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Dennis Heidner replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"The press report really doesn't give enough information to clearly answer why  they are…"
5 hours ago
Edward Foskey commented on Edward Foskey's blog post Preparing to Update the Heat Pump
"Gustavo, Thanks for the input. I agree with you in that I will be waiting till my system's…"
7 hours ago
Gustavo Melo commented on Edward Foskey's blog post Preparing to Update the Heat Pump
"Any system that is out of warranty is really a coin toss as to whether it is financially better to…"
7 hours ago
Dennis Heidner replied to J.C. Martel's discussion Disasters & sustainable energy
"Such as Greensburg…"
9 hours ago
Tom Delconte commented on Edward Foskey's blog post Preparing to Update the Heat Pump
"Thanks, Ed, I get it now. I would just put in what my hvac guy tells me to put in: a $17,000…"
9 hours ago
Jim Gunshinan commented on Jim Gunshinan's blog post The Universe Is Made of Stories
"Hi Tom, I'm sorry you didn't think my blog post was helpful or appropriate. I'll…"
11 hours ago
Tom Delconte commented on Jim Gunshinan's blog post The Universe Is Made of Stories
"Whatever happened to separation of church, state, and scientific home building science? What would…"
11 hours ago
Craig Savage's video was featured

What is Building America

The U.S. Department of Energy's (DOE) Building America program is a source of innovation in residential building energy performance, durability, quality, aff...
15 hours ago
Jim Gunshinan's blog post was featured

The Universe Is Made of Stories

The late poet and political activist Muriel Rukeyser famously said, The Universe is made of…See More
15 hours ago
Jim Gunshinan posted a status
"New blog post, "The Universe Is Made of Stories""
15 hours ago
Jim Gunshinan posted a blog post

The Universe Is Made of Stories

The late poet and political activist Muriel Rukeyser famously said, The Universe is made of…See More
15 hours ago
Craig Savage posted videos
20 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service