Anyone ever hear of a window, or unit of insulated glass, as having different winter and summer U values? 

 

This wasn't on an NFRC sticker.  It was on a glass manufacturer's spec sheet. 

 

They listed it like this:

 

Winter - Air / Argon  0.35 / 0.31

Summer - Air / Argon 0.32 / 0.28

 

Our program requires a U value of 0.30 to receive an incentive rebate.  So obviously, homeowners and contractors want to average the summer and winter Argon fill U values to come up with an average of 0.295 and call it good.

 

I think it is just a piece of insulated glass that they want to have installed/retrofitted into their existing wood windows, and get an incentive for that. 

 

Views: 762

Attachments:

Reply to This

Replies to This Discussion

The winter U-value is what is shown on the NFRC labels, and should be used for code compliance and incentive programs. It is calculated at -18C (about 0F) outside, and 21 C (about 70F), and a roughly 15 mph wind speed. The summer U-value is calculated with conditions where it is warm outside and hardly any wind. This means that the U-value will be a bit better, but it is not a representative condition for heat losss. The Solar Heat Gain Coefficient (SHGC) is more important during periods with solar gain. So think U-value for heating, and SHGC for cooling.

Christian
WIndows and Daylighting Group
Lawrence Berkeley National Laboratory
Adam:

Currently in communication with this gentleman:

Andre Anders, PhD
Leader, Plasma Applications Group
Lawrence Berkeley National Laboratory
1 Cyclotron Road, MS 53, Berkeley, California 94720, USA
Tel. 510-486-6745, Fax 510-486-4374

He's circulating the information among his associates and will be in touch following the holiday. Will probably find it's way Christian at LBNL, who has responded since last I checked in.

BTW, Christian's advice to use the winter number is probably not what you wanted to hear regarding the available incentive. If 0.30 U is a common cut off # for incentives, I would expect manufacturers to work to that figure, although in a manufacturing environment, such changes may be a challenge. Perhaps a bit of latitude from incentive providers is in order...who is going to notice a U difference of 0.01 ?

Thanks for surfacing this mystery.
Steve, Adam,

Andre forwarded your question to me, that is why I responded here. Many manufacturers have products that meet U=0.30, since that was the cut-off for the IRS tax credit.

If you are looking for even better windows, you can take a look at this website, where you can find listing of manufacturers that meet U=0.22 and less.
http://www.windowsvolumepurchase.org/

Christian
Thank you for the replies! Our program does require NFRC stickers, so this guy is going to be out of luck anyways.

But I was curious about the different winter and summer U values anyways. Thanks for the response and clairificaiton!

Adam

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Johnny Ritzo posted a discussion

Selecting a Water Heater

I am looking at updating the heating and water heating systems in a rental home I recently…See More
2 hours ago
Eric Kjelshus replied to Patrick Michaelyan's discussion Hot Upper Stories
"When I am asked to fix this home.   I start with a Heat Loss and gain, blower door IR  sq…"
3 hours ago

Edward Foskey just added their location.
(via Member Map)

8 hours ago
Profile IconMartin Easley and Richard Vito joined Home Energy Pros
13 hours ago
Bud Poll replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"This is a topic I have discussed many times, but unfortunately cost is all too often the deciding…"
17 hours ago
Sean Lintow Sr replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"If you can't talk them into replacing with IC rated... Look into Tenmat - those are designed…"
17 hours ago
Bachi Brunato posted a discussion

Boxing and Insulating Around Non-ICAT Cans

I have a client with 16) 4" halogen recessed light fixtures in the attic.I'd like to cover the cans…See More
23 hours ago
Dennis Heidner replied to Patrick Michaelyan's discussion Hot Upper Stories
"Could you have them make a simple two line graph of the outside temperature, noting sun/clouds,…"
yesterday
Bob Blanchette replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"You make some valid points, especially with the base rate charges. Increasing the base rate instead…"
yesterday
Bob Blanchette replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"Amen, make energy show it's true cost instead of subsidizing it. We have some of the lowest…"
yesterday
Dennis Heidner replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"The press report really doesn't give enough information to clearly answer why  they are…"
yesterday
Edward Foskey commented on Edward Foskey's blog post Preparing to Update the Heat Pump
"Gustavo, Thanks for the input. I agree with you in that I will be waiting till my system's…"
Saturday

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service