Anyone ever hear of a window, or unit of insulated glass, as having different winter and summer U values? 

 

This wasn't on an NFRC sticker.  It was on a glass manufacturer's spec sheet. 

 

They listed it like this:

 

Winter - Air / Argon  0.35 / 0.31

Summer - Air / Argon 0.32 / 0.28

 

Our program requires a U value of 0.30 to receive an incentive rebate.  So obviously, homeowners and contractors want to average the summer and winter Argon fill U values to come up with an average of 0.295 and call it good.

 

I think it is just a piece of insulated glass that they want to have installed/retrofitted into their existing wood windows, and get an incentive for that. 

 

Views: 3021

Attachments:

Reply to This

Replies to This Discussion

The winter U-value is what is shown on the NFRC labels, and should be used for code compliance and incentive programs. It is calculated at -18C (about 0F) outside, and 21 C (about 70F), and a roughly 15 mph wind speed. The summer U-value is calculated with conditions where it is warm outside and hardly any wind. This means that the U-value will be a bit better, but it is not a representative condition for heat losss. The Solar Heat Gain Coefficient (SHGC) is more important during periods with solar gain. So think U-value for heating, and SHGC for cooling.

Christian
WIndows and Daylighting Group
Lawrence Berkeley National Laboratory
Adam:

Currently in communication with this gentleman:

Andre Anders, PhD
Leader, Plasma Applications Group
Lawrence Berkeley National Laboratory
1 Cyclotron Road, MS 53, Berkeley, California 94720, USA
Tel. 510-486-6745, Fax 510-486-4374

He's circulating the information among his associates and will be in touch following the holiday. Will probably find it's way Christian at LBNL, who has responded since last I checked in.

BTW, Christian's advice to use the winter number is probably not what you wanted to hear regarding the available incentive. If 0.30 U is a common cut off # for incentives, I would expect manufacturers to work to that figure, although in a manufacturing environment, such changes may be a challenge. Perhaps a bit of latitude from incentive providers is in order...who is going to notice a U difference of 0.01 ?

Thanks for surfacing this mystery.
Steve, Adam,

Andre forwarded your question to me, that is why I responded here. Many manufacturers have products that meet U=0.30, since that was the cut-off for the IRS tax credit.

If you are looking for even better windows, you can take a look at this website, where you can find listing of manufacturers that meet U=0.22 and less.
http://www.windowsvolumepurchase.org/

Christian
Thank you for the replies! Our program does require NFRC stickers, so this guy is going to be out of luck anyways.

But I was curious about the different winter and summer U values anyways. Thanks for the response and clairificaiton!

Adam

RSS

Photos

Loading…
  • Add Photos
  • View All

Latest Activity

Joe Crisara posted a blog post

Give Your False Assumptions a Knockout Punch

By Derek LauberWe face seemingly unlimited obstacles when trying to manage and grow our…See More
11 hours ago
Profile IconJoe Crisara, Earth Advantage, Sydney G. Roberts and 6 more joined Home Energy Pros
11 hours ago
Jonny Fisher added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Minneapolis Blower Doors and Duct Blaster for sale

I have two Minneapolis Blower Doors + DG 700, duct blaster with manometer and some other…See More
11 hours ago
Jonny Fisher replied to Hamed Ghanbari's discussion Need a Minneapolis Blower Door + DG 700 in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I have two Minneapolis blower doors with DG 700.  I also have some other used equipment if you…"
12 hours ago
Nolan Walker replied to Hamed Ghanbari's discussion Need a Minneapolis Blower Door + DG 700 in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi Hamed, I have an extra Minneapolis blower door system - nolanwalker@gmail.com for more…"
13 hours ago
Mike Burton replied to Hamed Ghanbari's discussion Need a Minneapolis Blower Door + DG 700 in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I have a Minneapolis Bloor Door + DG700 I am wanting to sell. Please contact me at…"
15 hours ago
Hamed Ghanbari added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Need a Minneapolis Blower Door + DG 700

Looking to buy a Minneapolis Blower Door + DG 700, any assistant would be greatly appreciated.…See More
15 hours ago
Sandra K. Adomatis, SRA posted a status
"See my latest blog on "Appraiser Competency-The Simple Version" https://adomatis.wordpress.com/"
16 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service