Anyone ever hear of a window, or unit of insulated glass, as having different winter and summer U values? 


This wasn't on an NFRC sticker.  It was on a glass manufacturer's spec sheet. 


They listed it like this:


Winter - Air / Argon  0.35 / 0.31

Summer - Air / Argon 0.32 / 0.28


Our program requires a U value of 0.30 to receive an incentive rebate.  So obviously, homeowners and contractors want to average the summer and winter Argon fill U values to come up with an average of 0.295 and call it good.


I think it is just a piece of insulated glass that they want to have installed/retrofitted into their existing wood windows, and get an incentive for that. 


Views: 2787


Reply to This

Replies to This Discussion

The winter U-value is what is shown on the NFRC labels, and should be used for code compliance and incentive programs. It is calculated at -18C (about 0F) outside, and 21 C (about 70F), and a roughly 15 mph wind speed. The summer U-value is calculated with conditions where it is warm outside and hardly any wind. This means that the U-value will be a bit better, but it is not a representative condition for heat losss. The Solar Heat Gain Coefficient (SHGC) is more important during periods with solar gain. So think U-value for heating, and SHGC for cooling.

WIndows and Daylighting Group
Lawrence Berkeley National Laboratory

Currently in communication with this gentleman:

Andre Anders, PhD
Leader, Plasma Applications Group
Lawrence Berkeley National Laboratory
1 Cyclotron Road, MS 53, Berkeley, California 94720, USA
Tel. 510-486-6745, Fax 510-486-4374

He's circulating the information among his associates and will be in touch following the holiday. Will probably find it's way Christian at LBNL, who has responded since last I checked in.

BTW, Christian's advice to use the winter number is probably not what you wanted to hear regarding the available incentive. If 0.30 U is a common cut off # for incentives, I would expect manufacturers to work to that figure, although in a manufacturing environment, such changes may be a challenge. Perhaps a bit of latitude from incentive providers is in order...who is going to notice a U difference of 0.01 ?

Thanks for surfacing this mystery.
Steve, Adam,

Andre forwarded your question to me, that is why I responded here. Many manufacturers have products that meet U=0.30, since that was the cut-off for the IRS tax credit.

If you are looking for even better windows, you can take a look at this website, where you can find listing of manufacturers that meet U=0.22 and less.

Thank you for the replies! Our program does require NFRC stickers, so this guy is going to be out of luck anyways.

But I was curious about the different winter and summer U values anyways. Thanks for the response and clairificaiton!



Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Dennis Heidner replied to Rod Fox's discussion Utility Meter Accuracy
"Yup,  but it also looks like for the tariffs above residential services that they include…"
2 hours ago
Dan McKee posted a blog post

9 Tips To Get Your Furnace Winter Ready

A well heated, cozy home is what makes the day better when the winter comes in full fledged. So, it…See More
4 hours ago
Tauran Ivall replied to Tauran Ivall's discussion Energy Efficient Entry Door options out there?
"Thanks Graham, There is a distributor in Portland for them. Thanks for the link to the blog.  "
6 hours ago
Bob Blanchette replied to Rod Fox's discussion Utility Meter Accuracy
"The use of CT's screams commercial service, most likely over 200A. 200A and lower uses simply…"
6 hours ago
Dennis Heidner replied to Rod Fox's discussion Utility Meter Accuracy
"It's not just the CT's that you need to worry about.   The CT will pick up the…"
11 hours ago
Rod Fox replied to Rod Fox's discussion Utility Meter Accuracy
"Good point, Dennis. In the case of my original post, we're talking about a digital meter.…"
11 hours ago
Dennis Heidner replied to Rod Fox's discussion Utility Meter Accuracy
"I think you met the reply for Rod Frost."
12 hours ago
Kevin Wood replied to Tauran Ivall's discussion Energy Efficient Entry Door options out there?
" has training on the fiberglass doors. I wanted to transfer the link but I am not…"
15 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service