Anyone ever hear of a window, or unit of insulated glass, as having different winter and summer U values? 

 

This wasn't on an NFRC sticker.  It was on a glass manufacturer's spec sheet. 

 

They listed it like this:

 

Winter - Air / Argon  0.35 / 0.31

Summer - Air / Argon 0.32 / 0.28

 

Our program requires a U value of 0.30 to receive an incentive rebate.  So obviously, homeowners and contractors want to average the summer and winter Argon fill U values to come up with an average of 0.295 and call it good.

 

I think it is just a piece of insulated glass that they want to have installed/retrofitted into their existing wood windows, and get an incentive for that. 

 

Views: 1986

Attachments:

Reply to This

Replies to This Discussion

The winter U-value is what is shown on the NFRC labels, and should be used for code compliance and incentive programs. It is calculated at -18C (about 0F) outside, and 21 C (about 70F), and a roughly 15 mph wind speed. The summer U-value is calculated with conditions where it is warm outside and hardly any wind. This means that the U-value will be a bit better, but it is not a representative condition for heat losss. The Solar Heat Gain Coefficient (SHGC) is more important during periods with solar gain. So think U-value for heating, and SHGC for cooling.

Christian
WIndows and Daylighting Group
Lawrence Berkeley National Laboratory
Adam:

Currently in communication with this gentleman:

Andre Anders, PhD
Leader, Plasma Applications Group
Lawrence Berkeley National Laboratory
1 Cyclotron Road, MS 53, Berkeley, California 94720, USA
Tel. 510-486-6745, Fax 510-486-4374

He's circulating the information among his associates and will be in touch following the holiday. Will probably find it's way Christian at LBNL, who has responded since last I checked in.

BTW, Christian's advice to use the winter number is probably not what you wanted to hear regarding the available incentive. If 0.30 U is a common cut off # for incentives, I would expect manufacturers to work to that figure, although in a manufacturing environment, such changes may be a challenge. Perhaps a bit of latitude from incentive providers is in order...who is going to notice a U difference of 0.01 ?

Thanks for surfacing this mystery.
Steve, Adam,

Andre forwarded your question to me, that is why I responded here. Many manufacturers have products that meet U=0.30, since that was the cut-off for the IRS tax credit.

If you are looking for even better windows, you can take a look at this website, where you can find listing of manufacturers that meet U=0.22 and less.
http://www.windowsvolumepurchase.org/

Christian
Thank you for the replies! Our program does require NFRC stickers, so this guy is going to be out of luck anyways.

But I was curious about the different winter and summer U values anyways. Thanks for the response and clairificaiton!

Adam

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Profile IconWes Anderson, Jean-Paul and Bryan joined Home Energy Pros
22 hours ago
Dennis Heidner commented on Dale Stephens's blog post LED Lighting 24-month update 18,240 hours & counting
"Dale, good write up. For the landscaping bulbs,  if they had been T3 12V wedge bulbs,  I…"
yesterday
Brett Little commented on Tom White's video
Thumbnail

The Future of Housing - And How Airtightness Can Help

"It's very true! So many people and contractors have tons of insulated attics but no air seal…"
yesterday
Chris Leach replied to Richard Beyer's discussion "The Dangers of Using Spray Foam Insulation"
"The problems will surface soon enough . Why don't we take a second look at this over rated…"
yesterday
Don Fitchett commented on Tom White's video
yesterday
tedkidd replied to Bob Blanchette's discussion How does Cycles Per Hour affect real world AFUE?
"Want to spot a simpleton? It's a guy who thinks EE and comfort are disconnected.  Want…"
yesterday
tedkidd commented on Tom White's blog post Clean Energy Works Oregon: Total Home Performance
"Nice post Tom! I really like how he puts that. Leveraging interests so they can optimize…"
yesterday
Kent Mitchell commented on Tom White's blog post Clean Energy Works Oregon: Total Home Performance
"As a contractor in the region - we frequently wonder how/why you can be a non-profit?  Oregon…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service